I have a Utica Boiler. The water in my sight glass does not move even though the low level light came on. I unscrewed the nut on the underside of the tube and water started coming out, but the water in the sight glass did not move. I loosened the knobs at the top and the bottom of the glass about a quarter turn and the water drained from the sight glass. I replaced the nut and refilled the boiler and I was able to get the tube to be about half filled with water. I tightened the knobs back the way they were, which I'm assuming is closed. I filled it enough so that the low water indicator light turned off and left it that way.

My question is, how should those knobs be turned for the sight glass to work properly?
Show More
Show Less
Ask Your Own Plumbing Question
Answered in 1 hour by:
9/19/2013
Phil
Phil, Mechanical Engineer.
Category: Plumbing
Satisfied Customers: 8,824
Experience: Retired mech. contractor, shop owner, 51 yrs experience.
Verified
Welcome to Just Answer!

The knobs should be left closed at all times except when you are checking the water level, thats a safety measure in case the sight glass breaks.

You should check the low water cut out switch every 30 to 60 days by opening the sight class valves, and then opening the drain valve on the boiler slightly and noticing how low the water gets in the gage glass before the low water cut off switch opens and shuts the gas off to the burner. or the make up water valve fills the boiler back up to half glass again. Then close the boiler drain valve at the bottom of the boiler.

Do not let the water level get closer than 1 inch to the bottom of the glass.

If you get me the model number of the boiler and tell me if it is supply stream or hot water to the radiators i can be a bit more specific.


Phil
Ask Your Own Plumbing Question
Customer reply replied 4 years ago

The boiler is model number PEG112CDE and is supplying steam to the radiators.


 


So, if the knobs are supposed to be both closed, how is the sight glass supposed to indicate the water level in the boiler? (top and bottom - as pictured here):


utica boiler site glass


 


Right now, I have no idea how much water is in there because the water in the sight glass doesn't move and I don't want to overfill it.

Hello again, virtually all steam boilers ever built have an automatic water feed float system so that when the water gets a few inches low the water feed valve opens and fills the boiler to about half a glass.. From your reports that is how you boiler is operating.

When you want to read the sight glass turn both knobs on the sight glass 1/4 turn open and read the glass, then open the boiler *drain valve slightly* and you will see water in the drain where the drain valve goes.

You will see the water level in the sight glass drop, proving it works, then close the drain valve, and you will see the sight glass fill up again, proving the city water feed works... you should do that test every 30 days. 60 days between tests maximum.

After you do the test turn the knobs on the sight glass to the right.. that closes the valves and the sight glass will not read again until you open them for another test.

The sight glass is fragile, that is why it is left closed between tests.

 

The sight glass is ONLY an indicator it does not control the water level. The water level is monitored by a float valve. The checks mentioned above are to insure the float valve works... and that the switch it is connected to that kills power to gas valve stops the burner if the water in the boiler gets low.

Let me know if that makes any sense or not on your end, we keep going until you have full and complete answer you need, and understand it, there are no time limits here.

Phil

Ask Your Own Plumbing Question
Customer reply replied 4 years ago

Let me make sure I understand properly and have the correct procedure down for when I need to do this.


 


Right now, the red light on my low water cut off is off, so I don't need to do anything.


 


every 30 - 60 days, I should open the knobs a quarter turn, drain a little water to see if the level in the glass goes down. I'd imagine that I should turn off the heat and let the boiler cool before doing this.


 


Otherwise, when the light goes on, after letting the boiler cool (I know that cold water+hot boiler = bad Frown ), I should turn both knobs about a 1/4 turn open. that will show me the water level. Then, use the water feed into the boiler to fill it and when the sight glass is at an acceptable level, stop the water, close the knobs on the sight glass and turn the heat back on.


 


Is that correct, or am I missing a step.


 


Thank you for your patients, I just don't want to do something to mess up a very expensive part of my home.

Hello again, thats close.

Letting cold water into a hot boiler IS bad if you do it on a hot drained boiler, in this case the boiler water feed should kick in after you let just an inch or two of the boiler water out, so letting that small amount of water out and letting it refill is part of a normal operation.

If you do this when the boiler is on and firing, it should stop firing and the red light should come on when you let an inch or two of the water out... the burner should go off (thats part of the check and you should hear the water feed adding water to the boiler and the water level in the sight glass start to rise again.

Let me know if you more information, we continue with this until you are quite clear on the process... it will be good try it a few times, then check back with me if there are any questions.

Phil
Phil
Phil, Mechanical Engineer.
Category: Plumbing
Satisfied Customers: 8,824
Experience: Retired mech. contractor, shop owner, 51 yrs experience.
Verified
Phil and 87 other Plumbing Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago

Thank you, that was very clear.

Great!

you are welcome however to stay in touch in this thread if you need any further clarification.

Phil
Ask Your Own Plumbing Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer.
Category: Plumbing
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired mech. contractor, shop owner, 51 yrs experience.

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Marc

Marc

Plumber

1,127 satisfied customers

Plumbing heating & home maintenance contractor

Jerry

Jerry

Plumber

784 satisfied customers

over 20 years residential plumbing experience.

Theplumber717

Theplumber717

Plumber, Hvac Tech

656 satisfied customers

Lic Plumbing contractor, 28/yrs res,com,repair,Universal HVAC Tech

Mario

Mario

Master Plumber

604 satisfied customers

Master Plumber, Fire Sprinkler, and Jobbing Spec.

