My combi boiler’s buner keeps firing up in fixed 4 minutes…

Customer Question
Hello,My combi boiler’s buner keeps...
Hello,My combi boiler’s buner keeps firing up in fixed 4 minutes interval when there is no HW and CH demand. Please bear with me with the long description below.I moved into my current house in this summer. At that moment, the HW of the boiler (Worcester 24i RSF Combination Boiler) was working intermittently. After checkinig by following the installation manual, I replaced the PCB with a NEW one and the HW resumed working well.In this winter, both the CH and HW work well. However, I recently noticed the following sequence of behaviour of the boiler when there is no HW and CH (i.e all the TRV in the house are off) demand:
- Burner fires up for 18-20 secounds
- Burner stops the fire and rest for exactly 4 minutes
- Burner fires up again for 18-20 seconds.
The above 4-min-cycle repeats for the whole day when there is no HW and CH demand. It stops when I switches the boiler to HW only mode.I checked the installation manual and from there I got that the burner fires when
1) The CH programmer is on and the room theromostat is on
2) Internal Autofrostat demand
3) HW demandSo, I suspected that the problem might come from the “Internal Autofrostat demand” which fires up the burner at once after the 4 minutes anti-cycle delay. However, the boiler is inside the utility room which has a temperature simlar to that of the kitchen and it is always well above 10°C. I checked the resistance of the Thermistor (i.e. the central heating sensor) and it is within the range of 690 and 33k ohms (as per the installation manual) when it is either hot or in room temperature.
I then suspected that it was the problem of the PCB which calls for Internal Autofrostat demand even when the water is well above 4°C. I replaced the PCB with a refurbished one but the problem still occurred (CH and HW worked normally with this refurbished PCB). I returned that one and got another refurbished PCB but the problem still occurred. I then wonder whether the problem is caused by a faulty PCB.I get stucked now. Any advice on the cause of the problem?Thank you.
Submitted: 8 months ago.Category: UK Plumbing
Show More
Show Less
Ask Your Own UK Plumbing Question
Answered in 1 hour by:
11/15/2017
Plumber: Andrew Smith, Engineer replied 8 months ago
Andrew Smith
Andrew Smith, Engineer
Category: UK Plumbing
Satisfied Customers: 3,781
Experience: Domestic Gas, Commercial Gas, LPG, Unvented Hot Water, Part P Electrical, Commercial Catering
Verified
Are you getting warm water flow through the heating pipework?
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
No. When that 4-minutes cycle occurs while there is no HW or CH demand, the heating pipework is cold.
Plumber: Andrew Smith, Engineer replied 8 months ago
Ok.
If the heat is staying inside the boiler tben perhaps there is a hot water preheat on your model?
Can you find the GC no. To identify the full model (and build age)
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
My boiler, as per the manual, has no preheat function. I found that there are 2 GC numbers shown in the inside plate of the boiler (please see the attached photo). I also attached the installation manual of the boiler for your reference.
I checked the pipework outside the boiler again tonight. It is still cold even the 4-mins-no-demand cycle runs for more than an hour. I believe the pump keeps circulating the CH water within the pipework inside the boiler via the by-pass pipe. The pipework inside the boiler and the pump is super hot.
Plumber: Andrew Smith, Engineer replied 8 months ago
Ok.
Your boiler is old in design - no divertor valve and a twin pass heat exchanger.
If the fault was on the ch side tben the pump would run.
This would suggest the hw side and the hw flow switch.Have you checked to see if it is 'made' continually? This would mean the boiler would fire all the time but keep shutting down on overheat (then cooling and restarting)
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
Do you mean whether the sparking fires continually? No, it doesn't. The burner fires up for 20 seconds and then the fire is out (and no sparking) for 4 minutes, then the fire lights up again for 20 seconds.I am sorry that I don't quite follow what you wrote:
"If the fault was on the ch side tben the pump would run.
