I have a 13kw generac that I have had for 15 years. Today we…

I have a 13kw...

I have a 13kw generac that I have had for 15 years. Today we lost power and the generator started as it was supposed to but never switched over to the power panel. I went outside and the system set light was dimly flashing. I went to the transfer switch and it was showing "A" Utility as ON and "B" Standby as OFF. I turned off the generator and left it on manual, rotated the manual handle until "A" was OFF and "B" was ON. I went back and tried to start the generator and it took a great deal of tries before it finally started but within seconds the Over Speed light came on and the generator stopped. I waited about 2-3 minutes and tried again and the same issue reoccurred. Should I call for service or is there something I can/should do? By the way, the battery is only 2 years old and appears to be providing plenty of power.

Mechanic's Assistant: Do you have fuel in the tank? If so, is the shut-off valve open and the fuel clean?

It is natural gas powered and yes, the valve is on

Mechanic's Assistant: Do you plan on doing the work yourself?

If I can - unless you feel it requires a trained technician.

Mechanic's Assistant: Anything else we should know to help you best?

I get a high frequency of outages - which is why I have the generator. Last week, the power went on and off so many times that the generator got confused and I had to reset it, wait a bit and then powered it up - it worked fine. I had new brushes installed about 3 years ago.

Show More
Show Less
Ask Your Own Small Engine Question
Answered in 7 minutes by:
1/18/2018
Hank F.
Hank F., Technician
Category: Small Engine
Satisfied Customers: 16,006
Experience: Certified on Onan and Generac generators
Verified

Hello, my name is ***** ***** I am going to assist you with this.

What are the model and serial numbers of the genset?

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
Model 04760-0 serial#(###) ###-####

Ok, thanks.

First, you should never attempt to start the genset while the transfer switch is in the generator position. You should always start the genset first, and let it warm up for a minute or so, and then do a manual transfer. Starting a genset under load is a quick way to burn it up.

The system set light flashing like that is strange - it should not be happening.

If the genset is starting, it is not a battery issue, so the problem is deeper inside the genset.

This is going to require some serious troubleshooting.

Do you have a quality multimeter that is capable of reading frequency? One is giong to be required to troubleshoot.

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
Model 04760-0 serial#(###) ###-####
No - can you refer me to a local repair person?

I sure can.

What is your ZIP code?

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
Model 04760-0 serial#(###) ###-####
No - can you refer me to a local repair person?
27803

There are 2 authorized service facilities near you:

ELECTRICAL SERVICES & SOLUTIONS
900 S Church St
Rocky Mount, NC 27803
USA
Distance: 1 Miles
Get Directions(###) ###-####/p>

2
WW ELECTRIC LLC

SIMS, NC 27880
USA
Distance: 20 Miles
Get Directions(###) ###-####/p>

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
Excellent! Thank you Hank. Have a great day. Goodbye.

Not a problem.

Good luck with it.

Thank you for using Just Answer, and please take a moment to rate the quality of my assistance with you today.

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
I easily give you a 5 star rating - I do not see a separate area for rating.

There should be somewhere on your page to select the star rating you wish to give.

Ask Your Own Small Engine Question
Customer reply replied 7 months ago
I don't think you app is working properly. Anything I enter remains on the screen for my next entry. I can only ask that you forward my rating to your manager as there is no screen format allowing me to rate you.

Not a problem. I will forward it to Customer Service.

Thank you again for using Just Answer, and have a great day.

Hank F.
Hank F., Technician
Category: Small Engine
Satisfied Customers: 16,006
Experience: Certified on Onan and Generac generators
Verified
Hank F. and 87 other Small Engine Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Hank F. Your Own Question
Hank F.
Hank F.
Hank F., Technician
Category: Small Engine
Satisfied Customers: 16,006
16,006 Satisfied Customers
Experience: Certified on Onan and Generac generators

Hank F. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Curtis B.

Curtis B.

Technician

15,517 satisfied customers

have worked on and around most engine models for 35 yrs./Polaris ATV expert

Rick

Rick

Factory Authorized Trainer

4,218 satisfied customers

Outdoor Power Equipment technical trainer since 1990, covering eight states.

Jon K.

Jon K.

Small Engine Diagnostic Expert

2,995 satisfied customers

Gold certified Stihl tech, Service Manager for a rental/repair shop.Certified in most small engines

James W

James W

Small Engine Troubleshooting Expert

2,986 satisfied customers

7 years as Mechanic & Parts Manager for Brother who has Owned Lawn & Garden Repair shop for 35 years

Vince O.

Vince O.

