Onan 5.5HDKBA - 35895 diesel generator in an Avalanche

Customer Question
motorhome with Onan Q2000 inverter/charger...
Onan 5.5HDKBA - 35895 diesel generator in an Avalanche motorhome with Onan Q2000 inverter/charger. Everything perfect on shore power but when we go to genset, the transfer switch works, the junction box coming out of the transfer switch shows 119 volts on both hot legs (both to ground and neutral). There are two 120 volt fuse boxes...one appears to be just for the inverted circuits (fridge, microwave and some outlets). The main fuse box shows 119 volts but the inverted box is dead. We are getting an inverter control panel error 15 which resolves to "frequency under 54 hertz". I'll get a multi-meter today that tests frequency and verify but I am also confused about the two legs of the 50 amp generator versus the two fuse boxes and a couple other things...Are the two legs likely being divided so one goes to the main fuse block and the other leg goes to the inverted fuse box?That would indicate the two legs are both going to the inverter/charger?Can you clarify the likely relationship between the two power legs, the inverter/changer and the two fuse boxes?Can the generator produce poor frequency on just one leg?Is the diesel generator constant RPM or should it respond to load regards ***** ***** can low RPM cause low frequency output?Thanks,Bill
Submitted: 2 years ago.Category: Small Engine
Show More
Show Less
Ask Your Own Small Engine Question
Answered in 12 hours by:
10/18/2019
Technician: Hank F., Technician replied 2 years ago
Hank F.
Hank F., Technician
Category: Small Engine
Satisfied Customers: 18,095
Experience: Certified on Onan and Generac generators
Verified

Hello, my name is ***** ***** I am going to assist you with this.

It is not possible to have low frequency on one leg only. Frequency is only affected by engine speed, and would affect both legs equally.

Without seeing how this is wired, it is most likely that one leg feeds the inverter, while the other leg feeds everything else. When no using the inverter, the current is simply passed through the inverter.

The engine will hold a constant speed, but under load it is working harder. The electronic governor makes sure to keep the engine speed constant to keep the frequency constant.

If the genset were only running at 554 Hz, it would be shutting itself down on an Under Speed fault. Since it is not, it is most likely that there is a problem in the inverter itself.

Ask Your Own Small Engine Question
Customer reply replied 2 years ago
But the inverter works perfectly when on shore power.
Technician: Hank F., Technician replied 2 years ago

If you have good voltage on both legs coming out of the transfer switch when on gen power, there is no reason the fuse box does not have power, unless it is stopping at the inverter.

Have you tested the TS output on both shore power and generator?

Ask Your Own Small Engine Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Hank F. Your Own Question
Hank F.
Hank F.
Hank F., Technician
Category: Small Engine
Satisfied Customers: 18,095
18,095 Satisfied Customers
Experience: Certified on Onan and Generac generators

