Unit M/n is 4HP 13L 30P 2A. Init control board has solid red…

Unit M/n is 4HP...

Unit M/n is 4HP 13L 30P 2A. Init control board has solid red led, green not lit. compressor does not run but when the contactor is manually pushed it does run.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Well I did check the thermostat. fan comes on but not the cooling unit. What filters?

Contractor's Assistant: Do you plan on doing the work yourself?

Well I would like to but did call my friend who has a hvac business.

Contractor's Assistant: Anything else we should know to help you best?

No. there is power to the unit. red led on. green led off. contactor can be manually pushed in and unit runs. thermostat seems to be working, turns cooling coil fan on. that's about it I think.

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 3 months ago
I can manually push the contactor in and the compressor runs and fan spins.
Customer reply replied 3 months ago
inside the cooling coil fan runs and air comes out the vents.
Answered in 18 minutes by:
5/10/2018
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,822
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello.

There is a problem with one of the 4 main 24vac controls in the system, you will need a multi meter to do some testing.

.

If any of this is beyond your skill sets, tell me which direction you are from the center of the nearest town or city and I will locate a well rated service outfit in your area and run them through my own screening process for you.

.

If you would like me to train and coach you to a full diagnosis and repair yourself, and have a multi meter and considerable mechanical skills, rate this answer positively and I can do that for you without any time limits.

.

That way I do not loose my shirt helping you.

.

$25phone calls are 100% optional but will speed up the training,coaching and troubleshooting process in most cases.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and the wiring diagram glued inside the electrical controls box mounted INSIDE the unit that sits on a slab outside the house.. and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) tome.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,822
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 3 months ago
ok but those pics will take a few minutes. are you going to be here on line?
Customer reply replied 3 months ago
Sir I fixed it. I think the circuit board was locked out according to the trouble shooting table. I got the circuit board reset, and it came on by itself and I have 18 degree difference between register and return. The unit failed in mid january in the dead of winter when I think it was on a defrost cycle. I left it go because I have gas log backup. I think there might be a problem in that the freon might be teetering on low which would also cause a low pressure alarm. So I will get my friend here with his gauges and 410A bottle. I think we are done.
Customer reply replied 3 months ago
I don't think a call will be necessary. I will fill out your survey very favorably. Sorry it took so long but my neighbor and I were trouble shooting it, he used to install ac units.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,822
9,822 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,822 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Billy. I have another issue with another hvac problem. We
Billy. I have another issue with another hvac problem. We need your help to solve problem.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier central air unit. The fan on the outside
I have a carrier central air unit. The fan on the outside unit stopped working so I put a new fan motor in it. That did not do the trick so I put a capacitor in it and the fan started working but the … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a LENNOX 410a S/N 5810B09181 OR M/N XC21-036-230-04,
i have a LENNOX 410a S/N 5810B09181 OR M/N XC21-036-230-04 … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a lennox m/n xc15-024-230-05 that the fan will not
Hi. I have a lennox m/n xc15-024-230-05 that the fan will not start on. There is power to the unit but I do not see a reset button. I've tried powering down and pulling the main fuses. I'm assuming th… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hello, Im a HVAC technician that ran into a probably today
Hello, I'm a HVAC technician that ran into a probably today with a ruud gas package unit. I found the blower to continuously run, a bad capacitor, and contactor in (which I changed both with the excep… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello my GeoSource 2000 isnt working on heat. The compressor
Hello my GeoSource 2000 isn't working on heat. The compressor doesn't kick on it just runs air, Please help.… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a Honeywell HZ221 2 zone system. Both thermostats are
I have a Honeywell HZ221 2 zone system. Both thermostats are set for cool but zone 1's LED on the control panel has the heat ligth on (solid red). Zone 2 works good. Any ideas?… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a Lennox HVAC system M/N G24M4X-75A-6. System ran fine
I have a Lennox HVAC system M/N G24M4X-75A-6. System ran fine today in 90+ degree heat. Brought it down to a nice cool 72 in home. When I put system in fan only mode, compressor stayed on. I let it ru… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My HVAC has stopped running. The outside unit has just stopped.
My HVAC has stopped running. The outside unit has just stopped. Removing the side unit I see a RED light on. Any suggestions on resetting this unit.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
12 year old Heil gaspack/AC unit. compressor fan not running
12 year old Heil gaspack/AC unit Model # XXXXX S/N L9751 51622. The compressor sounds like it's on but the fan is not running nor is the relay in the controls area pulling in. When you manually push i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,822 satisfied customers
Is the circuit board bad in my Rheem RPML-048JAZ compressor?
Is the circuit board bad in my Rheem RPML-048JAZ compressor? Symptoms are as follows: air handler fan starts at proper room temperature setting; compressor 5 minute delay expires; compressor does not … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier Puron Model# 38EYG060300 The outside HVAC unit is
Carrier Puron Model# ***** The outside HVAC unit is broken. The fan and the compressor doesn't seem to run. I've tried resetting the circuit breaker with no luck. I looked around online and most peopl… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,822 satisfied customers
carrier 5 ton Ac unit 5 years old plus.Outdoor unit not running
carrier 5 ton Ac unit 5 years old plus.Outdoor unit not running nor cooling currently high temps outside 100 plus, thermostat seems to be communicating with furnace and outdoor temp sensor. Was readin… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,822 satisfied customers
Hi Gents, Looks like my AC Condenser has stopped working.
Hi Gents, Looks like my AC Condenser has stopped working. I have an Lennox XC21 Sig Series. The blower on the main unit works and reacts to my thermostat. I check the break box outside and the two fus… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
trip light is on (red) protector open or no compressor power
trip light is on (red) protector open or no compressor power Power is at unit -pushed in toggle and fan starts… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My 2 ton heil heat pump will run when I push in the relay but
My 2 ton heil heat pump will run when I push in the relay but only the compressor hums when turned on by thermostat...think it is thermostat or control board?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,822 satisfied customers
My condensing unit will not run, found the condenser fan motor
My condensing unit will not run, found the condenser fan motor very hot, took it out hooked it up gave it a spin it started and kept running. Put it back in gave it the unit a start call the compresso… read more
Doug Scott
Doug Scott
Owner/Service Technician
Bachelor's Degree
42 satisfied customers
Hello; i have a Ducane 3-ton hvac system, model # 2hp13l36p-1a,
Hello; i have a Ducane 3-ton hvac system, model # XXXXX new in spring 2007. has only been used two out of 3 years, seasonal business that is closed during the winter as well. The outdoor AC/compressor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x