1.5 ton system brand new, lineset length is 60feet,

Customer Question
1.5 ton coleman system...

1.5 ton coleman system brand new, lineset length is 60feet, subcooling is 3 superheat is 72, suction pressure 40 head pressure 220 factory charge is 5 ibs 11 oz, added 1 ib 6 oz for lineset length, even with low sc and high sh addding refrigerant makes no difference to pressures, it was doing this before and tech support diagnosed compresssor bad, replaced outdoor unit and system is doing the same thing, indoor txv has already been replaced as well, coils are both clean and static pressure is .4. what could be left?

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

All that has been checked

Contractor's Assistant: Do you plan on doing the work yourself?

Yes i need advanced refrigeration advice

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 months ago
with the suction pressure and my subcooling and super heat numbers I tried adding additional refrigerant and the pressures didnt move, so now system has 9ibs 11 oz in it, my llt is 75 and slt is 66 it was 71 degrees outside
Customer reply replied 2 months ago
80 return
Answered in 14 minutes by:
5/27/2018
HVAC Technician: hvacdave84, HVAC Technician replied 2 months ago
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 99
Experience: ARI and EPA certified
Verified
It sounds likenyou may be flashing in the liquid line due to the long lineset. Is there a sight glass anywhere close to the evaporator? Also, has the lineset been replaced when the new equipment was installed or was their old lineset re-used?
Ask Your Own HVAC Question
HVAC Technician: hvacdave84, HVAC Technician replied 2 months ago
is this 410a? I assume so with it being brand new but your pressures are more consistent with R22
Ask Your Own HVAC Question
Customer reply replied 2 months ago
no sight glass,everything is new well about a year old now
we have other units on the basement of this building working just fine this is on the second floor
Customer reply replied 2 months ago
410
Customer reply replied 2 months ago
lineset has been blown through with nitrogen both directions to insure no restrictions in the lineset as well
HVAC Technician: hvacdave84, HVAC Technician replied 2 months ago
Now that you’ve got 9lb in the unit, what are your pressures and line temps?
Ask Your Own HVAC Question
Customer reply replied 2 months ago
those were the pressures after the additional refrigerant
HVAC Technician: hvacdave84, HVAC Technician replied 2 months ago
What this SOUNDS like to me is a TEV issue. But if that has been tried and the condensing unit has been replaced per tech support recommendation, it is likely that it is not. I am Lead Technician at my company. If one of my guys were calling me with this issue, I would have them Record ALL airflow parameters, dry bulb and wet bulb temps, voltages, anything that could be a variable from what the system was designed for, and then, recover the charge, weigh in factory spec charge, (not adding anything for lineset length) check indoor unit to be sure no ice or frost needs to be melted from evaporator, and then run the unit. Attempt to charge it from factory charge by manufacturers spec sheet for subcooling for your specific unit. If you weigh in factory spec yourself, and then reach the recommended additional amount while just trying to bring your subcooling to spec. Don’t go over it.While if this system were 20 years old, we could go through hell changing this and that to try and bring things in line, the fact is that you shouldn’t have to and wouldn’t want to with new equipment.
The next step would be to call your supplier and explain to them that all you can do as a technician, especially with the consideration of not invalidating the warranty, is follow the manufacturer’s instructions, and that you have done that to a T, and cant afford to let your customer continue being disappointed. Request that they send a field Representative to evaluate the situation. Let the field rep take a look, and respectfully ***** ***** they either give you a reasonable diagnosis and plan for repair, or replace the system (the entire system)
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask hvacdave84 Your Own Question
hvacdave84
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 99
99 Satisfied Customers
Experience: ARI and EPA certified

