I have a Miller P3rA 024k central air, and a Miller cmf2 80 PG propane furnace. When I put on my A/C it doesn't blow on the inside, even though both the fans on the unit outside are blowing, and I can't find any leaks in the ductwork under the house.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes, and I replaced the batteries on the thermostat. I hosed off the filtyers on the ac unit outside, and tried to get the frost off the inside.

Contractor's Assistant: Do you plan on doing the work yourself?

If I can I will, it depends on what the problem is.

Contractor's Assistant: Anything else we should know to help you best?

The fan on the unit outside seems okay, but it seems to not get past where it meets the furnace. Is there a problem with the fan on the furnace?

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 2 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Customer reply replied 2 months ago
my phone number is(###) ###-####
Answered in 25 minutes by:
5/27/2018
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far the phone call offer box has not come up on this end, it should in a few minutes,

.

so far it sounds like the compressor is not running

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark that up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.If any of this is beyond your skill sets, or fails, tell me which directionyou are from the center of the nearest town or city and I will locate a well rated service outfit in your area andrun them through my own screening process for you.

.

Or I can coach you to a diagnosis if you have some technical skill sets.

Your question in that case goes beyond 'Just a simple Answer' and will require a few hours training and coaching to a full diagnosis and possible repair … IF you have a multi meter and considerable mechanical skills, rate this answer so far positively and I can do all that for you without any time limits … even if it takes days.

-----------------

That way I do not loose my shirt helping you, you can still refund if I fail.

$25phone calls are 100% optional but will speed up the training,coaching and troubleshooting process in most cases.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark that up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope by the time we are finished that I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. Rating will not increase your charges but it is how I earn a living

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
give me a few minutes to take and send them
Customer reply replied 2 months ago
give me an email address to send the pictures
Customer reply replied 2 months ago
I'll have to open it up again outside to get the wiring diagram, do you want me to do that (it's getting dark here (MA)
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

I got both photo's focus was fuzzy though hard to read. Those were not of the wiring diagrams however, I need the wiring diagrams.

.

Those are *sheets of paper glued to the service panels

click here to see some samples

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark that up with trouble shooting instructions.

.

Your question in this case goes beyond 'Just a simple Answer' and will require a few hours training and coaching to a full diagnosis and possible repair … IF you have a multi meter and considerable mechanical skills, rate this answer so far positively and I can do all that for you without any time limits … even if it takes days.

-----------------

That way I do not loose my shirt helping you, you can still refund if I fail.

please select the 'finish and rate your expert link' near the top of your page and click on it. that will not close the question but will get me paid for this extended coaching that will be required

.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Is there a dedicated fan in the furnace especially for the A/C?
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

There is just one main blower, two speeds, low speed for heat, high speed for cooling and that is controlled by a relay soldered into the printed circuit board

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Are you still there? (the typing is very slow on this)
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

I am here handling about 5 questions at a time, I do not stand by, I post after you respond as soon as I can

Ask Your Own HVAC Question
Customer reply replied 2 months ago
when I put on the (outside air) fan switch in the furnace it doesn't blow cold air, so I didn't know if it came from underneath or from above.
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

It only blows cold if the AC unit located outside is running,

Ask Your Own HVAC Question
Customer reply replied 2 months ago
it's running
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Good work, to close the question please select the 'finish and rate your expert link' near the top of your page and click on it.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
I meant the outside is running, I'll send the wiring diagram for the furnace as soon as I download the picture
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
9,793 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,793 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a HUNTER programmable thermostat. When I went to turn
I have a HUNTER programmable thermostat. When I went to turn on my central air for the first time this season, nothing happen. The temperature in the house says 84 degrees. … read more
hvacdave84
hvacdave84
53 satisfied customers
I have tempstar central a/c. Thermostat set to auto and
Good morning. I have tempstar central a/c. Thermostat set to auto and cool. Inside fan running, heartbeat LED on furnace is blinking normally, outside fan is running (t-bar shows both fuses are workin… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
My cental air is not working in my home. the unit outside is
my cental air is not working in my home. the unit outside is running , but no air is coming out of my vents … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I have a trane xb and the unit will come on the furnace can
I have a trane xb and the unit will come on the furnace can will come on, but it does not make a call to the condenser. So it does not cool down at all. Opened up the door, and receiving a blinking ds… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am using a fan and coil trane, my remote control says yt1f
i have just not been able to make the heating work i mean the mode i am the user not a technician. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I need to purchase a replacement for my furnace and need to
I need to purchase a replacement for my furnace and need to know what model to get .My old one is a serial number 57560388 ,model 3120-751.240 volts,60 Hz and a phase 1 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do I reset a "TB-PAC01-A" unit? It seems to be 'stuck'.
How do I reset a "TB-PAC01-A" unit? It seems to be 'stuck'. None of the buttons work. Display shows something but frozen… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
Need to resolve a roll out fault issue. York P4HUA12L04801A.
Need to resolve a roll out fault issue. York P4HUA12L04801A. Furnace is horizontal discharge left. Verified the heat exchanger is not cracked. Crimped closed the cross over nearest the roll out sensor… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My ac will not stay on it blows cold air only during the
my ac will not stay on it blows cold air only during the purge time then the led light on my zone board blinks green and the out side ac unit stops working ad the cold air stops blowing… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My central air conditioning is not working, checked circuit
My central air conditioning is not working, checked circuit breakers, changed batteries in my Honeywell thermostat, outside compressor does not turn on nor does the fan… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
All of a sudden both of my Venstar thermostats both stopped
All of a sudden both of my Venstar thermostats both stopped working. Tried to reconnect to wifi but it does not accept the WIFI connection. Help ?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a colman evcon furnace that blows fuse when i turn central
Have a colman evcon furnace that blows fuse when i turn central air on. The outside unit is not a coleman.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My AC just went out. I have 2 zones and 3 thermostats,
Hello my AC just went out. I have 2 zones and 3 thermostats, all thermostats are blank (no battery back up), breaker is on and fine, there seems to be no power going to the main units inside including… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
Hi Billy, I inspected a home yesterday morning that had a furnace
Hi Billy, I inspected a home yesterday morning that had a furnace manufactured by Miller (from a mobile home?) Installed in the basement. The S/N is 096855. Was the furnace manufactured in 1996? Also,… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a nordyne/miller (model CMF 80-PG conv.)natural gas
I have a nordyne/miller (model CMF 80-PG conv.)natural gas furnace in my mobile home. Last year I replaced the ignitor and it work fine. This year the furnace will not even begin to start (not even th… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
My central air was working earlier and has stopped delivering
My central air was working earlier and has stopped delivering cool air in the house. The fan in the unit (which is outside) blows air, however the air from the condenser (outside unit) seems to feel c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i am trying to wire a fan center into a Miller mobile home
i am trying to wire a fan center into a Miller mobile home furnace CMF2-80-PG CONV. Do not have a wiring diagram for unit or fan center. how do i wire it for a/c. can you help please… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a cmf2 80-pg its only 7 months old .even week it seem
I have a miller cmf2 80-pg its only 7 months old .even week it seem to have a problem the t stat calls for heat but nothing .I had call a tech two weekend in a row and he gets here and he cant find no… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x