Phil

Phil

Mechanical Engineer.

8,824 satisfied customers

Retired mech. contractor, shop owner, 51 yrs experience.

Bud

Bud

Plumber

538 satisfied customers

22 Years Field Experience - 17 Years Business Ownership - Residential or Light Commercial

Rick Mather

Rick Mather

Building Inspector

498 satisfied customers

Assistant Building Official, HVAC Tech

< Previous | Next >

Related Plumbing Questions
I also think air lock however when I open the bleed valve on
I also think air lock however when I open the bleed valve on each radiator come have a week stream of h2o and some nothing.… read more
Jim Hamilton
Jim Hamilton
High School or GED
246 satisfied customers
The water in the glass tube in my 3 year old gas fired steam
The water in the glass tube in my 3 year old gas fired steam boiler all of a sudden drops below the shutoff point and when I fill it up again, the system fires up but I run out of water in less than 5… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,198 satisfied customers
I am getting a steam/oiler boiler replaced. I've agreed to
I am getting a steam/oiler boiler replaced. I've agreed to having it replaced, installation included fittings and pipes.Salesman mentioned at the end that the Hartford loop will also be replaced and i… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Gas fired steam boiler Weil McLain. Pressure relief valve
Gas fired steam boiler Weil McLain. Pressure relief valve activated two times. No reading on pressure gauge. Previous response from justanswer.com three possibles 1.temperature too high 2.pressure too… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a new (3 Yr old) Utica steam boiler. Mubsight glass
I have a new (3 Yr old) Utica steam boiler. Mubsight glass is clear when off but really dirty while running. Fairly sure all my radiator venta are vbocked up and I'm planning to replace them. The ques… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Steam boilers are taking on water. Water is not returning to
Steam boilers are taking on water. Water is not returning to the boilers so when it calls for heat, it adds more water to the system. Then water travels up into radiators and they begin clanging. Some… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Steam Boiler sight glass is empty but the boiler won't
My Steam Boiler sight glass is empty but the boiler won't add water … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I would like to move hot water boiler to other side of
I would like to move hot water boiler to other side of house. It's now venting through chimney that also cents steam boiler. Can hot water heater be vented to side of house or does it have to be done … read more
canuck the pro
canuck the pro
251 satisfied customers
My old house has a steam boiler. Two new radiators heat
My old house has a steam boiler. Two new radiators heat unevenly and one squirts water from the steam valve. The old radiators work fine. How can I troubleshoot the new radiators? Thanks... Anne… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a thatcher steam boiler which is original in my house
I have a thatcher steam boiler which is original in my house built in 1935. I was told it once ran on coal and had since been converted to coal. Idk how to take pictures site so I'll describe my probl… read more
qwasert
qwasert
Residential Journeyman Plumber
Vocational, Technical or Trade Scho
8 satisfied customers
For some reason the radiators are not all getting hot. I have
For some reason the radiators are not all getting hot. I have a old steam boiler system, an additional problem is that at times. The radiator makes a loud banging sound, which is very annoying. What c… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I had a STEAM boiler crack last week during the first hour
I had a STEAM boiler crack last week during the first hour of use after it was turned off all summer. the water was drained slightly prior to this to clear out the rust and refilled to the 50 percent … read more
Rick Mather
Rick Mather
Building Inspector
Vocational, Technical or Trade Scho
498 satisfied customers
Hi, Floor standing gas fired STEAM boiler replacement, 210,000
Hi, Floor standing gas fired STEAM boiler replacement, 210,000 btu. Location is in a below ground basement without access to chimney or outside wall. Questions:-1) Is there a boiler that does NOT requ… read more
Marc
Marc
Plumber
Vocational, Technical or Trade Scho
1,127 satisfied customers
I have a New Yorker Classic CGS-A Series Steam boiler with
I have a New Yorker Classic CGS-A Series Steam boiler with Honeywell Limit & Thermostat connection box on top of boiler body. Also a McDonnel LWCO and a Effikal RVGP-PC-5BKF Damper. My Steamboiler tur… read more
Phil
Phil
Mechanical Engineer.
8,824 satisfied customers
I am a plumbing contractor in NJ, I have a house with steam
I am a plumbing contractor in NJ, I have a house with steam heat and the problem is half the radiators on the 1st and 2nd floor are only getting half hot. I have pitched all the rads changed all the a… read more
Rick Mather
Rick Mather
Building Inspector
Vocational, Technical or Trade Scho
498 satisfied customers
The damper on my boiler is closed asn the boiler has shut
Will a closed damper on a boiler caused the boiler to shut down and not come back on? And how do you open the damper?… read more
Accuratejoe
Accuratejoe
Owner of Accurate Mechanical
Vocational, Technical or Trade Scho
76 satisfied customers
i just had a steam boiler installed in my new house the old
i just had a steam boiler installed in my new house the old boiler was 60 years old. The new boiler is causing the pipes to bang extremly loud what could be the problem… read more
N.Y.City Plumber
N.Y.City Plumber
Vocational, Technical or Trade Scho
22 satisfied customers
Have Steam boiler in the basement. Water level in the tube
Have Steam boiler in the basement. Water level in the tube keeps going up. It is suppose to remain in the center. Did have a new valve put in the boiler by a qualified heating man (?) and still does n… read more
30yearPlumber
30yearPlumber
Plumbing & Heating Contractor
High School or GED
170 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x