I have a metal building and want to put windows in an outer…

Customer Question
I have a metal building...
I have a metal building and want to put windows in an outer wall. I want a 20 inch wide window that meets the fire egress requirements. I think it will need to be 20 inch wide by 42 tall. I can find some for roughly $600 each but not sure if it is the right kind as far as fitting it to be leak proof through the wall. I will be framing up to the outer skin of the building. What kind of outer frame or what method is best? I'm not quite sure exactly what to look for. Any example of how to install one on a metal building? The matal is corrugated and the ribs are 1 1/4 tall.
Submitted: 7 months ago.Category: Structural Engineering
Show More
Show Less
Ask Your Own Structural Engineering Question
Answered in 1 hour by:
12/23/2017
Structural Engineer: walkereng, Consultant replied 7 months ago
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 3,004
Experience: Over 30 years of Structural Engineering experience.
Verified

I can help.

Here a link to a Mueller Metal Buildings video that discusses the various methods of installing a window in a corrugated metal building wall:

https://www.youtube.com/watch?v=G_tbsk29plY

I hope this helps.

Let me know if you have any questions after you watch the video

Ask Your Own Structural Engineering Question
Customer reply replied 7 months ago
I’ve seen a few videos but none told me which parts to buy. I’m more interested in finding a 20w x 42h egress window with a frame for a metal building.
Structural Engineer: walkereng, Consultant replied 7 months ago

The bottom of the egress window opening can't exceed 44” from the finished floor. The minimum opening area of the egress window is 5.7 square feet. The minimum egress window opening height is 24” high. The minimum egress window opening is 20” wide.

A 3040 (3'x4') window should meet your needs.

You just need to contact your metal building manufacturer to sell you the windows and flashing required.

Ask Your Own Structural Engineering Question
Customer reply replied 7 months ago
I know the code. I need narrow so I will be using a 20 wide x 42 high. I can’t find one suitable for a metal building. Metal building companies act like they have no idea what I’m referring to. Their answer is “we offer two styles of windows”
Structural Engineer: walkereng, Consultant replied 6 months ago

You are going to have to go to a window manufacturer like Anderson to get your specific size window you are looking for. Here is a link to the Anderson site and a sample table of dimensions available.

https://awwebcdnprdcd.azureedge.net/-/media/aw/files/technical-docs/sizing/sizing-windowswithstormwatch--400series-tilt-washhungfull-frame.pdf

If you feel you have received a satisfactory answer to your question, please click the Rating button that is appropriate. Experts are credited for each adequately Rated answer they provide. If you have additional questions, please let me know. Thanks

Ask Your Own Structural Engineering Question
Customer reply replied 6 months ago
I know where to buy windows. The question is about the window frame and method for installing into a metal building.
Structural Engineer: walkereng, Consultant replied 6 months ago

I am sorry that I can not seem to help you. I will opt-out of the question and maybe another expert can help you.

Ask Your Own Structural Engineering Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a structural engineerLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask walkereng Your Own Question
walkereng
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 3,004
3,004 Satisfied Customers
Experience: Over 30 years of Structural Engineering experience.

walkereng is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

He answered my question promptly and gave me accurate, detailed information. If all of your experts are half as good, you have a great thing going here.

DianeDallas, TX

< Previous | Next >

Meet the Experts:

walkereng

walkereng

Consultant

3,004 satisfied customers

Over 30 years of Structural Engineering experience.

vgdlpc

vgdlpc

Master's Degree

17 satisfied customers

Civil Engineer, Major in Structures and Foundations. Professional Engineer 11 years of experience.

