My ac stopped working. Found no 24v and found a transformer
My ac stopped working. Found no 24v and found a blown transformer on the primary side, so replaced the transformer. Then I had power to the thermostat, good 24v, fan ran but no ac or heat. So I replac… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
14,361 satisfied customers
I just replaced my carrier control board (ICM275) and wire
I just replaced my carrier control board (ICM275) and wire harness. I go to start my furnace and it Keeps blowing the 3amp (low voltage) fuse. I disconnected the thermostat and tried the direct wire c… read more
Appliance Guru
Appliance Guru
21,340 satisfied customers
I have a Carrier Furnace/Air conditioning unit (gas) which
I have a Carrier Furnace/Air conditioning unit (gas) which was installed new 6 years ago. The 3 amp fuse in front keeps blowing when I try to turn on AC. Any idea why?… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
9,972 satisfied customers
I have a York Stellar Plus model # p2udd12no7601c furnace.
I have a York Stellar Plus model # ***** furnace. Two weeks ago, it wasn't working, basic checks revealed crumbled hot surface igniter and blown fuse @ side switch. New fuse and igniter fixed for abou… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
8,427 satisfied customers
I replaced a 3m22 thermostat with a Honeywell. The 3m called
I replaced a 3m22 thermostat with a Honeywell. The 3m called for the c wire to be connected but the Honeywell dose not. the Honeywell worked fine for a few hours and then it stopped. Am I doing someth… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,029 satisfied customers
Gotoman - have followed the procedure here voltage
Hi Gotoman - have followed the procedure here for low voltage wires and it when I get to the R wire the fuse blows. The thermostat is good as it is brand new and actually a temp replacement for a Nest… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,423 satisfied customers
My totaline Stat went blank after turning on AC. Checked breaker
My totaline Stat went blank after turning on AC. Checked breaker it's fine. Traded out blank stat downstairs with upstairs. Works fine upstairs. So don't think it's bad stat… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
9,972 satisfied customers
im working on a trane model 4tee3f37a1000aa that keeps blowing
i'm working on a trane model 4tee3f37a1000aa that keeps blowing the 5A fuse between the transformer and the ICM fan conrol. Any idea what might be causing this? When I replace the fuse and reprogram t… read more
Appliance Guru
Appliance Guru
21,340 satisfied customers
My furnace which is a Payne Model# XXXXX(AAJA) stopped
My furnace which is a Payne Model# XXXXX(AAJA) stopped working late last spring. Ran the diagnostic test and the fuse that controls the Induction motor blew. The induction motor will run when jumped. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,423 satisfied customers
I have a furnace / ac with a White-Rodgers 50A55-486 control
I have a furnace / ac with a White-Rodgers 50A55-486 control board. In the past, I've had intermittent problems with the control board fuse blowing. It happened pretty consistently at one point last y… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
8,427 satisfied customers
I have a lennox Furnace/AC, and the 3a fuse on the circuit
I have a lennox Furnace/AC, and the 3a fuse on the circuit board blew recently. I've replace the fuse and the unit comes up normally (2 green slow blinking lights) but upon the next cycle (thermostat … read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
14,361 satisfied customers
I have a carrier heat pump. having problems in the air handler
I have a carrier heat pump. having problems in the air handler mod # XXXXX keeps blowing the 5 amp fuse on the control board. Replaced board, ran fine for about a hour, blew the fuse, replaced, blowed… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
14,361 satisfied customers
I got home after the long holiday weekend to find that my AC
I got home after the long holiday weekend to find that my AC does not work. It worked fine before we left. The thermostat seems to be working, it clicks, but nothing comes on. The heater will not star… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
My heat pump system stopped working after a power outage and
My heat pump system stopped working after a power outage and continues to blow the low voltage 5 amp fuse when we turn it on. We tested the transformer and it read about 21 volts. We tested the start … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
The induction blower and the main air blower motor runs constantly,
The induction blower and the main air blower motor runs constantly, no matter what the thermostat is set at. Turned of ...and later...removed the thermostat-same problem. No visual wire damage in the … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,423 satisfied customers
Lennox G20 furnace not firing up after temperature falls
I have a Lennox Whisper Heat G20 furnace and had been having problems with it not firing up every time the thermostat went below the desired temperature. I'd have to turn the furnace off/on to get it … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,423 satisfied customers
Hi, I have a Goodman furnace model GSM 100-4. It is ten years
Hi, I have a Goodman furnace model GSM 100-4. It is ten years old. When we turned it on this year, it didn't work. Here's whats happening: on a call for heat, the inducer motor comes on but the 3 amp … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
burner starts runs for about 15 seconds then shuts down for
burner starts runs for about 15 seconds then shuts down for 10 seconds then starts again and works fine?… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

8,427 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,029 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

A-1 Tech

A-1 Tech

Service Manager

526 satisfied customers

I have been in the HVAC business for over 40 years.

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x