Rheem blower motor starts and runs for 2 min, then stops and
Rheem blower motor starts and runs for 2 min, then stops and before it quits spinning then it starts back up and continously repeats the process … read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
13,799 satisfied customers
Can the fan speed on the RCHA-48A1GH21 be adjusted to a
Can the fan speed on the RCHA-48A1GH21 be adjusted to a lower speed when in AC mode? … read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
13,799 satisfied customers
I have a Rheem RHLL-HM6024JA and the blower motor stopped
Hi I have a Rheem RHLL-HM6024JA and the blower motor stopped working. It seems like it starts to spin but stops and hesitates. What could be wrong? … read more
BillyHvac
BillyHvac
Journeyman Service Technician/Inspector
State Licensed Mechanical Contractor
16,009 satisfied customers
We have a question. Our AC condenser went out, right in the
Our AC condenser went out, right in the middle of the hot summer.Our current AC models are: Rheem AC condenser 14AJM42A01 (3.5 ton) Rheem AC inside unit RHLL-HM3821JA (3 ton)Based on manufacturer (Rheem), these are fully compatible.To replace just AC condenser, we would have to go with a unit from a newer line of condensers.Our choices are: Rheem AC condenser to replace with: RA1436AJ1NA (3 ton) Rheem AC condenser to replace with: RA1442AJ1NA (3.5 ton)Rheem does not test newer lines with older lines.Question: If we are to replace just the condenser, would it be preferred to go with the same 3.5 ton specification (Model RA1442AJ1NA), even though our inside unit is 3 ton. … read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
11,975 satisfied customers
I have a rheem air handler and with nothing running the
I have a rheem air handler and with nothing running the heating elements come on then go off every 10 mins or so … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,486 satisfied customers
I have rhc-tst551cmms thermostat that I'm trying to install
I have rhc-tst551cmms thermostat that I'm trying to install It has 4 terminals R,C,Data1,data 2. What wires go to data1 And data 2 spots. Hookup up to rheem 500series thanks… read more
BillyHvac
BillyHvac
Journeyman Service Technician/Inspector
State Licensed Mechanical Contractor
16,009 satisfied customers
I have a rheem split system heat pump ac model RHLL-HM6024JA
I have a rheem split system heat pump ac model RHLL-HM6024JA and would like to know what filters are reccommended for my unit. the filter size is 22x24… read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
4,080 satisfied customers
Sir MY REHEM UNIT. KEEPS BLOWING A 30 WATT FUSE LOCATED
Sir MY REHEM UNIT. KEEPS BLOWING A 30 WATT FUSE LOCATED IN THE INDOOR UNIT. 1-4-2015 Digital thermostat was replaced. HEAT STRIPSHAVE BEEN REPLACED Circuit board for outside unit was replaced. All rep… read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
11,975 satisfied customers
LOOKING AT RARL-060JEZ AND RHLL-HM6024JA OR RHML OR RHPL
LOOKING AT RARL-060JEZ AND RHLL-HM6024JA OR RHML OR RHPL AIR HANDLER ALL IN 5 ton configuation. Live in SW Florida. Any thought on the 16AJL60A01 compressor… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
13,799 satisfied customers
Good morning, Douglas, replacement 5 ton Rheem Heat
Good morning, Douglas, replacement 5 ton Rheem Heat pump, should I use the air handler with an ECM motor or the regular RHLL with single speed? Iv been living with a single speed and it seems ok (in S… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,486 satisfied customers
I have a rheem high efficiency furnace a/c unit. Turned it
I have a rheem high efficiency furnace a/c unit. Turned it on for the first time this year and all was well. after a while I noticed the blower not blowing as fast and I could smell something burning.… read more
BillyHvac
BillyHvac
Journeyman Service Technician/Inspector
State Licensed Mechanical Contractor
16,009 satisfied customers
Hi. I have a new thermostat and it has different wiring guides
Hi. I have a new thermostat and it has different wiring guides for conventional or heat pump, 1H/1C or 2H/1C, 2H/2C. How do I know what my system is? My air handler is a rheem RHLL-HM6024JA… read more
airheatman
airheatman
Heating & Air Conditioning Contractor
6 years college
13,799 satisfied customers
Rheem HM-6024JA Air Handler. Id like to slow the fan. Heat
Rheem HM-6024JA Air Handler. I'd like to slow the fan. Heat is not a problem, as I'm in Central Florida. Is there a simple wire change? I'm pretty handy. Just don't know what wires to change. Thanks m… read more
BillyHvac
BillyHvac
Journeyman Service Technician/Inspector
State Licensed Mechanical Contractor
16,009 satisfied customers
I have a Rheem RGGC-150C unit. The blower motor (inside) will
I have a Rheem RGGC-150C unit. The blower motor (inside) will usually not start when the upper set temperature is reached for cooling or, failing that, the blower is turned "on" (not auto) unless I go… read more
Appliance Guru
Appliance Guru
23,533 satisfied customers
My furnace blower will not turn on but all other functions
my furnace blower will not turn on but all other functions appear to be working, such as outside ac , heat etc... the blower motor sounds like it going to start and then just doesn't. I even got it to… read more
Comfort Specialist
Comfort Specialist
Licensee, Designer & Estimator
Vocational, Technical or Trade School
1,369 satisfied customers
We have a Lennox G16Q4/5-125-1 furnace/AC unit. Sometime today
We have a Lennox G16Q4/5-125-1 furnace/AC unit. Sometime today the unit failed to come on when the thermostat told it to. The power to the blower motor kicks on, but the blower doesn't turn. Instead t… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I HAVE A RHEEM SPLIT SYSTEM, AIR-COOLED CONDENSING UNIT, COIL
I HAVE A RHEEM SPLIT SYSTEM, AIR-COOLED CONDENSING UNIT, COIL WITH BLOWER: OUTDOOR UNIT MODEL NUMBER: 14AJM42 INDOOR UNIT MODEL NUMBER: RHLL-HM3821+RCSL-H*3821 CAN YOU PLEASE TELL ME THE "SEER" RATING… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,486 satisfied customers
How is the low temperature compressor lock out controlled on
How is the low temperature compressor lock out controlled on a Rheem RPRL-060 JEC connected to a RHPL-HM6024JA air handler, and a 24 V Thermostat. It shuts down at somewhere between 32-35 outdoor temp… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,486 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,029 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Jerry

Jerry

Service Technician

576 satisfied customers

HVAC Technician. Hearth Products Specialty

A-1 Tech

A-1 Tech

Service Manager

526 satisfied customers

I have been in the HVAC business for over 40 years.

Thehvacguy

Thehvacguy

LIC HVAC,Plumber

426 satisfied customers

Certified HVAC Universal Technician,Lic plumbing contractor, 28 yrs exp

Drcool

Drcool

HVAC Technician

264 satisfied customers

i have been an A/C tech for the past 30 Years. working on window types, split type, and package

N4IEA

N4IEA

NATE Certified; HVAC Technician

227 satisfied customers

Retired, HVAC / Electrical Technician / Contractor 35-years Experience.

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.