This would suggest the hw side and the hw flow switch."
What is the implication of this?
Plumber: Andrew Smith, Engineer replied 8 months ago
Has the hw flow switch been looked at?
I think the boiler thinks the tap is running and fires up. Then when the heat has nowhere to go it overheard and shuts down. Then cools down and repeats.
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
However, the problem does not occur when the programmer is switched to "0" (i.e. no central heating) or when the CH water temperature is turned to the minimum. If the boiler thinks that the tap is running and fires up, it would keep on doing this even when the programmer is switched to "0" or the CH temp. is turned to minimum. Right?
Plumber: Andrew Smith, Engineer replied 8 months ago
Correct.
It's difficult if not stood in front if it with a multimeter.
This boiler has no bypass.
When in hw mode the flow switch fires the boiler and heats the water through one set of pipes in the heat exchanger.
When ch is called for then the pump starts and the water is heated through 2 other pipes in the heat exchanger.
Are you able to do Check O on page 33?
The only thing that can fire the boiler without the pump coming on is the hw flow switch
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
I will do the flow switch check by following the procedure "O" on page 33 tonight. On the other hand,
I found a fixed by-pass in figure 2 and figure 36. Is it different from the bypass you mentioned.
On the other hand, when this 4-minutes-cycle-with-no-demand is running, the hw pipe inside the boiler is cold while the ch pipe (including the bypass pipe) inside the boiler and the pump is super hot. I believe the pump is running when this 4-minutes-cycle-with-no-demand problem occurs.
Plumber: Andrew Smith, Engineer replied 8 months ago
Ok.
Still strange then.
If the pump is running then try removing the frost stat and seeing how it behaves?
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
34;removing the frost stat"? I don't know where it is. The manual mentioned the "built in frost thermostat" in page 17 (last paragraph) but didn't show it in any of the diagram or the parts list. I thought that it is something in the PCB that works with the
"central heating sensor". That was why I checked the "central heating sensor" and found that it is fine and also replaced the PCB twice but the problem is still there.
Plumber: Andrew Smith, Engineer replied 8 months ago
It looks like the case, the only thing left to check is the wiring harness between the stat and PCB if you have checked both?
Uncommon but possible.
Ask Your Own UK Plumbing Question
Customer reply replied 8 months ago
I have checked the flow switch. It works ok. I checked again the CH and HW sensor on the PCB connector end, they also give the expected resistance.
I found the following sequence when the 4-minutes-cycle-with-no-demand is interrupted by HW demand:
- burner fires for 20 seconds
- the fire stop, then within 4 minutes, turns on the hot tap
- burner fires up at once to provide HW. When the hot tap is closed, burner keeps on firing for 20 seconds more.
- then the fire stops. After 4 minutes, the burner fires up again and the 4-minutes-cycle-with-no-demand repeats.If the cause of the problem could not be identified, my next bet is to order a NEW PCB and give it the last chance (even my current PCB is less than 6 months old and I already tried 2 refurbished PCBs)..
Plumber: Andrew Smith, Engineer replied 8 months ago
Sorry, but that would be my guess too or a wiring harness fault?
Ask Your Own UK Plumbing Question
Customer reply replied 7 months ago
Hello,I have replaced the PCB with a NEW one but exactly the same problem still occurs. The previous expert mentioned that it could be wiring harness fault. I tried disconnecting the CH sensor and the HW sensor. The LED flashes when either one of them is disconnected. So, the problem would not be the wiring harness of these 2 sensor. How can I find which wiring is creating the problem? Or, do you have any idea why the problem occurs? Thank you.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a plumberLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Ridley Your Own Question
Rick Ridley
Rick Ridley
Rick Ridley, UK Heating Engineer
Category: UK Plumbing
Satisfied Customers: 1,561
1,561 Satisfied Customers
Experience: 30 Years on the tools, now retired, Ex CORGI