StructuralEng

StructuralEng

Consultant

6,402 satisfied customers

Structural Engineer

Matt

Matt

Engineer

45 satisfied customers

Mechanical Engineering Hons degree, been working in automotive industry for the last 18 years - Engine development engineer

ibosley

ibosley

Master's Degree

88 satisfied customers

Mechanical Engineering

Ellen

Ellen

Consultant

109 satisfied customers

attorney and legal researcher

P. Simmons

P. Simmons

Attorney

149 satisfied customers

45 years old, retired Marine Officer, current attorney

< Previous | Next >

Related Structural Engineering Questions
I'm cutting an egress window into my basement wall. My
I'm cutting an egress window into my basement wall. My casement window cutout will be 36" wide and 48" tall. My header will be four 2x12's bonded with construction adhesive and will be using 3/8 spax … read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
Can you provide guideline when metal framed framing requires
Can you provide guideline when metal framed framing requires wind bracing and when it doesnt?… read more
Rick
Rick
Supervisor
24,233 satisfied customers
We are building a house and the front porch is suspended
Hi! We are building a house and the front porch is suspended over 10 ft tall poured concrete walls. It will be constructed with corrugated steel and a slab poured over it. I am worried because they di… read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
We are building a house and the front porch is suspended
Hi! We are building a house and the front porch is suspended over 10 ft tall poured concrete walls. It will be constructed with corrugated steel and a slab poured over it. I am worried because they di… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
We have a shop with a 12' wide and 11' tall shop door. The
We have a shop with a 12' wide and 11' tall shop door. The existing header over the shop door is a 5.5" wide by 9" tall glu lam beam. We need to shrink the height of the 9" tall beam as much as possib… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
What size microlam is needed for a 22' wide opening? I'm
what size microlam is needed for a 22' wide opening? I'm taking the center support out (3 ft wall between 2 garage door openings ) to create a 22 ft wide continuous span. My intent/plan is to use (2) … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
I have a question about a common Fink or W truss system
Hi, I have a question for you about a common Fink or W truss system installed in a 30' x 40' building (so the truss span is 30'). The top chords are 2 x 6. The bottom chord and diagonal bracing are 2 … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
I want to open up the wall between my kitchen and living room.
I want to open up the wall between my kitchen and living room. The wall is load bearing. The joists are 2x4 16 inch oc and the attic is non storage non occupied. The attic does hold the HVAC ducts, el… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
I intend to remove a section of a foundation wall that
Hello, I intend to remove a section of a foundation wall that should be 38Wx50Hx8D" which is currently solid concrete. The intent is to install an egress window in its place. I would like to determine… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
I am building a new house with a wrap around concrete porch.
I am building a new house with a wrap around concrete porch. I am getting conflicting proposals on how to support the concrete porch. There will be poured concrete walls on both ends of the porch with… read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
I'm wanting to cut an opening and install a 20' x 10' overhead
I'm wanting to cut an opening and install a 20' x 10' overhead door. The opening is to be cut into a 6" thick, 25' wide and 12.5' tall concrete tilt-wall panel. Can I cut an opening that large in this… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
We are installing an egress window in our basement foundation wall. The joists run paralle
We are installing an egress window in our basement foundation wall. The joists run parallel to the wall. The window is 47.5" wide and 53" tall. The contractor suggested leaving 11" of concrete in plac… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
My wooden post frame garage 26' X 24' with corrogated metal
My wooden post frame garage 26' X 24' with corrogated metal skin was built in one corner of the property. It was not built square with the property lines but instead was built a few degrees clockwise.… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
Im adding an addition on to my home. It will be one level,
I'm adding an addition on to my home. It will be one level, 24' wide x 13' plus a basement. The project is in madison, WI. A portion of the basement of the addition will function as a bedroom. As such… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
I have a pole barn with 6"x6" pressure treated columns framing
I have a pole barn with 6"x6" pressure treated columns framing the door openings. The door opening is 18' wide. I wanted to double the columns with the same 6"x6" pressure treated and mount an i beam … read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
Im building a tire bale structure, and I need to pour a footing
I'm building a tire bale structure, and I need to pour a footing that will essentially only bear the weight of the slab above it and the things few things that will be in the workshop above it. How bi… read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
I need to design a new "wall of glass windows" for a home
I need to design a new "wall of glass windows" for a home modification. The home is a single story wood frame/stucco residence on a slab foundation--the "glass window wall" is an external load bearing… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,402 satisfied customers
i want to build a concrete wall around my property 36 inches
i want to build a concrete wall around my property 36 inches deep and 12 inches above ground and 12 inches wide. i will install a fence on top the wall. any problems with this?… read more
walkereng
walkereng
Consultant
Bachelor's Degree
3,004 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x