Have a water furnace geo system. Went to replace filter with…

Customer Question
Have a water furnace...

Have a water furnace geo system . Went to replace filter with a water furnace filter and am unable to get filter into unit. Seems to be blocked by something, but see nothing .

Contractor's Assistant: Did you check the furnace's filters?

Same brand and size.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Such as what, please?

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 22 hours by:
5/27/2018
HVAC Technician: Michelle-mod, Moderator replied 2 months ago
Michelle-mod
Michelle-mod, Moderator
Category: HVAC
Satisfied Customers: 12
Experience: Moderator
Verified
Hello:
I'm Michelle, the moderator for this category here on JustAnswer!
I'm so sorry that a JustAnswer Expert has not connected with you yet. I wanted to reach out to see if you still needed assistance with your question?
Please use the reply box below to let me know if you'd like to continue or cancel.
Thank you,
Michelle~Moderator
Ask Your Own HVAC Question
Customer reply replied 2 months ago
but if replies normally take so long, not a service I would want to utilize. Should reply not be received soon, please advise how I cancel program and receive credit for my payment.Thanks.Fred
HVAC Technician: hvacdave84, HVAC Technician replied 2 months ago
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 99
Experience: ARI and EPA certified
Verified
The best way to change the filter is to make sure that the unit is completely off. If the blower is running at all, the air pressure against the filter will pull it into the sheet metal of the filter rack, causing it to snag.
Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask hvacdave84 Your Own Question
hvacdave84
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 99
99 Satisfied Customers
Experience: ARI and EPA certified

hvacdave84 is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Motor kicks on but water is around the furnace but nothing
Motor kicks on but water is around the furnace but nothing else happens it's appears to be leaking a little bit of brown water … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My home ac seems to freeze up. It seems like when i set my
My home ac seems to freeze up. It seems like when i set my thermostat to 77 it does good. But when i go lower than that it freezes every time. I had a friend check it out and it has plenty of freon.… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a 3.5 ton water furnace heat pump, about 3 years old
I have a 3.5 ton water furnace heat pump, about 3 years old and the unit was not cooling. Checked freon, but charge was ok. I concluded that it was the txv valve, and I replaced it. Unit starts up ok,… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Goodman LP furnace that is used as part of a
I have a Goodman LP furnace that is used as part of a geothermal system. The 15 amp breaker for the furnace trips daily. It only seems to trip when running the geo unit. It does not trip when using LP… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am not getting any water flow on my system. I just got
It is an open system with a well. The well is working fine but there is no flow through the waterfurnace… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a WaterFurnance GeoThermal System with a TPCC32U01
I have a WaterFurnance GeoThermal System with a TPCC32U01 thermostat. This afternoon I had some plumbing work done on supply line to my Geothermal unit. I confirmed water is going into main unit. I ha… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
Have a closed loop climate master geo system that is coming
Have a closed loop climate master geo system that is coming up with a E4 low water temp shutdown. I've had original installer look at it, they replaced some glycol and said they didn't know what else … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a G71MPP 36B -070-01 On the heat CFM side I only
I have a G71MPP 36B -070-01 On the heat CFM side I only can get 1045 cfm I need 1200 to run my new Water furnace in heat mode Can I adjust it on the PCB or Do I need to put in a new PCB for a 60C-90 u… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Recently installed 2 3-ton Series 5 Waterfurnace units in new
Recently installed 2 3-ton Series 5 Waterfurnace units in new construction. When the heat strips are on the units are so quiet you could sleep next to them. When the Geo is running and the pumps are o… read more
jhvac
jhvac
2 satisfied customers
water furnace geo thremo unit red emergency light coming on
water furnace geo thremo unit red emergency light coming on unit is about 20 years old have had no problems in recent years in the early years they came out and added a little water to the system and … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Heil furnace Model h9mpv075f12c1 Serial a053259287.
I have a Heil furnace Model h9mpv075f12c1 Serial a053259287. when the furnace comes off low cycle and goes into high the burners shut off. the code is 4 which means limit or rollout switch. I took off… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Quick Question from someone that feels like an idiot right
Quick Question from someone that feels like an idiot right now. We are in a rental house and we just brought a newborn home. I'm wanting to inspect the filters for our air units and have no idea where… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My home is 2400 square feet not including a finished basement
My home is 2400 square feet not including a finished basement that is approx 1200 square feet. I was recently given an estimate to replace a 33 year old Furnace and Central Air Unit. Here is the propo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I HAVE A COLEMAN PRESIDENTIAL 11 MODEL 7663A. I AM UNABLE TO
I HAVE A COLEMAN PRESIDENTIAL 11 MODEL 7663A. I AM UNABLE TO FIND WHERE THE FILTER IS LOCATED.… read more
G Wurtz
G Wurtz
Instructor of HVACR Program
Master's Degree
57 satisfied customers
We installed a Burnham furnace 12 years ago. I has developed
We installed a Burnham furnace 12 years ago. I has developed a crack in the block. I went to a consumer reporting site and it appears that this is standard for the course - they all seem to crack afte… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a geo thermal heat pump,its a paradise unit made by
I have a geo thermal heat pump,its a paradise unit made by water furance.Its the most exspensive heat source per month to run out of any furance I ever had.I can heat my house cheaper by using our 60 … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY UNIT STARTED NOT TO COOL GOOD THEN FROZE UP AND NOW WILL
MY UNIT STARTED NOT TO COOL GOOD THEN FROZE UP AND NOW WILL NOT COOL DOWN AT ALL THIS ALL STARTED AFTER THE PUMP FOR CONDENSATION WENT OUT… read more
Ryan V.
Ryan V.
UA Local 350 Journeyman
High School or GED
6 satisfied customers
I have a Trane System with a XT300 Electronic Thermostat.
I have a Trane System with a XT300 Electronic Thermostat. The display read HOLD -AC and I am unable to get the system to turn on at all. Any suggestions?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.