Structural Engineering

Ask Structural Engineering Questions and Get Expert Answers ASAP

Ask an Expert,
Get an Answer ASAP!

I need to calculate the load-bearing capacity of a steel…

Customer Question
I need to calculate the...
I need to calculate the load-bearing capacity of a steel I-Beam 6"x6"x1/4", 13'-6" long supported by 9" masonry on each side
Submitted: 6 years ago.Category: Structural Engineering
Show More
Show Less
Ask Your Own Structural Engineering Question
Answered in 5 minutes by:
12/28/2011
Structural Engineer: StructuralEng, Consultant replied 6 years ago
StructuralEng
StructuralEng, Consultant
Category: Structural Engineering
Satisfied Customers: 7,716
Experience: Structural Engineer
Verified
StructuralEng : Hi
StructuralEng : I can help with this
Customer:

Thanks

StructuralEng : The max uniform load or max point load?
StructuralEng : What grade of steel?
Customer:

Uniform load

Customer:

I know it varies with the grade of steel. This is not a load-bearing beam, just a garage door opening in a masonry wall. What do you suggest?

Customer:

Zoning wants to know.

StructuralEng : Te only load on it will be CMU in the wall? The wall is not load bearing?
Customer:

No load. The roof trusses are 13'-6" apart. This is a one story structure.

Customer:

Putting in a 12' door.

StructuralEng : No load other than the CMU, right?
Customer:

What is CMU?

StructuralEng : What is the height of the CMU above the opening? What is the thickness of the CMU?
StructuralEng : Concrete masonry unit
Customer:

Less that 1'. Maybe 10".

StructuralEng : Really? An you're getting questioned about a beam size? Give me a few minutes to run some numbers
Customer:

PIA zoning guy.

StructuralEng :

You can use a W5x16 or a W6x12. The first number is ***** depth in inches and the second number is ***** weight of the beam in pounds per foot. Depending on the thickness of the masonry, you might need something bigger just to provide a wide enough bearing surface for the masonry.

StructuralEng :

How thick is the masonry.

StructuralEng :

If you've found my answer helpful, please click the green "accept" button. I'll be happy to answer additional questions on the topic. If you could provide feedback, I would appreciate it.

Customer:

The masonry is about 8" thick I think. Not sure, but I'll stay with that. What kind of load-bearing capacity does that W6x12?

StructuralEng :

The W6x12 can take much more from a strength standpoint. Deflection is controlling the design. ACI 530 requires beams that support unreinforced masonry to be designed for a deflection limit of L/600, which in your case is 1/4"

StructuralEng :

It's only at approximately 50% of the beam capacity from a strength standpoint.

StructuralEng :

The last comment I would have is to make sure the bearing condition is detailed properly to ensure overall stability.

Customer:

Nice and flat, I take it. Do I bolt it down?

StructuralEng :

You can also use a steel tube 7x4x3/8 laid flat. This will give you a nice 7" flat surface to bear the masonry on.

Customer:

Box tube, right?

StructuralEng :

The bearing detail will depend somewhat on what is supporting it, but you'll want it bolted at both ends, but one end needs to be able to move (for thermal expansion and contraction) so you'll want that properly detailed. Also, you'll want full depth stiffeners. And you need to make sure that the masonry is grouted properly at the bearing locations.

Customer:

Thank you for your help. Slot those holes.

StructuralEng :

Correct, the HSS is a steel tube 7" x 4" with a 3/8" thick wall.

Customer:

Thanks again.

StructuralEng
StructuralEng, Consultant
Category: Structural Engineering
Satisfied Customers: 7,716
Experience: Structural Engineer
Verified
StructuralEng and 87 other Structural Engineering Specialists are ready to help you
Ask your own question now
Structural Engineer: StructuralEng, Consultant replied 6 years ago
No problem. Best of luck with your project.
Ask Your Own Structural Engineering Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a structural engineerLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask StructuralEng Your Own Question
StructuralEng
StructuralEng
StructuralEng, Consultant
Category: Structural Engineering
Satisfied Customers: 7,716
7,716 Satisfied Customers
Experience: Structural Engineer

StructuralEng is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

He answered my question promptly and gave me accurate, detailed information. If all of your experts are half as good, you have a great thing going here.

DianeDallas, TX

< Previous | Next >

Meet the Experts:

walkereng

walkereng

Consultant

2,733 satisfied customers

Over 30 years of Structural Engineering experience.

vgdlpc

vgdlpc

Master's Degree

17 satisfied customers

Civil Engineer, Major in Structures and Foundations. Professional Engineer 11 years of experience.

