HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Connect one-on-one with {0} who will answer your question

Related HVAC Questions
My Rheem 90s classic wont fire up...the fan runs but it
My Rheem 90s classic wont fire up...the fan runs but it won't light then the fan shuts off minutes latter..Help … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I got an Armstrong G1N80AU natural gas furnace and got a 4
I got an Armstrong G1N80AU natural gas furnace and got a 4 flashes failure code which as per the O&M manual indicates an open limit switch or limit switch circuit fault. I checked the rollout switch, … read more
servtech50
servtech50
HVAC/R service tech
296 satisfied customers
20 yo Lennox with faulty air pressure sensor - replaced but
20 yo Lennox with faulty air pressure sensor - replaced but still not working apparently. I have been able to tap it to get it to work, but not today.… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor's Degree
6,158 satisfied customers
I have a nordyne propane furnace modle # kg6rc we cant get
I have a nordyne propane furnace modle # kg6rc we can't get it to work ,it has a light blinking 2 lights which means pressure switch is open with inducer open now we changed the pressure switch but it… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor's Degree
6,158 satisfied customers
I have a 11 year old furnace (Lennox model 80MGF2-45A-9) I
I have a 11 year old furnace (Lennox model 80MGF2-45A-9) I am getting the combustion Blower to come one when Thermostat calls for heat but the burners do not light, nor does the electronic ignition sp… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a 31 fault code on the LED. No blockage in my exhaust
I have a 31 fault code on the LED. No blockage in my exhaust and intake pipes. The manual suggests a pressure switch fault. I have intermittent flame. When I do have flame, the LED code goes away to s… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor's Degree
6,158 satisfied customers
Replaced a draft inducer motor on a ICP-Heil furnace. Reset
Replaced a draft inducer motor on a ICP-Heil furnace. Reset gas valve. Blower motor engages, but draft inducer does not start nor does the ignitor or gas valve. Model #NDGK075DF06. Can you help?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have a model # XXXXX which runs through the test
I have a model # XXXXX which runs through the "test" mode witout any issues. However, the burners are not lighting- What could this be and what else can I check? (BTW, I didn't see an LED light/ code)… read more
airheatman
airheatman
HVAC Technician
6 years college
10,401 satisfied customers
have a 92% heil that the the inducer draft motor comes on then
have a 92% heil that the the inducer draft motor comes on then i get flame then the inducer motor shuts off and the flame stays on for 10 sec then the blower comes on any answers… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I am getting a reading of three flashes on my diagnostic light
I am getting a reading of three flashes on my diagnostic light , we tested the air switch from normally open and blew into it and the contacts sounded like they closed so we verified that it closed wi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,375 satisfied customers
I have a 4-year old York Furnace (Model No GY9S0). I had problems
I have a 4-year old York Furnace (Model No GY9S0). I had problems in the past with the inducer motor (Fasco A225) due to a drainage issue that has been rectified. I also replaced the inducer motor las… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,375 satisfied customers
i have a rheem imperial 80 plus furnace 25 yrs old.burner was
i have a rheem imperial 80 plus furnace 25 yrs old.burner was going off and on,put vaccum on pressure hose works fine,replaced pressure switch and hose cleaned out what hose attachs to,inducer seems t… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
OUr Amana furnace pilot light is off. We followed the directions
OUr Amana furnace pilot light is off. We followed the directions to light it that did not work. We do not see a reset button. How do we light it?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
I have a goodma furnance model# GMT090-3. The unit hums but
I have a goodma furnance model# XXXXX The unit hums but the heat does not kick on. When I open the panal I'm getting 3 light blinks. according to the panel, this means that the pressure switch is fail… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,375 satisfied customers
trane 90v gas furance system gos off on code pressure switch
trane 90v gas furance system go's off on code pressure switch default but draft inducer motor does not come but when i remove wires from limit inducer switch and jump still does not come taking out sw… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I have a Trane XE78 furnace. The problem I have seems electrical.
I have a Trane XE78 furnace. The problem I have seems electrical. The blower constantly runs when cooling cycle stops. Thermastat is on auto/ cooling. I disconected thermastat to c if that was the pro… read more
BillyHvac
BillyHvac
Journeyman Service Technician
State Licensed Mechanical Contractor
14,011 satisfied customers
Furnace 376CAV (1997 Trane Day and Night Plus80) not heating Problem
Furnace: 376CAV (1997 Trane Day and Night Plus80) not heating Problem Description: Error 31. 1. Turn power off for 15 minutes. 2. Turn on power. Thermostat ON. 3. Blower goes for ~60 sec. LED flashes … read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x