I have two twinned York furnaces hot air and two ac York Ac
I have two twinned York furnaces hot air and two ac York Ac coils in plenum linked I want to buy back up thermostat which is control for whole system it works fine but must be. 20 to 30 yrs old is the… read more
Tamar D
Tamar D
Mechanic II
Vocational, Technical or Trade School
1,188 satisfied customers
I am replacing my 4-ton residential split system with a new
I am replacing my 4-ton residential split system with a new Trane system (furnace and condenser), but details are being worked out. I'd like a system with 2 stages of cooling in the furnace--that is, … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
8,427 satisfied customers
Furnace blowing cold air,Filter is good,burner is on.
Furnace blowing cold air,Filter is good,burner is on … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,643 satisfied customers
What are your fees to chat please. What is the usual fee
I have a carrier 58 MVP natural gas furnace. The furnace was not heating the house and temperatures got into the 50s on Saturday. The blower was cycling on and off and I had error codes 4 short and 2 Long. On Sunday still the same but error codes 2 short and 3 long. Our repairman did come today and found condensation water backed up in the furnace. He drained a lot of water (more than 1/2 gallon) and cleaned out the trap. The furnace is working ONLY on low burner and low fan speed now. After 16 minutes of low burner it should kick into high burner and high blower speed. It will only run on low burner and low blower speed. The technician did use a jumper wire and the high burner and high fan speed did work and we left the jumper on to get the house up to temperature. Currently the furnace is running on low burner and low blower. The outside temperature is moderate now only 35 degrees and the house temperature is maintaining our requested 68 degrees. Looking on the internet I have seen this issue posted but no solutions. The technician is still researching this with a Carrier representative. My hunch is it may be due to the water backed up from the burners?? What are your thoughts on how to get the high burners and high blower to work automatically after the normal 16 minute period of low burner and low blower. There are no error lights on the furnace now just the continuous solid white light indicating all is well. We always run our carrier thermostat on continuous fan. The unit was installed in 2005 and had not problems. We also have a carrier heat pump which we use only for air conditioning in the warm weather. No issues with the heat pump and no issues until today with the carrier 58 MVP natural gas furnace. I have seen this issue posted on the internet but without any solution. … read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
10,107 satisfied customers
Limit switch is tripping every time stage 2 fires up on my
limit switch is tripping every time stage 2 fires up on my furnace … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
772 satisfied customers
I have a Goodman GMVC950704CXAB two stage gas furnace. Low
Good morning, I have a Goodman GMVC950704CXAB two stage gas furnace. Low stage works fine. When the unit gone into high stage, it runs fine. When air handler blower kicks on to high speed, it runs for… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
10,107 satisfied customers
I have York two-stage gas furnace with single stage Honeywell
I have York two-stage gas furnace with single stage Honeywell digital thermostat. Second heating stage delay is controlled by a timer on the circulating blower housing. Furnace totally quit, and I fou… read more
Appliance Guru
Appliance Guru
21,442 satisfied customers
We have an 11 year old Carrier Weathermaker 8000TS furnace,
We have an 11 year old Carrier Weathermaker 8000TS furnace, model 58TUA100-12 hooked up with a single stage programmable thermostat set to drop the temperature down to about 62F during the weekdays, a… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
10,107 satisfied customers
I have a Goodman GMH 95 115 5 DX propane furnace. I had it
I have a Goodman GMH 95 115 5 DX propane furnace. I had it installed last year and it ran through winter and summer with no blower problems. This fall I had a 20 x 12 room added and wanted to try incr… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,118 satisfied customers
I have a Honeywell 7184A 1000 controller on my York furnace,
I have a Honeywell 7184A 1000 controller on my York furnace, ran out of fuel oil, filled the tank, have 2 inline filters, bled the line- Hit the red reset button - turned on power to the furnace... it… read more
Rick
Rick
Supervisor
28,736 satisfied customers
Hello, I do have a Weathermaker Infinity 58MVP080-14. Lately,
Hello, I do have a Weathermaker Infinity 58MVP080-14. Lately, it seems that it takes an unusual time to get to the set temperature. It also seems that the second stage (not sure if this is the correct… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
14,390 satisfied customers
have a Trane XL80 2 stage unit. when I turn on heat just
have a Trane XL80 2 stage unit. when I turn on heat just get a click sound as if the thermostat is sending a signal to start the heater; however nothing turns on, no fan, nothing cooling works just fi… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
10,107 satisfied customers
I HAVE A NEW LENNOX FURNACE, TWO STAGE BURNER AND 5 SPEED FAN
I HAVE A NEW LENNOX FURNACE, TWO STAGE BURNER AND 5 SPEED FAN (MAYBE THREE) ITS INSTALLED AND WORKS FINE BUT WE HAVE JUST A REGULAR THERMOSTAT FOR HEATING AND COOLING, THIS FURNACE CAN BE WIRED FOR TW… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,429 satisfied customers
I have a Tempstar smartcomfort VS90 Variable-Speed Two-Stage
I have a Tempstar smartcomfort VS90 Variable-Speed Two-Stage Gas furnace. When hooked up to the generator (8,000 watts) the furnace is getting a 120 volts. The burner will light, the first blower moto… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
338 satisfied customers
my payne furnace constantly runs in two cycle mode only. the
my payne furnace constantly runs in two cycle mode only. the second stage is always kicking in no matter how long the furnace is on. also, when the furnace shuts down after coming up to temp, there is… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a York variable speed diamond 95 ultra gas forced air
I have a York variable speed diamond 95 ultra gas forced air furnace. Up until this morning I have had no trouble with this. I went to bed at 7pm and it was fine, at 3 am the second stage fan was not … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,429 satisfied customers
i have a carrier 58 mvp gas furnace. it is operating in low
i have a carrier 58 mvp gas furnace. it is operating in low heat mode. the green light is on solid. i have cleaned the electrostatic filter and the insert filters. it was popping a 12 code (blower cal… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,118 satisfied customers
I have a coleman evcon residential furnace everything operates
I have a coleman evcon residential furnace everything operates and the blower kicks on at low speed and then the unit shuts off with an error code of High Aux. or Spill Limit Switch Open. What does th… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

HVAC Expert

10,502 satisfied customers

Certified Mechanical Engineer and HVAC Expert with 30 years of experience

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,029 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

A-1 Tech

A-1 Tech

Service Manager

526 satisfied customers

I have been in the HVAC business for over 40 years.

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.