Hank F. is online now

Related Small Engine Questions
Not producing power. Onan 4000 genset. About a month. Tried
about a month. Tried replacing voltage regulator. Getting 16 volts output … read more
Paul Hill
Paul Hill
1,638 satisfied customers
My generato onan 4000 shuts down after disconnecting the
My generato onan 4000 ky shuts down after disconnecting the load for cool down. Sometimes a fault code 14 displays, sometimes there is no code. Can you tell me the steps for checking voltage, frequenc… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Recently changed my spark plugs, solenoid and stepper motor.
Hello. Recently changed my spark plugs, solenoid and stepper motor. My onboard battery is fully charged. The generator starts and runs but is not charging my house. … read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Generac 20kw air cooled generator, Generac guardian, circa
Generac guardian , circa 2012, battery not being charged while unit is running. … read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I want to change a kohler 6.5 cz currently configure as 120
I want to change a kohler 6.5 cz currently configure as 120 v 60 hz output to 240 v 50 hz … read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
New Xantrex 2000 watt sine wave inverter/80 am.p battery
New Xantrex 2000 watt sine wave inverter/80 am.p battery charger trips out regularly on Onan generator when batte.ry charger function is operating. As charger begins to ramp up charging current...star… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have an Onan Diesel 8000 quiet generator in my RV. It
I have an Onan Diesel 8000 quiet generator in my RV. It works find and charges the house batteries fine, but drains the chassis batteries when running. Any thoughts as to what is the issue? … read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have a guardian ultra source portable generator(15kw)
I have a guardian ultra source portable generator(15kw) model:004583-0. The problem that i have is i was connecting the generator to my house and forgot to turn off the main breaker out side of the ho… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have a 7.5kw onan diesel gen, have code 33 replace temp
i have a 7.5kw onan diesel gen, have code 33 replace temp sensor code still there, is it possible that the A1 circuit? board be bad… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have a Yamaha EF3000ISEB Generator that only has 109 volt
I have a Yamaha EF3000ISEB Generator that only has 109 volt out put. At an idle and at high rpm with a load I have about the same voltage. What do you think would be failing?… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I want you Hank i would like ro work with you on my computer
I want you Hank i would like ro work with you on my computer i instead of my cell phone if possible. I think I've read enough that I'll understand what you tell mw to do now.my onan 4000 is code 14.my… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Hi, my onan 3.5 kva on my sailboat does not charge the boat
Hi, my onan 3.5 kva on my sailboat does not charge the boat bateries although it properly powers all the rest of boat's 240 v consumers, such as electric cooker, water heater, plugs, etc. what might b… read more
Charles
Charles
Certified Mercury Tech
5,752 satisfied customers
Our onan genset 6.5 generator in our 99 discovery motorhome
Our onan genset 6.5 generator in our 99 discovery motorhome has a problem> When we run it to charge the house batteries it will run apprx. 10-20 minutes and then start running rough. We replaced al… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have a champion generator. Mod No. C46540, 4000W/3500W. When
I have a champion generator. Mod No. C46540, 4000W/3500W. When I run it to power our home, I must make sure that l1 and l2 power is near the same draw. If I try to run the generator with only draw on … read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Motorhome -2012 Winnebago Adventurer 32H Onan 5500 watt Energy
Motorhome -2012 Winnebago Adventurer 32H Onan 5500 watt Energy Command 30 Parrallex Model ATS501 Mini Power Control System by Precision Circuits, Inc. System will not transfer over power to applicance… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Second level fault code was a 14 Overfrequency Fault (Engine
Three blinks indicated Service Fault code, then Second level fault code was a 14 Overfrequency Fault (Engine governor unable to maintain rated frequency) Can you explain this fault more and how it can… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
I have an RV with a 5.0 Onan Generator, model 5 OBGA 3CR 16004C,
I have an RV with a 5.0 Onan Generator, model 5 OBGA 3CR 16004C, which runs great. Last summer the microwave, air conditioner and 110V plugs quit working. I connected a volt meter to the output of the… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Can I wire in a plug to my RV generator to act as emergency
Can I wire in a plug to my RV generator to act as emergency power to my house? It's an ONAN 8000 Watt quiet diesel. The house has be wired with an emergency panel and plug for use with an external gen… read more
Hank F.
Hank F.
Technician
High School or GED
18,095 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Curtis B.

Curtis B.

Technician

20,427 satisfied customers

have worked on and around most engine models for 35 yrs./Polaris ATV expert

Rick

Rick

Factory Authorized Trainer

4,218 satisfied customers

Outdoor Power Equipment technical trainer since 1990, covering eight states.

Vince O.

Vince O.

Small Engine Technician

3,349 satisfied customers

Over 30 years experience repairing lawn and garden equipment. Chainsaws, mowers,blowers and trimmers

Jon K.

Jon K.

Small Engine Diagnostic Expert

2,995 satisfied customers

Gold certified Stihl tech, Service Manager for a rental/repair shop.Certified in most small engines

James W

James W

Small Engine Troubleshooting Expert

2,989 satisfied customers

7 years as Mechanic & Parts Manager for Brother who has Owned Lawn & Garden Repair shop for 35 years

RUSS

RUSS

SERVICE TECHNICIAN

1,723 satisfied customers

28 YEAR SERVICE TECHNICIAN

roger

roger

Small Engine Technician

390 satisfied customers

23 years of being a shop owner..small engine trade schools

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x