Rather than going up to the 160 Degree CH Set point the unit…

Customer Question
Rather than going up to...
Rather than going up to the 160 Degree CH Set point the unit cuts off in the 104-108 range each time (3 102, 104, 106 (climbs) and then:6 108 - Burner off due to reaching temperature set point and decreasesWarm here now so too much immediate concern, but would like to see this to its previous 160. One thing to note is I have fiddled with a valve that appears to "bypass" the boiler. To the best of my knowledge it was half open and then I closed it (thinking this would route all water to boiler).Only thing that has really changed though from working winter unit to today's top temp of 108.
Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 hours by:
5/30/2018
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,632
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of your boiler? do you have an outside sensor?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
There is a sensor outside of the home that registers roughly between 38-70 degrees this time of year.The unit is a Triangle Tube Solo 250Thanks
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago

Sounds like your DHW is wird to the central heat control circuit. Since you have an outside sensor the boiler water set point will drop when it gets warmer outside. BUT this should have no effect on DHW boiler water set point if th DHW tank aquastat is wired to the the proper terminals

Ask Your Own HVAC Question
Customer reply replied 2 months ago
The issue is that the heat cuts off prior to zones coming up to correct temperature. For example, I have a zone I want to bring up to 78 and the boiler comes on, heats to 108 and then cuts off dropping to 94 but the zones don't seem to heat to the necessary levels.
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago

78 is significantly higher than normal design room temp (70-72) so it will probably take longer than normal for the room temp to rise particularly if the outside temp is relatively warm. If you want to run room temp that warm during the warmer weather months the outdoor reset control setings may need to be adjusted.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago

Do you ave more questions?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
I can't seem to find that documented. Are you certain that is what is occurring with the Triangle Tube? The reason I'm asking is I have a radiator tied into the system - 10 zones of radiant floor heat and 1 zone radiator with a thermostat right next to it. If I set that zone to something like 80 (radiator zone) my impression is the boiler should run up until that zone is 80. Yet it continues to cycle on and off.So my question is how to force the boiler to go to 160?
HVAC Technician: Rick, HVAC Supervisor replied 2 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,632
24,632 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I recently had installed a new Trane 2.5 Ton unit (model No.
I recently had installed a new Trane 2.5 Ton unit (model No. 4TCY5030A) for my 576 sq. ft. mobile home (12' x 48'). It replaced a 20-year-old 2.5 Ton unit (brand unknown), which was working well, exce… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a westinghouse comb boiler model wbrc140w propane
i have a westinghouse comb boiler model wbrc140w propane fired boiler,I installed it myself,the unit fires,heats water,internal pump circulates for approx 2 min shuts down with no error codes,i did no… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
We had a brand new HVAC system installed last fall. It
We had a brand new HVAC system installed last fall. It consists of: Rheem gas furnace, Rheem AC and matched coil, central air filter, and Aprilaire humidifier. We had the same type of (pad-style, Apri… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Last night the boiler setpoint on my Burnham residential boiler
Last night the boiler setpoint on my Burnham residential boiler dropped back from 180F to 104F and things started getting a little chilly. We in-floor radiant heat here, and this same thing happened 2… read more
Rick
Rick
HVAC Supervisor
24,632 satisfied customers
Phil: I have a Weil Mclain boiler and my thermostat is set
Phil: I have a Weil Mclain boiler and my thermostat is set at 75, but unit shuts off at 70 and the circulating pump keep running. The house does not seem to be 70 degrees but my thermostat for my furn… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I just bought a home with a Weil-Mclain boiler. I have no
I just bought a home with a Weil-Mclain boiler. I have no experience with boilers. The boiler has been turned on recently because of a cold snap in my area. However, if I do not keep the thermostat se… read more
Rick
Rick
HVAC Supervisor
24,632 satisfied customers
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE TEMP GAUGE SHOWS ONLY 170 DEGREES AND BURNER IS SET TO TURN OFF AT 160… read more
Rick
Rick
HVAC Supervisor
24,632 satisfied customers
Our Triangle Tube Prestige Excellence combi system is overheating
Our Triangle Tube Prestige Excellence combi system is overheating the house by 10 degrees over what thermostat is set to. Domestic hot water seems to be working fine.… read more
Nathan Marshall, MP
Nathan Marshall, MP
Master Plumber,HVAC Tech,Tradesman
Vocational, Technical or Trade School
275 satisfied customers
i have a jvs125 125000btu mini therm which services three zone
i have a jvs125 125000btu mini therm which services three zone values. the high limit is 180degrees. when one of the zones calls for heat the furnace hums and or starts to vibrate .never had this prob… read more
Rick
Rick
HVAC Supervisor
24,632 satisfied customers
The heaters on our 2 Rheem Ruud water heaters - model GN100-270,
The heaters on our 2 Rheem Ruud water heaters - model GN100-270, manufactured in 2007, have quite abruptly started being very loud, when this had never happened before. They are installed in series an… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
We have a combi boiler, however despite replacing the circuit
We have a combi boiler, however despite replacing the circuit board and the sensor, the boiler fails to fire up when it is on a timed setting. The pressure has not dropped, but unless the heating and … read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Ive a remaha avanta combi boiler, installed a year ago, serviced
I've a remaha avanta combi boiler, installed a year ago, serviced just before xmas, water from shower not really hot enough. Plumber who serviced boiler said this was because of lower outsie temo (boi… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
3 satisfied customers
I just hooked up a Buderus 142-60 with a propane conversion
I just hooked up a Buderus 142-60 with a propane conversion kit. the unit fired up fine and heats the water for my hydro-air system, but when it gets to 130 degrees it shuts down with Y0 code and an F… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
The fan in my air handler continues to in the AUTO mode even
The fan in my air handler continues to in the AUTO mode even when the AC has shut down due to reaching the temperature set point. I have a Honeywell TH6220D Focus Pro 6000 Thermostat which I first sus… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Lokinvar Knight model KBN285, recently it started
I have a Lokinvar Knight model KBN285, recently it started to make loud banging and knocking noises each time that it cycles. what do I need to be concerned about? The system is about 5 years old.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a Laars Endurince boiler Model EBP-110. The supply water
I have a Laars Endurince boiler Model EBP-110. The supply water temperature is too high at 195 degrees Fahrenheit. How can I adjust it to 160 degrees Fahrenheit. Please let me know, Tom… read more
SF Plumber
SF Plumber
Associate Degree
224 satisfied customers
I have had a Trane XL14i heat pump for two summers now and
I have had a Trane XL14i heat pump for two summers now and this year for some reason it is having trouble keeping up with the heat. For example the thermostat is set to 67 and the internal house is at… read more
The Home Smithy
The Home Smithy
Home Improvement Repair Consultant
1,890 satisfied customers
Hi, I have a (non-condensing) Worcester Bosch Junior 28i combi
Hi, I have a (non-condensing) Worcester Bosch Junior 28i combi boiler. Recently it has started losing pressure whenever the Central heating is used. If the heating is not used, just hot water, there d… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x