I am working with a Nutone upright gas furnace with a standard A coil on it. It keeps breaking the the condensate pipe. The pipe shatters. Original pipe was sch 10 cpvc. It shattered. I replaced it with sch 80 cpvc. It shattered. It looked like mechanical abuse to me. Something dropped on it. The costumer is however an elderly lady and the unit is in a closet with no storage occurring there. The condensate system is connected to both the A coil and the condensate from the condensing furnace, but is is the A coil piping that breaks. I am at wits end!! what is happening.
Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 51 minutes by:
5/30/2018
HVAC Technician: Bill, HVAC Technician replied 2 months ago
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 114
Experience: Service Mgr
Verified

Hello,

is it possible the ac is freezing up to where it breaks the drain?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
anything is possible but I checked the pressures and it seems fine. Wouldn't the coil freeze up and cut air flow? That doesn't happen. What about the TVX valve?
Customer reply replied 2 months ago
Billy, I have made a temporary drain with clear poly tubing. If the freeze theory is true, should frost form in the tubing. Right now we have high humidity and 75-80 degree temperatures. What do you expect the gauge readings to be under those circumstances?
HVAC Technician: Bill, HVAC Technician replied 2 months ago

r410 or r22?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Dill so you have an answer?
Customer reply replied 2 months ago
410A
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a four year old GV90+ 5 furnace and it just blew the
I have a four year old GV90+ 5 furnace and it just blew the thermal fuse on the flue. What would cause this? What do I need to check before I replace the fuse. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I replaced a downflow furnace and cooling coil in a 2nd floor
I replaced a downflow furnace and cooling coil in a 2nd floor closet and now inspector wants a drip pan underneath. I don't see how this is possible because the cooling coil is above a discharge plenu… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
what is the cause of a streaky greenish-brown residue (or sediment?)
what is the cause of a streaky greenish-brown residue (or sediment?) on the exterior of a gas furnace exhaust vent for about 2 feet of the vent at the point where the leaves the furnace?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
when I replace the old furnace, does it follow that the condenser
when I replace the old furnace, does it follow that the condenser outside is replaced even though it is only 3 years old? Should I look for a furnace at 80% or 97%. Average cost to replace a furnace?… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
Hi I have a nordyne e3 series downflow a/c and heat pump air
Hi I have a nordyne e3 series downflow a/c and heat pump air hendler. Model #E3EB-015H. The coils keep leaking water from the inside of the coil down onto the blower. Oh it is new has done this from d… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
Hello, I have a couple of questions pertaining to a 1993 KeepRite
Hello, I have a couple of questions pertaining to a 1993 KeepRite gas furnace Mod.#cgk100n09,Ser.#l934023094. First Q.What AFUE was this furnace rated at in 93 and what would that compare to today's A… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Model #RPNK-149JAZ installed in 1850 sq ft house in summer
Model #RPNK-149JAZ installed in 1850 sq ft house in summer of 2006, fails to come on as of 7/26 AM, set at 75 deg F thermometer reading 83 deg F. "Snowflake" showing in thermostat as selected for cool… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am having an issue with condensation on the pipes to/from
I am having an issue with condensation on the pipes to/from the unit upstairs.....so much so that the water pan underneath is full (flood meter does not appear to be working) and therefore a constant … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a tech whos.given.me a quote for a ruud system. The
I have a tech who's.given.me a quote for a ruud system. The condenser is a ultra 16 series 2 stage uasl 036jec. Furnace rpge0705 and didn't state model number for coil just said its a 3.0 ton box coil… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I want to install an outside air intake system on my Heil Enviro
I want to install an outside air intake system on my Heil Enviro Plus 80 furnace. I'm concerned about the 3 in dia. connection at the furnace. It is equipped to accept an intake. What do I need and ho… read more
Tim D.
Tim D.
Technical Service Manager
Vocational, Technical or Trade Scho
7 satisfied customers
I am a licensed HVAC contractor. I am installing a RUUD 2
I am a licensed HVAC contractor. I am installing a RUUD 2 stage condensing gas furnace. The standard venting for this furnace is sch 40 PVC. The application for this furnace is a 2 story residential t… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have been having problems with this issue for long time,
I have been having problems with this issue for long time, I need help, WE have refrigerated air and heating thru the heater, just put on heat for winter and cool in summer, well in the summer there i… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a RUUD High Efficiency Residential Heating unit in my
I have a RUUD High Efficiency Residential Heating unit in my attic. It was installed in 2004 and is 93.5 per cent efficient. Don't know model #. After replacing the air filters the heating system won'… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Our contractor just installed a Carrier 5-ton Performance Series
Our contractor just installed a Carrier 5-ton Performance Series 24APA7 and a Boost 80 58PHX110-20 furnance. I thought I was getting an Infinity 80 58CVX110120 furnace with a variable speed motor. The… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I want to replace/upgrade my existing RUUD 3 ton split AC 10
I want to replace/upgrade my existing RUUD 3 ton split AC 10 seer system, but I am not able to spend on a high end efficient unit. It has an indoor gas furnace and coil upflow in a closet. The indoor … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
According to the IRC mechanical code, under what conditions
According to the IRC mechanical code, under what conditions can a fossil fuel furnace be located in a utility closet inside a bath or bedroom? In addition, was there an era when the mechanical code di… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
9I just recently ( 3 wks ) ago had a York YP9-80 95% gas modulatin
9I just recently ( 3 wks ) ago had a York YP9-80 95% gas modulatin furnace installed to replace an old oil furnace My contract stated they would to the removal of old furnace intall the gas furnace. H… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
i have just had a trane coil installed on top of a rheem oil
i have just had a trane coil installed on top of a rheem oil furnace. the coil is condensating profusely and black mold is forming on the supply duct on top of the furnace. should i have put in a tran… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x