Small Engine Technician

2,927 satisfied customers

Over 30 years experience repairing lawn and garden equipment. Chainsaws, mowers,blowers and trimmers

Wayne

Wayne

Engine Rebuilder

2,041 satisfied customers

many years on egine rebuilding, lawn mower,roto tiller,Truck,and small engines

RUSS

RUSS

SERVICE TECHNICIAN

1,723 satisfied customers

28 YEAR SERVICE TECHNICIAN

< Previous | Next >

Related Small Engine Questions
My 22 kW generac is in auto mode and just starts for no
my 22 kW generac is in auto mode and just starts for no reason not in exesize mode … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a Generac 17kW automatic standby generator. Our
I have a Generac 17kW automatic standby generator. Our neighborhood had a brief power outage yesterday. The generator turned on as it was supposed to, but it did not supply AC to our house. I checked … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a generac model # 0046661 13kw generator with
I have a generac model #(###) ###-####13kw generator with flashing red overspeed fault condition . … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I am out of power at my house 40Kw I'm not sure which
I am out of power at my house 40Kw I'm not sure which Generac generator will start manually and will run the house but stops with an over speed light on the generator what does that mean and can I fix… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a Generac Generator that uses a transfer switch that
I have a Generac Generator that uses a transfer switch that is designed to take the output from the generator when there is a power failure and feed some of my household circuits like freezers, furnac… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I just installed a used Generac Guardian 04390-2 which is a
I just installed a used Generac Guardian 04390-2 which is a 13kw unit on Natural gas and 15kw on LP. I am using it on gas. The generator was certified by a generac dealer and I installed a 1" gas line… read more
Curtis B.
Curtis B.
Technician
Associate Degree
15,517 satisfied customers
Our new Generac 22kw started during a half hour outage last
Our new Generac 22kw started during a half hour outage last week, but the load was not transferred until about 30 seconds later. We had a three hour outage this morning and the generator started, but … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a Generac Guardian 43901. It is hardwired to my house.
I have a Generac Guardian 43901. It is hardwired to my house. Over the weekend we had a couple of power outages. During the first outage the generator went on without a problem. It stayed on for about… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
My Generac Guardian 20kW Standby generator was just
My Generac Guardian 20kW Standby generator was just installed after I moved it to a new home. Whenever we (my electrician and I) follow the manual directions, at the end when you switch the generator … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a natural gas generac guardian bought in 2002-in auto
I have a natural gas generac guardian bought in 2002-in auto mode the generator turns on and runs constantly even though the power is not out--what component shoud I look to change?… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a 25kW gas-powered, water-cooled standby Generac generator
I have a 25kW gas-powered, water-cooled standby Generac generator that's about 6 years old. We have never had much need of it for long durations such as those that occured after the hurricanes of 2005… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have installed a generac model 6052 (14kw ) generator with
I have installed a generac model 6052 (14kw ) generator with a 200 amp ATS. The generator runs perfect except it will not reconize the utility side of the switch. When I have the utility power on and … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a used generac standby generator. I has run on propane
I have a used generac standby generator. I has run on propane and I would like to change it to natural gas..I do not have any manuals, and I would like to get them. The generator model # XXXXX XXXXX S… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
I have a Generac 04760-2 generator with a 004945-1, 200 amp
I have a Generac 04760-2 generator with a 004945-1, 200 amp automatic transfer switch. They were installed in the fall of 2005 and have been trouble free. A few days ago, we had a power outage. When t… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
what would cause breaker on 17000 kw generac home standby generator
what would cause breaker on 17000 kw generac home standby generator to be thrown when utility power goes out. generator came on but no house power. had to manually shut generator down. electrical co. … read more
Jon K.
Jon K.
Small Engine Diagnostic Expert
Some College, military training,
2,995 satisfied customers
Dear Hank, I have a 16kw Generac Quietsource Home Standby
Dear Hank, I have a 16kw Generac Quietsource Home Standby Generator with Aluminum enclosure running on Natural Gas. It was working flawlessly until we had two back to back power outages. During the fi… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
Have completed installation of Generac 10KW Gaurdian Series
Have completed installation of Generac 10KW Gaurdian Series generator and Generac 50A ATS. While performing operational tests after installation, manual generator operation is satisfactory, unit runs … read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
Both my neighbor & I installed an 8KW Guardian generator 3
Both my neighbor & I installed an 8KW Guardian generator 3 weeks ago My neighbor experienced an overspeed alarm after the initial installation three weeks ago. On his automatic weekly start last satur… read more
Hank F.
Hank F.
Technician
High School or GED
16,006 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.