Replace 2X4 load bearing basement wall.Open span of 22.5 feet. house width is 26 feet. Beam will support upper floor and roof. Standard shingle roof. 84 lumber says four 1.75 X 14 inch versa-lam panels mated together. I would prefer to use a 8 or 10 inch I-beam with the correct post/column at each end with proper concrete footings. Existing floor joist will be attached mechanically with curtis joist hangers. What are the proper 8 or 10 inch I-beam and column/post sizes.
Show More
Show Less
Ask Your Own Structural Engineering Question
Answered in 2 minutes by:
1/26/2012
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,852
Experience: Over 30 years of Structural Engineering experience.
Verified

walkereng :

I can help.

walkereng :

I have attached a file. Can you take a look at it and answer the questions at the bottom? This will help me answer your question.

walkereng :

I am on the East Coast, so it is getting close to 1:00 a.m., can you work up your answers to my questions and I can finish this up in the morning?

walkereng :

I will switch over to the Q&A format and the system will send you an e-mail. When you are ready to reply, just check your e-mail and reply to the latest one you get. You information will come back to me in an e-mail. Talk to you in the morning. Thanks

Ask Your Own Structural Engineering Question
Customer reply replied 5 years ago

1. basement beam, span 22.5 feet. No post or column in middle, support at ends only.

2. The floor floor joists span is 26 feet, the widith of the house. They extend two feet over the cinder block basement walls.

3. Roof tresses are factory made. Not sure about the load distribution. The hallway wall on the upper floor is directley above the basement wall we want to remove. I would guess and say it does carry some of the roof load.

4. Pasadena, Maryland

5. Asphalt shingles

6. 2 story basement, upper floor,roof.

I really need to try and find out if any roof load or wall load is coming down from the 2nd floor and roof. This will make a huge difference in the beam size. If you have factory built trusses, they are generally designed to span from exterior wall to exterior wall without any intermediate support. You have a hallway on the 2nd floor above the basement wall, but do you also have a 1st floor wall above the basement wall? If I run the loading case with just 40 psf Live Load and 10 psf Dead Load only on the 1st floor, I get the same size quadruple laminated beam that was sized at 84 Lumber. If I add in 2nd floor load and roof load those laminated members do not work at all for the 22.5' span.

Can you look up in the attic to investigate the possible connections between the bottom chord of your trusses and the top of the 2nd floor hallway walls? Can you see if there are any vertical truss members right above the 2nd floor walls? Or maybe you can send me a picture or two from the trusses in the attic. Attach them with the paperclip in the toolbar of the chat window.
Ask Your Own Structural Engineering Question
Customer reply replied 5 years ago
The house is only two levels basement and 1st floor.I have my son looking in the attic now. The tresses have the metal mending plates and are made out of 2X4 stock. The vertical supports do not align over top of any walls. The live load and dead load psf are exactly what the 84 lumber engineer used in his calulations.
You can use a W10x30 steel beam (50 ksi). This beam is 5.75" wide, 10.5" deep and weighs 30 pounds per linear foot.

You will need to have a solid mechanical connection between the floor joists and the top flange of the steel beam, for lateral support.

You can use a 30"x30" concrete footing that is 12" thick. Place 5 - #4 rebar in each direction, 3" up from the bottom of the footing.

You can use a Std. weight 3" diameter steel column A501 or A53 Grade B for your supports.
Ask Your Own Structural Engineering Question
Customer reply replied 5 years ago

Is there any way we can use a W8 beam with the 50ksi? When we lay out the footings for the support posts do the posts need to be in the center? One end of beam will be next to the cynder block wall, so to be centered we would need the new footing to be tied into the existing foundation footing? At the other end the post will be next to an existing king stud, should we excavate under the existing concrete floor to get the footing centered next to the king stud? Can the footings be dug down deeper to reduce the size?

You could use a W8x40 steel beam (50 ksi). This beam is 8.125" wide, 8.25" deep and weighs 40 pounds per linear foot.

The center of the steel column posts can be 15" in from your the ends without a problem. That will make the post in the center of the new footings.
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,852
Experience: Over 30 years of Structural Engineering experience.
Verified
walkereng and 87 other Structural Engineering Specialists are ready to help you
Ask your own question now
Customer reply replied 5 years ago
We want to know if we could use a 12 inch diameter 4 foot tall concrete cason instead of the 30X30X12 inch footing.
Without a soil report, I do not recommend it.

The 12" diameter caisson end has an area of 113 square inches.
The 30" x 30" footing has an area of 900 square inches.
That is 8 time more bearing area than the caisson.

Piles/Caissons depend on end bearing and also skin friction. I do not feel you will be able to develop enough skin friction to equal the extra bearing resistance you will need.

The only way I could tell, would be if you had an actual soil investigation that gave me the design parameters based on the actual soil you have onside.
Ask Your Own Structural Engineering Question
Ask walkereng Your Own Question
walkereng
walkereng
walkereng, Consultant
Category: Structural Engineering
Satisfied Customers: 2,852
2,852 Satisfied Customers
Experience: Over 30 years of Structural Engineering experience.

walkereng is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

He answered my question promptly and gave me accurate, detailed information. If all of your experts are half as good, you have a great thing going here.