StructuralEng

StructuralEng

Consultant

7,716 satisfied customers

Structural Engineer

Matt

Matt

Engineer

45 satisfied customers

Mechanical Engineering Hons degree, been working in automotive industry for the last 18 years - Engine development engineer

ibosley

ibosley

Master's Degree

88 satisfied customers

Mechanical Engineering

Ellen

Ellen

Consultant

109 satisfied customers

attorney and legal researcher

P. Simmons

P. Simmons

Attorney

149 satisfied customers

45 years old, retired Marine Officer, current attorney

< Previous | Next >

Related Structural Engineering Questions
What size angle iron (steel lentil) do I need to support a
What size angle iron (steel lentil) do I need to support a brick opening 10' wide with 1 story above. It's a non load bearing wall. … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
My house is 28 ft x 60 ft. Near the center of house is a
My house is 28 ft x 60 ft long. Near the center of house is a kitchen that is 12ftx16ft, with a load bearing wall between it and living room. The living room is 16ft x 16 ft. Between the two rooms is … read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
Need a wide flange steel beam sized for a 16' opening for a
Need a wide flange steel beam sized for a 16' opening for a sliding glass door. The opening supports only a roof load only (cathedral ceiling 4/12 roof pitch) of a single story house of a room that is… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
If I take an 18 inch steel I beam - split it lengthwise (ie:
If I take an 18 inch steel I beam - split it lengthwise (ie: two 9 inch wide - long T's) - then bolt or weld the two pieces together....do they have the same approximately load bearing capacity? My 18… read more
Peter Lavallee
Peter Lavallee
Principal Engineer
Masters of Civil Engineering
2 satisfied customers
From NY. just moving in to a -level ranch home. I would like
Hello my name is ***** ***** NY. just moving in to a bi-level ranch home. I would like to have cathedral ceiling only in the living room space, roughly the house is 28'wideX50'long 4/12 roof pitch. I … read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
I am renovating an older home that has a flat roof framed
I am renovating an older home that has a flat roof framed with 2 x 8's 16" on center supporting the roof structure. Roof is plywood with a foam roof on top so the static load is very low. I have a 20'… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
I need to size a beam to replace a bearing wall. the opening
I need to size a beam to replace a bearing wall. the opening will be 9'6". The beam will carry joists coming in from both sides, 16"o.c., uniform load. Span on both sides is about 14 ft. There are par… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
My 2-storey house has a stairwell opening that is 3ft x 7ft
My 2-storey house has a stairwell opening that is 3ft x 7ft 8in. One long side is on a 2x6 bearing wall on a spread footing. The short sides are double 2x10 continuous floor joists. The other long sid… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
What size steel beam ( with 3/8" steel plate) 10 feet garage
what size steel beam ( with 3/8" steel plate) for a 10 feet garage door opening with 6 to 8 feet of 12 " masonry above… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
I need to design a steel lintel spanning a 6'4" masonry opening.
I need to design a steel lintel spanning a 6'4" masonry opening. Wall construction is 8" CMU with common brick veneer. This is a one story building. The masonry above the opening to the roof is 13'. T… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
I was trying to calculate load bearing capacity of a rectangular steel structure with I be
I was trying to calculate load bearing capacity of a rectangular steel structure with I beams. The structure is 18 ft wide and 20 ft long and 78 inches high. The 6 inch beams are on 4 ft centers and t… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
Part of my house is supported by a beam consisting of 4 wood
Part of my house is supported by a beam consisting of 4 wood 2x10s nailed together side by side, resting on 8x8 wood posts at each extremity of the beam. The beam spans 16 feet. The posts are on concr… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
I would like to build a western cedar structure with 6"x6"
I would like to build a western cedar structure with 6"x6" or 6"x8" posts and beams. The posts will be 8' tall, the beams will be 15' and 13' long. In the middle of the 13' beam, a 4' 6"x6" post will … read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
I want to support a clear span over 34. The beam must hold
I want to support a clear span over 34'. The beam must hold 2" X 8" on one end which are 13' long. Above this is a bedroom with bath and pitched roof above that. What steam beam will do the job with o… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
Could you explain install two channels C200 x 28 ( flange 2
Could you explain install two channels C200 x 28 ( flange 2 3/8" wide with 4" bearing on solid masonry?… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
Supported length 10 (20/2) snow load 52.2 kpa Clear span
Supported length 10' (20'/2) snow load 52.2 kpa Clear span 20' Dead Masonry load above 1' x 20'… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
I want to remove a first floor load bearing wall, and install
I want to remove a first floor load bearing wall, and install an LVL beam with steel columns. The beam span between columns would be 12', and I plan to use 4 LVL beams bolted together (24" spacing), e… read more
StructuralEng
StructuralEng
Consultant
Bachelor's Degree
7,716 satisfied customers
I want to support a floor that is 24 foot wide by 24 foot long,
I want to support a floor that is 24 foot wide by 24 foot long, with a steel beam running down the center of it underneath. What size beam would I need to bridge the total area? The floor will only be… read more
walkereng
walkereng
Consultant
Bachelor's Degree
2,733 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x