Rick Ridley is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Rick Ridley

Rick Ridley

UK Heating Engineer

1,561 satisfied customers

30 Years on the tools, now retired, Ex CORGI

Chamberlain Maintenance

Chamberlain Maintenance

Plumber

324 satisfied customers

Qualified Plumber with over 17 years experience in Domestic & Commercial plumbing.

qwasert

qwasert

Plumber

203 satisfied customers

Condensing and Combi Boilers

Marc

Marc

Plumber

156 satisfied customers

Plumbing and Heating expert with 25+ years experience, 21+yrs self employed as a contractor.

Ardent Engineering

Ardent Engineering

Engineer

49 satisfied customers

Registered Gas Installer

Dan_Robinson

Dan_Robinson

Plumber

33 satisfied customers

Owner and Director of Jennings Heating Ltd. Registered to work with Gas and High pressure hot water systems.

Elliott Oxton

Elliott Oxton

Plumber

15 satisfied customers

Lead engineer at eoxtongasservice

< Previous | Next >

Related UK Plumbing Questions
I have a glow worm 30hxi boiler. My initial problem was an
Hi I have a glow worm 30hxi boiler. My initial problem was an error code F13. This could happen at random times, sometimes within seconds of the boiler starting, but sometimes only after a few hours. … read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
I have a Gloworm 24cxi boiler that keeps cycling every 20
Customer: Hi, I have a Gloworm 24cxi boiler that keeps cycling every 20 mins or so for about 5 mins. the CH demand is off and the temp stat is on zero. when it cycles the heat is dissipated to the rad… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
MAIN HE 12" Boiler blowing fuse. My wife reported no hot
MAIN HE 12" Boiler blowing fuse. My wife reported no hot water (CH isn't on at this time). I've found a fused spur to the timer, with the fuse blown. Replaced the fuse (3A), timer (electronic) illumin… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
I have a Worcester 28i Junior that's several years old. I've
I have a Worcester 28i Junior that's several years old. I've come to run the hot tap and only cold water. Tried the heating and no heating. In either case it doesn't seem to be firing up - can't hear … read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
Worcester Bosch 400HF boiler and the rads are heating up when
Worcester Bosch 400HF boiler and the rads are heating up when on HW. Diverter valve has been changed and problem persists. Everything else okay.… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
Boiler on demand ch/hw, room thermostat turn to max , everything
Boiler on demand ch/hw, room thermostat turn to max , everything is 'lit up' but the boiler is not firing up to heat the water up ?… read more
Brian
Brian
Plumbing & Heating Engineer
131 satisfied customers
Worcester Bosch Highflow 400.Following BG service had room thermostat
Worcester Bosch Highflow 400. Following BG service had room thermostat fitted. No CH since. Pump now runs continuously and green Demand light is permanently on. HW is working. BG have fitted new flow … read more
canuck the pro
canuck the pro
262 satisfied customers
I have a year 2003 Ferroli mondea 102 and have a constant intermittent
I have a year 2003 Ferroli mondea 102 and have a constant intermittent problem in both modes ch/hw, all starting sequences are ok. Problem is intermittent low ignition flame that does not always sprea… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
Just fitted tp9000 to ideal w2000. Hot water working fine but
Just fitted tp9000 to ideal w2000. Hot water working fine but when ch should be on I'm just getting the pump without the boiler kicking in? Any ideas? Connections are 1=Bridge to L 2=not used 3=Boiler… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
We moved in to our house 2 years ago, from the start we found
We moved in to our house 2 years ago, from the start we found a problem with the central heating (CH). When the programmer switches on, morning or afternoon the diverter or 3 way valve always sends th… read more
canuck the pro
canuck the pro
262 satisfied customers
ref Ultracom 30 CXi with RF. Overnight setting at 18.5 deg,
ref Ultracom 30 CXi with RF. Overnight setting at 18.5 deg, and showing 21 deg. At these settings the boiler should not be working however last night the radiatiors were constanly hot. Couple of times… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
My combi boiler is always on even with the clock set to off
My combi boiler is always on (heating the water for the rad's) even with the clock/timer & stat set to off, & switched to Taps only?… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
The room stat will not turn on the pump or boiler. I I remove
The room stat will not turn on the pump or boiler. I I remove the call for heat wire from the junction box it is live, when I put it back in with pump live and boiler live the terminal is no longer li… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
Hello, I am looking to replace our present CH/HW controller
Hello, I am looking to replace our present CH/HW controller with an up to date one - such as a Honeywell THR860. The current system consists of: * Randall 102 time switch * 3-wire room thermostat * HW… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
Potterton Suprima 100 boiler. Erratic function: sometimes comes
Potterton Suprima 100 boiler. Erratic function: sometimes comes on as per timer instruction, sometimes not. Will open the motorised valve for CH or HW but not both at same time. So the valves are work… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
Can you help with a boiler problem with a Worcester 24i RSF
Can you help with a boiler problem with a Worcester 24i RSF combi boiler, mechanical timer, no room stat. Hot water supply is working fine. Central heating demand fires boiler OK but after about a min… read more
Andrew Smith
Andrew Smith
Engineer
3,781 satisfied customers
My newly installed Glowworm sx boiler seems to be constantly
My newly installed Glowworm sx boiler seems to be constantly on despite us not having switched on the central heating or hot water. Its not constantly lit but is making a noise as if it was operationa… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
the operating switch seems to have a problem, i keep having
the operating switch seems to have a problem, i keep having to switch it from hot water on to hot water off for the heating to come on?? the boiler fires up fine when i run the hot water. tonight it i… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
1,561 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x