I am using a takagi th-3 -p heater as a heat source for a…

Customer Question
I am using a...

I am using a takagi th-3 -p heater as a heat source for a radiant system. it is not heating, keeps shutting down.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I have a loop with a circulator and 3 radiant zones off the loop

Contractor's Assistant: Do you plan on doing the work yourself?

The flow is at 2.4 gal I am a heating installer. All three zones are calling for heat, all circulators are on. Why is the flow rate not higher? And why does it keep going to stand by?

Contractor's Assistant: Anything else we should know to help you best?

As long as flow is going through the th-3, shouldn't it be firing off?

Submitted: 7 months ago.Category: Plumbing
Show More
Show Less
Ask Your Own Plumbing Question
Answered in 5 hours by:
12/3/2017
Plumber: Phil, Mechanical Engineer. replied 7 months ago
Phil
Phil, Mechanical Engineer.
Category: Plumbing
Satisfied Customers: 9,695
Experience: Retired mech. contractor, shop owner, 51 yrs experience.
Verified

Hello, if there is any air trapped (at the high points of the hot water loop or inside the floor coils) the system will be 'vapor locked' and not flow any water through the boiler and the boiler will go off when its high limit switch trips.

Venting the air is step number one.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

Ask Your Own Plumbing Question
Customer reply replied 7 months ago
I am a heating professional, the obvious is not what I am having issues with. The heat source is a Takagi h-3 lp radiant heat unit. It is limiting the flow rate (which is what fires it off) in the circulation loop. When fist pluged in it runs at 1.9 gpm and decreses til it is under the required limit for ignition of .4 gpm. once the unit cycles once and shuts down it does not reignite even if flow rate is above the required .4 gpm
Plumber: Phil, Mechanical Engineer. replied 7 months ago

Thanks, ***** ***** thing we need to be sure of is that the differential on the flow switch is not to wide ... for instance, trips off at 0.4 gpm and does not come on until 1 gpm or whatever... you can test that by fitting a jumper across the flow switch for a few seconds only.... in order to see if bypassing the flow switch allows the boiler to fire or not.

If the boiler then fires we know it went off on the flow switch and the differential was too wide or the flow switch was sticking...

.

IF however the boiler does not fire then it is is quite likely that at low flow rates the boiler trips its high temperature cut out switch, will not reset unless you cycle power to the boiler to reset it. wait 10 or 20 minutes for the boiler to cool before attempting the soft reset.

Let me know how all that goes, we can proceed from there without any time limits

Ask Your Own Plumbing Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a plumberLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer.
Category: Plumbing
Satisfied Customers: 9,695
9,695 Satisfied Customers
Experience: Retired mech. contractor, shop owner, 51 yrs experience.

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Marc

Marc

Plumber

1,127 satisfied customers

Plumbing heating & home maintenance contractor

Jerry

Jerry

Plumber

786 satisfied customers

over 20 years residential plumbing experience.

Theplumber717

Theplumber717

Plumber, Hvac Tech

656 satisfied customers

Lic Plumbing contractor, 28/yrs res,com,repair,Universal HVAC Tech

Phil

Phil

Mechanical Engineer.

9,695 satisfied customers

Retired mech. contractor, shop owner, 51 yrs experience.

Mario

Mario

Master Plumber

604 satisfied customers

Master Plumber, Fire Sprinkler, and Jobbing Spec.

