Looking at a 100+ yo cabin, in snow country with 4x6

floor/ceiling joists wr oc with...
Looking at a 100+ yo cabin, in snow country with 4x6 floor/ceiling joists wr oc with 25 ft span. Concern?
Show More
Show Less
Ask Your Own Structural Engineering Question
Answered in 25 minutes by:
10/19/2017
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,971
Experience: Over 30 years of Structural Engineering experience.
Verified

1. Do you have any pictures you can share with me?

2. Your posting says "joist wr oc". I assume "wr" was supposed to be a number?

3. What is the closest city you are near, for actual snow load values?

Ask Your Own Structural Engineering Question
Customer reply replied 8 months ago
24” oc
Twin Bridges CA
Customer reply replied 8 months ago
Was the picture helpful?
Customer reply replied 8 months ago
How about just a courtesy response that my question is being worked, and that you are not a robot?

Sorry for the delay. I am working on your question right now.

Ask Your Own Structural Engineering Question

I’d like to point out that a Professional Engineer’s standard of care typically includes a site visit to assess field conditions and get an overall understanding of the structure. This can obviously not be accomplished through the internet. The information provided here is meant for planning purposes only (general sizing and budgeting) and is based on the information provided by you. All loading cases considered are for vertical loads only, no lateral analysis has been completed. The information should be verified by a professional engineer who can visit the site to ensure that potentially important information has not been overlooked or omitted.

I assumed your beams are Douglas Fir (#2 grade) and they clear span 25' and are spaced at 24" o.c.

With this configuration and just adding a standard minimum roof Live Load of 20 psf and a roof Dead Load of 10 psf, your members are at 255% of the Allowable Bending Stress and are at 522% of the Allowable Total Load Deflection.

Needless to say, they are grossly overstressed at a 25' clear span.

If you were to place a cross beam at midspan, making your roof beams have two 12.5' clear spans, you could just barely carry a Load Load of 40 psf.

Your snow load is significantly higher than that in El Dorado County:

http://edcapps.edcgov.us/building/request_snow_load.asp

If you were to place a cross beam at midspan of your floor beams, making your floor beams have two 12.5' clear spans, you could just barely carry a Load Load of 40 psf, which is the required Floor Live Load in the Building Code.

If you feel you have received a satisfactory answer to your question, please click the Rating button that is appropriate. Experts are credited for each adequately Rated answer they provide. If you have additional questions, please let me know. Thanks

walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,971
Experience: Over 30 years of Structural Engineering experience.
Verified
walkereng and 87 other Structural Engineering Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
Thank you
This is very helpful.

Good Luck with your project!

Ask Your Own Structural Engineering Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a structural engineerLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask walkereng Your Own Question
walkereng
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,971
2,971 Satisfied Customers
Experience: Over 30 years of Structural Engineering experience.

walkereng is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

He answered my question promptly and gave me accurate, detailed information. If all of your experts are half as good, you have a great thing going here.

DianeDallas, TX

< Previous | Next >

Meet the Experts:

walkereng

walkereng

Consultant

2,971 satisfied customers

Over 30 years of Structural Engineering experience.

vgdlpc

vgdlpc

Master's Degree

17 satisfied customers

Civil Engineer, Major in Structures and Foundations. Professional Engineer 11 years of experience.

StructuralEng

StructuralEng

Consultant

6,391 satisfied customers

Structural Engineer

Matt

Matt

Engineer

44 satisfied customers

Mechanical Engineering Hons degree, been working in automotive industry for the last 18 years - Engine development engineer

ibosley

ibosley

Master's Degree

88 satisfied customers

Mechanical Engineering

Ellen

Ellen

Consultant

109 satisfied customers

attorney and legal researcher

P. Simmons

P. Simmons

Attorney

149 satisfied customers

45 years old, retired Marine Officer, current attorney

< Previous | Next >

Related Structural Engineering Questions
I'd like to add 4 sliding doors 16' wide by 10' high on the
I'd like to add 4 sliding doors 16' wide by 10' high on the first floor of a townhouse. I also have an opening at the lower level already but it has two beams. I would like to see if there is a way I … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I have a 23' foot span in my basement that presently has 1,
I have a 23' foot span in my basement that presently has 1, 5 1/8 square post for center bearing on a 5 1/8 x 10 1/2 glulam. Only floor load above, since roof is clear span exterior plate to plate. Wh… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I have a room in my home 27' divided in half by a wall. The
I have a room in my home 27' long divided in half by a wall. The roof has trusses perpendicular to the wall, how can I find out if I need to add a beam when I remove the wall and if a beam is needed h… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
We are looking at buying a condo that does not have
Hello, we are looking at buying a condo that does not have electrical junction boxes in the ceiling for overhead lights. The ceiling is concrete. The developer says that they cannot drill to install j… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I have a two story home. 30'x 50' overall. I want one large
Hi. I have a two story home. 30'x 50' overall. I want one large room front to back on one side of the house so I need a wood beam to span unsupported for 20'. this is on the first floor so it needs to… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I have all 4 measurements of a field in feet for each side.
I have all 4 measurements of a field in feet for each side. It is not quite a square area. Consider an area that is not quite square. One side is 570 ft. (length) 2nd side is 712 ft. (width) 3rd side … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I want to eliminate th first support pole in my basement in
I want to eliminate th first support pole in my basement in my ranch style house. I currently have 3 2”x10” beam. With poles every 10'. I would like Two answers. … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I need to place 3500# 4 x 8 pallets on a flat roof that has
I need to place 3500# ***** x 8 pallets on a flat roof that has a 25# ***** dead load limit … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I am going to rebuild the patio cover. The cover will be 4x8
I am going to rebuild the patio cover. The cover will be 4x8 5' on center with 2x4 spaced 4" apart. The posts are going to be 6x6. My question is will a 6x12 be sufficient between the two posts 18' ce… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I've got four metal roof trusses that are bent due to
I've got four metal roof trusses that are bent due to material falling on the flat roof. is it acceptable to attach angle iron over the bent areas? … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I want to relocated my bedroom egress window to open into a
I want to relocated my bedroom egress window to open into a covered entryway. Does California Building Code allow opening onto a roofed area?… read more
walkereng
walkereng
Consultant
2,971 satisfied customers
I am building a sunroom attached to my home. 12' by 20' in
I am building a sunroom attached to my home. 12' by 20' in northern Indiana. I would like to have a cathedral ceiling using rafter hangers and a ridge beam spanning the 20' length. What size lvl shoul… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
Plumber hammered his way through our slab to find a cable
Plumber jack hammered his way through our slab to find a cable that had been pulled apart. What remedy do we have … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
What's size beam would I need to Span 65 ft no load. It's
What's size wood beam would I need to Span 65 ft no load … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I'm in the process of finalizing plans for building my own
Hello!I'm in the process of finalizing plans for building my own home in the Baltimore area. The plans were designed by a European architect for a relatively green building in a cold climate. The desi… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
I want to build a retaining wall in my backyard to make the
I want to build a retaining wall in my backyard to make the yard level. I was considering using used power poles that I can get for free. The yard has an uneven grade that goes down into a conservatio… read more
walkereng
walkereng
Consultant
2,971 satisfied customers
Just looking for advise on how to remove a load bearing
Hi, just looking for advise on how to remove a load bearing corner (where two the the exterior walls meet) to make room for an extension.. I have structural plans to remove this corner and replace wit… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
Alum i beam size center point load 2000lb load 20 ft span.
alum i beam size center point load 2000lb load 20 ft span … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,391 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x