I have a Heil pgx330080k00 heater air conditioning unit.

Customer Question
I have a Heil...

I have a Heil pgx330080k00 heater air conditioning unit . blower motor will not come on when turned on . shows no default code .

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes .

Contractor's Assistant: Do you plan on doing the work yourself?

No i had ahvac guy looking at it but cant figure it out . replaced theinterface board but no change .

Contractor's Assistant: Anything else we should know to help you best?

Wondering if it is low freon would there be a pressure switch .could it be the ECM ?

Submitted: 25 days ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
5/25/2018
HVAC Technician: Phil, Mechanical Engineer replied 25 days ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,479
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, either the power is off to the air handler (check that first)....

OR the 3 amp automotive type fuse pressed into the printed circuit board mounted on the blower is bad, it purple, (check that next)

Or the motor or 24vac transformer is bad, use a multi meter to measure AC voltage between R and C on the thermostat terminal strip located on the printed circuit board,

Tell me what you discover

-----------------------------------------

,

If any of this is beyond your skill sets, or fails, tell me which direction you are from the center of the nearest town or city and I will locate a well rated service outfit in your area and run them through my own screening process for you.

.

Or I can coach you to a diagnosis if you have some technical skill sets.

Your question in that case goes beyond 'Just a simple Answer' and will require a few hours training and coaching to a full diagnosis and possible repair … IF you have a multi meter and considerable mechanical skills, rate this answer so far positively and I can do all that for you without any time limits … even if it takes days.

-----------------

That way I do not loose my shirt helping you, you can still refund if I fail.

$25phone calls are 100% optional but will speed up the training,coaching and troubleshooting process in most cases.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower , that shows where the thermostat wires connect,

and I will mark that up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope by the time we are finished that I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. Rating will not increase your charges but it is how I earn a living

If you need more assistance, please use the reply box and let me know.

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,479
9,479 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,479 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial
I have a Nordyne Furnace Model GL1RA 090C-16B with a serial # XXXXX GLA020805917. I have a problem with the furnace as it is blowing only cold air. I have cleaned the heat sensor, and replaced the air… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem heat pump with electric auxillary heat and a
I have a Rheem heat pump with electric auxillary heat and a Honeywell RTH7500 thermostat. The aux heat does not activate when in the system is set to HEAT although the display indicates the aux heat i… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I am working on a Lennoxgas furnace model # G1603/4-100-1,
I am working on a Lennoxgas furnace model # XXXXX SERIAL # XXXXX Heater burners ignite, main blower comes on, unit heats for about one minute then gas valve loses power, flames go out and five seconds… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have 2 extra wires wrapped around the cable. which one is
I have 2 extra wires wrapped around the cable. which one is the C wire? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell HZ322 and zone 1 is blinking yellow on
I have a Honeywell HZ322 and zone 1 is blinking yellow on the controller board and is sending no power to the thermostat … read more
Phil
Phil
Mechanical Engineer
9,479 satisfied customers
Our HVAC is behaving strangely. It's a split system with the
Our HVAC is behaving strangely. It's a split system with the compressor outside and the evaporator and air handler inside. When our AC cycle begins, everything is fine. But when it ends, the air handl… read more
Phil
Phil
Mechanical Engineer
9,479 satisfied customers
My thermostat has no power and I have no heat, gas, steam
My thermostat has no power and I have no heat, gas, steam Utica boiler 24v . … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a large hot water heat system with 8 zones using
I have a large hot water heat system with 8 zones using wired thermostats all connected to 2 Caleffi ZVR104 relay panels. Each wired thermostat is connected via 2 wires (R and W) on the ZVR's thermost… read more
hvacdave84
hvacdave84
53 satisfied customers
I have a new job where I have to replace the outside
I have a new job where I have to replace the outside condenser which is located on the roof. As you can imagine, there are multiples of condensers on the roof. What is the best way to be absolutely ce… read more
Phil
Phil
Mechanical Engineer
9,479 satisfied customers
I have an innovator series mod g32q3 that when heat is
I have an innovator series mod g32q3 that when heat is called for the exhaust fan starts, you hear a click, then it stops. it has the right light flashing slow (pressure switch open or open rollout sw… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am installing zone valves and can find no wiring diagram
I am installing zone valves and can find no wiring diagram for my very old Aquastat relay type L8048a … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Rheem Criterion II gas furnace and when we moved
I have a Rheem Criterion II gas furnace and when we moved in the furnace did work via the t'stat. Well I bought a new t'stat and hooked up the wire per the labels on the curcit board, B,G,W,Y,O etc. t… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I have a Totaline P374-0300 thermostat the wiring is W,O,G,R,C,Y
I have a Totaline P374-0300 thermostat the wiring is W,O,G,R,C,Y I need to know which wire color goes w/ which letter I have a White, Green, Red, Yellow, Blue and Brown wire.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Getting code alternating fast flash on both lights ,
Customer: I'm Art - getting code alternating fast flash on both lights … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old Goodman gas furnace. The induced draft relay
I have an old Goodman gas furnace. The induced draft relay is clicking in and out every few seconds. Of course the draft blower shuts off as soon as this happens then cuts on then off. Etc. Every once… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Bryant 383kav furnace wont heat. It is not trying to light,
My Bryant 383kav furnace won't heat. It is not trying to light, it does nothing. The blower works if set to on, there are no codes flashing on the control module, a component test shows everything fun… read more
caleb
caleb
63 satisfied customers
Good Morning, I have a honeywell TH8320U1008 thermostat on
Good Morning, I have a honeywell TH8320U1008 thermostat on a brand new seer 16 heatpump with a three stage electric furnace for aux heat. I would like to absolutely minimize the use of the aux heat. I… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x