Bud

Bud

Plumber

538 satisfied customers

22 Years Field Experience - 17 Years Business Ownership - Residential or Light Commercial

Rick Mather

Rick Mather

Building Inspector

498 satisfied customers

Assistant Building Official, HVAC Tech

< Previous | Next >

Related Plumbing Questions
Rick, Didn't seem to work. For the past hour and the gauge
Rick, Didn't seem to work. For the past hour and the gauge on the boiler you showing 35 PSI higher than he was beforeb by 15psi. Virgin was finished temperature was a 60 fahrenheit in pressure was a 1… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have radiant heat using a elec on demand is working fine
I have radiant heat using a elec on demand is working fine but added another zone and now not enough flow. Is it possible to add a small water heater to help with volume for flow. My name is zane … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,701 satisfied customers
I have an E110CN that has been in service for DHW for about
I have an E110CN that has been in service for DHW for about 2 months and has been working fine. Just finishing installation for Central Heating and have commissioned for startup. Have Taco ZVC404 conn… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a navien tankless water heater and i cannot get
I have a navien tankless water heater and i cannot get steady hot water out of it. when i look in through the little window there is a sensor or igniter that has too loops that glow red. one of them a… read more
Hauserplb
Hauserplb
Associate Degree
142 satisfied customers
Plumbing: can I tap into a 1/2" sink water line to feed a
Plumbing: can I tap into a 1/2" sink water line to feed a takagi water heater that will be feeding under floor radiant heating for a garage and one rarely used sink. The water heater will be located 4… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Need help with munchkin boiler I have a 6 zone hydronic
Need help with munchkin boilerI have a 6 zone hydronic system with dhw - radiators, baseboards, an air handler, and a single radiant zone. I am adding a seventh radiant zone for a small bath - maybe 2… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rinnai REU-V2532 with S/N 0403 103507 installed to provide
Rinnai REU-V2532 with S/N 0403 103507 installed to provide domestic hot water and hot water for heating loop. Have had intermittent problem when the unit automatically produces hot water for heating l… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Using a Bosch tankless water heater. Just installed radiant
Using a Bosch tankless water heater. Just installed radiant heat in the house and it is powered by the tankless water heater (in addition to providing hot water). It works fine for regular use, but wh… read more
Paul the Plumber
Paul the Plumber
Vocational, Technical or Trade Scho
21 satisfied customers
I have quiteside dual purpose heater 180btu. It not heating
I have quiteside dual purpose heater 180btu. It not heating rooms above 62 degrees. Whats causing this. Pipe to unit is 3/4. Please helpx It keeps cycling from burn to not burn. No error msg displayed… read more
qwasert
qwasert
Residential Journeyman Plumber
Vocational, Technical or Trade Scho
8 satisfied customers
Have a Rinnai 2424c instantaneous WH that was advertised as
Have a Rinnai 2424c instantaneous WH that was advertised as capable to provide both radiant and HW heat. Rinnai now says that they don't recommend using it for radiant, instead they recommend a wall h… read more
WTRHTRPRO
WTRHTRPRO
92 satisfied customers
I am going to place a 40 gal hw tank with no other power source
I am going to place a 40 gal hw tank with no other power source close by with the bottom of tank equal to the top of my wood stove to have a thermosyphen off of the stove. the water comming from my we… read more
cruzmark
cruzmark
Foreman
Vocational, Technical or Trade Scho
I have a knight high efficiency boiler with baseboard radiation.
I have a knight high efficiency boiler with baseboard radiation. I want to add a radiant loop for our new sunroom (in the concrete floor) Can this be added by adding another zone downstream of the cir… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a knight high efficiency boiler with baseboard radiation
I have a knight high efficiency boiler with baseboard radiation 5 zones 170 degree water I have a pump (Taco) at boiler that only runs water through the boiler (not out to the house) just down stream … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a noritz gas tankless water heater. I want to use it
I have a noritz gas tankless water heater. I want to use it with my hvac system to provide hydronic heat, but also use it for domestic hot water for the house. I know it can be done, just need the plu… read more
Jim Hamilton
Jim Hamilton
High School or GED
246 satisfied customers
What is the proper way to use a hot water heater for infloor
What is the proper way to use a hot water heater for infloor heating? The house is 1250 sq.ft.. Domestic water heater is a 50 gal. Infloor water heater is a 40 gal connected in a closed loop. Seems li… read more
Patrick
Patrick
Bachelor's Degree
1,269 satisfied customers
i have an open system with a wall mount heater and 1 zone radiant
i have an open system with a wall mount heater and 1 zone radiant floor heat . when the heat comes on my pressure gauge goes from 45 to about 90 psi. if i drain off alittle water from a sink it will d… read more
Patrick
Patrick
Bachelor's Degree
1,269 satisfied customers
We built a new home and installed a tankless water system.
We built a new home and installed a tankless water system. At the same time the plumbers added a 'circulating line' so we could have instant hot water when we ran the faucet, but it did not work. We m… read more
Bud
Bud
Plumber
High School or GED
538 satisfied customers
I just installed a 50 gal energy smart whirlpool HW heater
I just installed a 50 gal energy smart whirlpool HW heater for a closed loop radiant heat system. I have received a couple different error codes since the install was completed. 4 flashes, upper eleme… read more
Plumber Matthew
Plumber Matthew
Journeyman Plumber / Foreman
High School or GED
154 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x