How do i reset a pressure fault on a armstrong heat pump…

Customer Question
how do i reset a...
how do i reset a pressure fault on a armstrong heat pump model 4shp13le6p-6? it happens every year when need to turn to cooling....ii reset breaker. i thought last time i had to jumper a wire on the pump.
Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 16 minutes by:
5/26/2018
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,823
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, there is either a manual reset button on the high pressure cut out switch inside the heat pump that sits outside the house, OR you can reset it by turning the thermostat to the OFF position, wait one minute then turn it back on.

.

If the high pressure switch did indeed trip, then the outside units condenser coil is likely dirty, they need cleaning every few years using a coil cleaning kit available at most larger hardware stores,

.

If any of this is beyond your skill sets, or fails, tell me which direction you are from the center of the nearest town or city and I will locate a well rated service outfit in your area and run them through my own screening process for you.

.

Or I can coach you to a diagnosis if you have some technical skill sets.

Your question in that case goes beyond 'Just a simple Answer' and will require a few hours training and coaching to a full diagnosis and possible repair … IF you have a multi meter and considerable mechanical skills, rate this answer so far positively and I can do all that for you without any time limits … even if it takes days.

-----------------

That way I do not loose my shirt helping you, you can still refund if I fail.

$25phone calls are 100% optional but will speed up the training,coaching and troubleshooting process in most cases.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark that up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope by the time we are finished that I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. Rating will not increase your charges but it is how I earn a living

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
red and green lights still blinking alternately. i have did the thermostat of and on. when i hold in the resets the fan on pump runs well until released. this happens every year and its 3 years old. they have replaced the control boad before. i remember jumping a wire on thermostat wire area on pump one time. any other suggestions
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

The error codes are very useful.... about 30% of the time, the rest of the time they are not helpful or are simply bogus... trouble shooting by error code is like fixing your car based on the warning lights.

For me to help you on this end I need the following:

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark that up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

Or I can opt out to one of our other experts here, let me know your preference

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Thanks but that is not a wiring diagram, click here for some examples of wiring diagrams

We can go from there

Ask Your Own HVAC Question
Customer reply replied 2 months ago
The lights are a antishort cycle
14BD4C62-4C97-46BC-BAED-...png14BD4C6...png9B47BDD0-FE40-44A6-BB2C-...png9B47BDD...pngF954DAE9-59A0-4797-90F9-...pngF954DAE...png50AFD8C8-139F-4B3C-ABA6-...png50AFD8C...png
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Thanks, ***** ***** wiring diagram are the high pressure switch, S4 marked HI-PS on the upper right hand corner of the wiring diagram, and the low pressure switch marked LO-PS on the upper right hand corner of the diagram,

with the power OFF fit a jumper wire across the LO-PS if the system runs its low on refrigerant or has a restriction in the refrigerant line at the cooling coil.. it would then short cycle and you would get the 'anti short cycle error... if the jumper works, immediately shut the unit down and call in an HVAC service tech to find and repair the leak or restriction,

But first let me know if the jumper allowed the compressor to keep running for up to 2 minutes or not,

no longer, shut it down its not good run the compressor for long periods when its out of refrigerant

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,823
9,823 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,823 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a york heat pump with a YHJF 3.5 ton compressor unit
I have a york heat pump with a YHJF 3.5 ton compressor unit and AHE air handler. Emergency heat turns on all three heating elements in a 15KW unit. Auxiliary heat does not turn on any of the three. An… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
armstrong heatpump with gas backup heat pump keeps quiting
armstrong heatpump with gas backup heat pump keeps quiting I remove 24v wire to defrost board and get a green led and jump 24v to contactor and it starts working. Works a week or two and have to do it… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Armstrong G1B91BUO75B12B-1A, s/n 8404J23843: inducer just comes
Armstrong G1B91BUO75B12B-1A, s/n 8404J23843: inducer just comes on for second or two then shuts off, 120 volt to inducer goes away, r-w jumpered, new board does same thing. Any ideas?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My Rudd zephyr series heat pump keeps burning up low voltage
My Rudd zephyr series heat pump keeps burning up low voltage transformers when swapping from cooling to heating… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a White Rodgers Digital Comfort Set II thermostat that
I have a White Rodgers Digital Comfort Set II thermostat that is about 15 years. I am replacing this with an updated Hunter touch screen. When I opened the cover plate on the older thermostat, I was s… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
new install... I have a honeywell wireless focus pro stat yth
new install... I have a honeywell wireless focus pro stat yth 6320 with optional out door sensor. air handler is an armstrong g2d95ct. and the heat pump is an armstrong 4shp14le. my question is how do… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a used TRANE Heat pump that was installed 6 months ago
I have a used TRANE Heat pump that was installed 6 months ago with the original RiTemp 8085C Thersmostat, the problem I am having is that when the outside temperture drops below lets say 40f and the h… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Trane XC90 that keeps setting intermittently the Open
I have a Trane XC90 that keeps setting intermittently the "Open High Limit Device" error code (4 Flashes). This furnace is about 10 years old. I have changed the filter and cleaned the evaporator to r… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a tappan Model B5BMT60KC where the technitian installed
I have a tappan Model B5BMT60KC where the technitian installed the thermostat wires whereby he jumpered W1 to W2. Does this mean that my heat strips are activated every single time the unit is powered… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Heil two stage natural gas fired hot air furnace (I
I have a Heil two stage natural gas fired hot air furnace (I don't have the model number with me, but it's about 5 years old and I believe 75,000 btu/hr). For several years I've had and continue to ha… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My thermostat is displaying MALF , malfunction I assume. Is
My thermostat is displaying "MALF", malfunction I assume. Is this a problem with the thermostat itself or something with the heat pump/cooling system ?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I had a new Armstrong pump installed to my hot water furnace.
I had a new Armstrong pump installed to my hot water furnace. When I tried to turn the heat on, the button lights for maybe 3 seconds and the system never turn on. NO HEAT. I do have a message to chan… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My heat pump cools in heat mode and heats in cool mode. Nothing
My heat pump cools in heat mode and heats in cool mode. Nothing has been altered. What gives!!!!… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
i have a ruud model # uppb-024jaz 1 1/2 ton a/c unit that
i have a ruud model # XXXXX 1 1/2 ton a/c unit that cools just one room. All of a sudden the high pressure reset (a red button on the outside of the unit) is popping very frequently. I had a technicia… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I am replacing a Honeywell 3611 programable thermostat for
I am replacing a Honeywell 3611 programable thermostat for a heat pump, because the display went blank and heat not coming on. I am replacing it with a Honeywell RTH7600 programmable thermostat. When … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello I have had a Lennox heat pump for about five years.
Hello I have had a Lennox heat pump for about five years. Recently, we had cold weather, about -18 celsius and the auxiliary heat, my gas furnace was called upon. When it warmed up, the heat pump did … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
We tried to turn my AC on for the first time this summer and
We tried to turn my AC on for the first time this summer and it will not go on. We have checked the batteries and reset the thermostat and even reset the breaker box but nothing happenes. We changed i… read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
RAKB-060JAZ just stopped working today for no apparent reason.
Rheem Model# XXXXX just stopped working today for no apparent reason. Checked breakers & thermostat, neither resolved the problem. Fan won't even turn on.… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x