Hi I am designing a roof for an addition on an old building. I would like to save a part of the old roof system.

Tutor's Assistant: OK. Got it. You've come to the right place. Tell me a bit more about what's going on so we can help you best.

The snow load requirement is large. It's 387 psf. the roof in question was built with TJI's 16" deep 24" OC. the rafters are running a 9'6" span 8/12 slope making the rafters 11'5 long. Total roof area = 171 sq ft. would this roof meet the required snow load rating?

Tutor's Assistant: Is there anything else the Structural Engineer should be aware of?

I think thats enough info

Submitted: 1 year ago.Category: Structural Engineering
Show More
Show Less
Ask Your Own Structural Engineering Question
Answered in 5 minutes by:
3/29/2017
Structural Engineer: StructuralEng, Consultant replied 1 year ago
StructuralEng
StructuralEng, Consultant
Category: Structural Engineering
Satisfied Customers: 7,761
Experience: Structural Engineer
Verified
Hello
Ask Your Own Structural Engineering Question
Structural Engineer: StructuralEng, Consultant replied 1 year ago
387 psf? That can't be correct?
Ask Your Own Structural Engineering Question
Structural Engineer: StructuralEng, Consultant replied 1 year ago
That's 10' depth of snow
Ask Your Own Structural Engineering Question
Structural Engineer: StructuralEng, Consultant replied 1 year ago
Which 16" TJI? There are different classes? 230? 530?
Ask Your Own Structural Engineering Question
Customer reply replied 1 year ago
387 psf is correct. Not sure on the TJI class let's assume the strongest one untill I can get more info.I'm a contractor in the area. I have aprox. 15' of snow in my yard. The requirement is for 100% of the ground snow load. I'm told in most other areas they use a percentage.
Structural Engineer: StructuralEng, Consultant replied 1 year ago
Wow!
Ask Your Own Structural Engineering Question
Structural Engineer: StructuralEng, Consultant replied 1 year ago
Ok. Give me a few minutes to run numbers.
Ask Your Own Structural Engineering Question
Structural Engineer: StructuralEng, Consultant replied 1 year ago
It does check out for 16" TJI 560. No other one is close for 16" depth.
Ask Your Own Structural Engineering Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a structural engineerLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask StructuralEng Your Own Question
StructuralEng
StructuralEng
StructuralEng, Consultant
Category: Structural Engineering
Satisfied Customers: 7,761
7,761 Satisfied Customers
Experience: Structural Engineer

StructuralEng is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

He answered my question promptly and gave me accurate, detailed information. If all of your experts are half as good, you have a great thing going here.

DianeDallas, TX

< Previous | Next >

Meet the Experts:

walkereng

walkereng

Consultant

2,769 satisfied customers

Over 30 years of Structural Engineering experience.

vgdlpc

vgdlpc

Master's Degree

17 satisfied customers

Civil Engineer, Major in Structures and Foundations. Professional Engineer 11 years of experience.

StructuralEng

StructuralEng

Consultant

7,761 satisfied customers

Structural Engineer

Matt

Matt

Engineer

46 satisfied customers

Mechanical Engineering Hons degree, been working in automotive industry for the last 18 years - Engine development engineer