hvacdave84 is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having
I have a Carrier 38Tkb030 320 =2.5 ton unit that I'm having trouble getting more that 10 degrees of cooling between the return and the vent. I've adjusted the charge to the spec in the manual for a pi… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Can you explain me more about expansion valves? What if
Can you explain me more about expansion valves ? What if subcooling is normal ( 10 ) & superheat is high ?… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
What should the supercooling be for rheem air conditioner
What should the supercooling be for rheem air conditioner RAMB-060JAZ? Thanks … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I need help to diagnose a Goodman heat pump with TXV.
I need help to diagnose a Goodman heat pump with TXV. Possible system is miss-matched. I need someone who can also query the Goodman database for the proper part number.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Replaced stuck 410a compressor, weighed in exact charge and
Replaced stuck 410a compressor, weighed in exact charge and did not have any suction pressure, changed txv but I only get 90 psi suction with with a 50 degree suction line and a 27 degree evap I have … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
Hello, Ive been out of the HVAC industry for many years and
Hello, I've been out of the HVAC industry for many years and prefer to service my own HVAC systems (I have two - one upstairs and one down). I'd like an expert to answer three key questions. But first… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Carrier condenser 25HCA342a300, Indoor FV4BNF005, indoor ambient
Carrier condenser 25HCA342a300, Indoor FV4BNF005, indoor ambient 80, outdoor ambient 92, suction pressure 165, superheat 11, liquid pressure 340, subcool 12, charge seems correct, problem is only 8 de… read more
R G
R G
44 satisfied customers
tam unit with 13 seer single stage condensing unit , no sub
tam unit with 13 seer single stage condensing unit , no sub cooling and a 5 degree super heat 130 suction pressure, 225 discharge 410A system.… read more
hvacdave84
hvacdave84
HVAC Technician
99 satisfied customers
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a
I have a 3 ton Trane XL13i mod. # 4TTX3036A 1000AA with a variable speed air handler mod. # XXXXX Does this have a TXV and do you use the superheat or subcooling method for charging? What are reasonab… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a 2.5 ton split system heat pump. Both condenser and
I have a 2.5 ton split system heat pump. Both condenser and air handler is 2.5 tons, 1150 sq ft. Pressures are 138 suction, 370 head. According to the manual, superheat and subcooling should be 7-9 +/… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
just got back into hvac cant remember superheat on how to
just got back into hvac can't remember superheat on how to fiquire by rule of thumb can you help… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
IT is 60F o/s temp today on a unit I must get close to correct
IT is 60F o/s temp today on a unit I must get close to correct charge today. R-22 suc press. is 30# XXXXX line is frosting by evap coil. Is charge to hi? Thanks, Ed… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I am trying to determine if my Lennox HSP26-060-4P is properly
I am trying to determine if my Lennox HSP26-060-4P is properly charged. I am a former HVAC tech, so I know enough to be dangerous. The unit is operating fine at this time. The unit is approximately 7 … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
What is the proper method to diagnose a Bad Indoor TXV on a
What is the proper method to diagnose a Bad Indoor TXV on a heat pump split-system with an Outdoor TXV, such as a Trane System?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I just installed a rheem rapm-36jez with a rhpn-hm3624jc, the
I just installed a rheem rapm-36jez with a rhpn-hm3624jc, the indoor unit sat 3 feet lower then the outdoor unit. it has a 33 foot line set 3/4, 5/16 . I added 4.5 oz of 410 to adjust for the lenth of… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Working on a three year old Amana 3Ton, Seer16 with TXV, R410a
Working on a three year old Amana 3Ton, Seer16 with TXV, R410a Copeland scroll (single speed with bypass for two stages cooling). Running on high, Suction 140 psig, liquid 300 psig, superheat 9F, subc… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
problem unit iced. let it thaw out. gauges read 265/50. outside
problem unit iced. let it thaw out. gauges read 265/50. outside temp 104. inside 80. good air flow. added freon 22. discharge now 275 suction 50. diconnected txv bulb and exposed to out side air. no m… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
Mark, added 16 oz. to system. Outside temp 77f, low side 51psi
Mark, added 16 oz. to system. Outside temp 77f, low side 51psi high side 170psi. Sub. went up to 18f & super up to 25f. Covering condenser raised high side to 185psi low side stayed about the same. In… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x