DianeDallas, TX

< Previous | Next >

Meet the Experts:

walkereng

walkereng

Consultant

2,852 satisfied customers

Over 30 years of Structural Engineering experience.

vgdlpc

vgdlpc

Master's Degree

17 satisfied customers

Civil Engineer, Major in Structures and Foundations. Professional Engineer 11 years of experience.

StructuralEng

StructuralEng

Consultant

6,064 satisfied customers

Structural Engineer

Matt

Matt

Engineer

40 satisfied customers

Mechanical Engineering Hons degree, been working in automotive industry for the last 18 years - Engine development engineer

ibosley

ibosley

Master's Degree

88 satisfied customers

Mechanical Engineering

Ellen

Ellen

Consultant

109 satisfied customers

attorney and legal researcher

P. Simmons

P. Simmons

Attorney

138 satisfied customers

45 years old, retired Marine Officer, current attorney

< Previous | Next >

Related Structural Engineering Questions
I am building a garage that is 16 1/2' wide and 24' 10" deep
I am building a garage that is 16 1/2' wide and 24' 10" deep with a 3/12 pitch roof. I want to put a ridge beam in that would span the 16 1/2' and support the rafters. I need to know what size of beam… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
I have a 4” x 4” I-beam to span a 38' space. There will be a
I have a 4” x 4” I-beam to span a 38' space. There will be a 4,000 lb total load hanging from the I-beam at four evenly spaced points. What size and how many posts would I need to support the I-beam? … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
I am restoring an old home near Mena Arkansas. It's a 2
I am restoring an old home near Mena Arkansas. It's a 2 story with low ceilings due to duct work added for central A/C. I would like to remove a 22 ft span of 2nd floor and create an open space betwee… read more
walkereng
walkereng
Consultant
2,852 satisfied customers
The slab for my basement was poured a couple weeks ago.
Hello! The slab for my basement was poured a couple weeks ago. Yesterday I notice a crack (vertical) at the edge of the slab. Only vertically. There is no cracking on the slab surface. See pics and pl… read more
walkereng
walkereng
Consultant
2,852 satisfied customers
I'm attempting to remove a wall in my bathroom and I found a
I'm attempting to remove a wall in my bathroom and I found a 4x4 stud in one corner. I'm trying to determine if it is load bearing or not. … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
Are you allowed to cut studs on the outside and install pvc
Are you allowed to cut studs on the outside and install pvc plumbing?? I feel cutting 2 inches into a stud is wrong?… read more
walkereng
walkereng
Consultant
2,852 satisfied customers
I plan on removing a portion of a load bearing wall in my
Hi. I plan on removing a portion of a load bearing wall in my house and replacing it with steel i-beam. I need assistance in determining the beam size required and support post placement. The room spa… read more
walkereng
walkereng
Consultant
2,852 satisfied customers
Calculation for a glue Lam Beam and a house I have four
Calculation for a glue Lam Beam and a house I have four locations one I need is a 16 foot span supporting were the two static Joyce come together in the middle of the house nothing above it but attic … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
I am trying to find out how much weight (PSI) - load bearing
I am trying to find out how much weight (PSI) - load bearing that a 4'x4'x1/2" piece of plywood would hold. We use 4"x4" sheets of 3/4" normally to cover excavated holes up to 3' diameter. Someone sug… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
Size of a glue lam beam span 14" lenght of room 23" feet.
size of a glue lam beam span 14" lenght of room 23" feet. the beam will be supporting a 2nd floor room plus roof? … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
What I-beam size would I need for a span of 16 feet.
What I-beam size would I need for a span of 16 feet … read more
walkereng
walkereng
Consultant
2,852 satisfied customers
I need to calculate a steel and stainless steel rectangular
Hi There, I need to calculate a steel and stainless steel rectangular beam. The span is 102". The dead load is approximately 280lbs and the approximate live load will likely not be more than 600lbs. … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
My garage currently is a one story garage attached to a two
My garage currently is a one story garage attached to a two story house. I am going to convert my attic above my garage to living space. The trusses that are currently intalled does not allow that. Wh… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
The slab for my basement was poured a couple weeks ago.
Hello! The slab for my basement was poured a couple weeks ago. Yesterday I notice a crack (vertical) at the edge of the slab. Only vertically. There is no cracking on the slab surface. See pics and pl… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
I am designing a 25' wide x 27' deep garage with a second
I am designing a 25' wide x 27' deep garage with a second story bedroom above. There will be an integral 27'-9"x 10" deep steel beam " A " at the halfway point of the 25' span width of the garage.One … read more
walkereng
walkereng
Consultant
2,852 satisfied customers
I have a condo/loft. Need to cut about 3-4 feet by 3 foot
I have a condo/loft. Need to cut about 3-4 feet by 3 foot while through the edge of the second floor that looks over the 1st floor. The floor is concrete. I have pictures to reference. … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
I was wondering how much force would the edge of 3/4"
Hello I was wondering how much force would the edge of 3/4" treated plywood be able to with stand before it would de-laminate? … read more
matt50025002
matt50025002
Owner of a waste management company
Master\u0027s Degree
118 satisfied customers
I want to remove the wall between my livingroom and kitchen
I want to remove the wall between my livingroom and kitchen and need to know what size beam i am going to need to support the load.The beam is going to be 14.5 feet long, it is on the 1st floor of a 2… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
6,064 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x