ibosley

ibosley

Master's Degree

88 satisfied customers

Mechanical Engineering

Ellen

Ellen

Consultant

109 satisfied customers

attorney and legal researcher

P. Simmons

P. Simmons

Attorney

150 satisfied customers

45 years old, retired Marine Officer, current attorney

< Previous | Next >

Related Structural Engineering Questions
I want to take out a 15 ft section of a wall that picks up a
I want to take out a 15 ft section of a wall that picks up a single story roof span that is 2x4 rafters 24 oc the rafters are 18ft long from ridge down to outer wall plate , id ;like to flush a beam i… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I am looking to size a steel beam for residential framing in
Hello, I am looking to size a steel beam for residential framing in Montville NJ 07045. The joists on each side of the beam is around 19 ft. It is a two story structure, and will be supporting a roof … read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
For a snow load on a roof, how many pounds per square inch
For a snow load on a roof, how many pounds per square inch required for snow up to 18 inches … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I need to calculate the size of Steel I beam required to
Hello. I need to calculate the size of Steel I beam required to support 100lbs per lin ft uniform load. my clear span will be 35'… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
Trying to figure out the best way to remove a center post in
trying to figure out the best way to remove a center post in my sons garage, the structure is 22 feet wide, the roof slopes to all 4 sides. currently there is a metal post under the rafters in the cen… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I am raising a section of roof to give more ceiling
I am raising a section of roof to give more ceiling clearance in the room below. The size is 16' x 16' and the ends are supported with a clearspan double 1 3/4" x 12" glue lam on one side which is exi… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I have a building over 100 years old its brick exterior walls.
I have a building over 100 years old its brick exterior walls. first floor beam is metal second floor beam is metal 2 I beams bolted together. The beam holding up the roof is a 5 ply 2x13 1/4 nailed .… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I have a 24 ' wide building; 8/12 pitch; I am in snow country;
I have a 24 ' wide building; 8/12 pitch; I am in snow country; design snow loads are 100#/sq. ft.. I would like to install a glu- lam ridge beam and one glu-lam purlin /side. End bearing points are 20… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
Require minimum size W beam to support 60 lbs/sq.ft live load
Require minimum size W beam to support 60 lbs/sq.ft live load plus 10 lbs/sq.ft dead load ( total design of 70 lbs. sq.ft.) over a span of 48 feet with one support at 24 feet. Beam will be used to sup… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
Greetings, Im designing an addition along the back (long)
Greetings, I'm designing an addition along the back (long) side of a ranch with two gable roof systems offset slightly (gables on sides, not back). Because the garage and former breezeway part of the … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
Hello. Im building a garage with an apartment over it and
Hello. I'm building a garage with an apartment over it and would like to know what size steel I-beam I'd need to clear span (no columns) it. It is a 38'x38' box. I am not planning on having much (if a… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
I am considering engineered I beams as rafters for an apartment
I am considering engineered I beams as rafters for an apartment garage project. The horizontal distance is 14 ft, the pitch is 12X12, the overall rafter length from ridge to knee wall is just under 20… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
I am going to be building a modular home in wv as soon as i
I am going to be building a modular home in wv as soon as i can sell my house in md. the building code in WV for snow load is 40psf. My roof is a 5/12 pitch with a flat ceiling. I am 70 years old and … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
10x10 posts (hard maple-oak-hickery) 12ft. 7in oc/ beams/to
10x10 posts (hard maple-oak-hickery) 12ft. 7in oc/ beams/to support rafters 32in. oc (4x 8) same wi'oods covered with 2x6 boards same woods load 185lbs per sq ft i,m real slow on a computer is my ques… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
My situation: I am building a lean to addition to my barn.
My situation: I am building a lean to addition to my barn. The lenth will be 16 feet, the width 12 feet and the rafters , at a 4/12 pitch 14 feet. One side is attached to the barn, the other will be o… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
I am constructing a timber outbuilding with a shed roof that
I am constructing a timber outbuilding with a shed roof that is cantilevered towards the peak. The main beam will support about 600 sq ft, I am keeping it a free span of 30' with no interior posts, th… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,761 satisfied customers
If I use selection tables to design my entire garage, will
If I use selection tables to design my entire garage, will I need to determine the allowable bearing pressure dirrectly under the footing and make sure its lower then the allowable bearing pressure of… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
We want to span a 22 ft opening using a pine timber. The beam
We want to span a 22 ft opening using a pine timber. The beam will support a shed style roof with 2x8 rafters, 2x4 strapping and metal roofing. What size beam should we need?… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,769 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.