Have questions about how much voltage a welder needs to operate correctly? Need welder troubleshooting tips? The person who operates the welding machine needs to have good dexterity and should provide attention to detail. Welder problems/questions can be related to their load, wiring and connections and so on. To know more about welder problems, below are a few common questions answered by Experts.

Will a plug-free welder that requires the use of a 40 amp, 230 volts single phase source to start the arc run on a 50 am, 250 volts plug and receptacle?

The 50 amp plug and receptacle can be used, however, it should be fed with a 40 amp breaker and if the plug does not come equipped with a cord, a #8 rubber cord with three conductors in it need to be used.

A welder’s input rating is 230 volts, 48 amps, with the outlet 60 feet from the breaker panel, what sized wire is required?

As long as the cable is protected from physical damage, use this set up: using 6/2 ground cable, two insulated conductors and a bare ground within the jacket of the cable. This provides a 55 amp circuit using cable. Since 55 amps is not a standard size, the next standard size breaker available is 60 amps.

Will a 240 volt welder, that requires 32 amp supply 48 amps outlet, run off a transformer of 110 volts and 32 amp outlet?

If the outlet is providing just 110 volts, the welder may not work. Ideally it would be better to have a new, dedicated circuit installed especially for the welder. The wire and the outlet for the new circuit must be rated properly. In the U.S. that would be a #8 copper wire. The RCD need not be anything special but needs to be rated properly for the load and wire which feeds the welder outlet. The store clerk can be consulted for the proper wire size and amperage load. If 32 amps is not a standard RCD rating, the next size number can be used.

How many amps should the new breaker be for a new 220 volt, 50 amp arc welder that needs to run on a 220 outlet of the current breaker box?

This would require a 50 amp breaker and if the romex is being wired in, it should be a #6. If the receptacle is being piped, it can be a #8 single conductor. Additionally, the receptacle would need to be matched to the welder plug cap. This is dependent on the plug style. In case a matching one is being purchased, the box will provide a wiring diagram. Do not forget the ground wire as it is also an important wiring.

Listed above are some of the welder problems or questions which can arise. There may be many other facets and areas of welder problems that you may have questions about. Welder repair and welder troubleshooting is possible when needed in a customized manner with the assistance of Experts. Despite the presence of many avenues for answers and information, Experts can be the source who can provide accurate, unique, specific, step by step instructions and expertise which is difficult to obtain reasonably from any other source.
Please type your question in the field below

3 verified Electricians are online now

Electricians on JustAnswer are verified through an extensive 8-step process including screening of licenses, certifications, education and/or employment. Learn more

Online
Mike

Master Electrician

Working on MBA

★★★★★
1426 positive reviews
Online
Jason

Service Technician

Associate Degree

★★★★★
4922 positive reviews
Online
Mike G.

Master Electrician

Vocational, Technical or Trade Scho

★★★★★
9751 positive reviews
See all Electricians