I purchase a honeywell wifi thermostat, but I have a heat pump. trying to figure out the wiring. it seems that the W wire now goes to O/B, but not sure where the W2 wire goes. When the new thermostat calls for AC, it comes out with heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

RTH8580WF is the honeywell wifi

Contractor's Assistant: Do you plan on doing the work yourself?

When the new system was installed, the HVAC guy used a honeywell and wired it for a conventional. it words fine, but I want to add the wifi feature

Contractor's Assistant: Anything else we should know to help you best?

I'm doing the work

Show More
Show Less
Ask Your Own HVAC Question
Answered in 25 minutes by:
5/5/2018
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. Wiring code for the thermostat should be Red to R Blue to C Yellow to Y1 Orange to W/o/b (white) W2 to Aux/e Green to G

Ask Your Own HVAC Question

I have same thermostat. The terminal letters on outside are for heat pump. You will need to go into installer setup and set for heat pump with aux heat. Russ

gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified
gotoman for ac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 3 months ago
No, didn't help. I have no orange wire. Here's the story--At the end of last summer, I had my two AC units replaced with two, 16 seer heat-punps.
I also had two Honeywell THD110D1006 thermostats installed.
We wanted to add multiple programming and wifi capability to our home HVAC, so I purchased two Honeywell RTH8500 WiFi series thermostats.
When I set out to change the first one, I noted that my HVAC guy had wired it for conventional AC and not for Heat Pump.
I had him return (he’s a friend from church) to help me figure out the heat pump wiring. We tried it as illustrated in the manual, however, when the thermostat called for cool, only warm air was returned.
Nothing we did changed that behavior.As I researched, I found many illustrations for an 8-wire configuration, but it took more research to find a wiring diagram for the 6-wire configuration that I had.
I wired the thermostat for heat pump wiring as follows:
RED to RH/RC uses a jumper
Blue to O/B
Green to G
White to AuxE
Yellow to Y
Brown to C
However, the call for cool, still only produced warm air.
I see in the manual, under System Setup that Function 0170 have options for changing the settings for Heat Pump. I am not certain which to use.
I need some help/insight --- Am I missing something?
I’m also having difficulty connecting the wifi to my home wifi network, but I’m convinced I will get that to work.
Customer reply replied 3 months ago
oops....sorry for the poor grammar. I didn't proof-read my post. Function 0190 also has settings for heat pump, but not sure which to use their either.
Thanks.

Do not worry about 190 that is setting reversing valve.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
5,358 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My a/c will not turn on but the heat does. And the old
My a/c will not turn on but the heat does JA: Did you double-check the thermostat's settings? And what about the filters? Customer: yes and the old thermostat turns the a/c on JA: Do you plan on doing… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Reolacing a thermostat which has and all were occupied. a C
Reolacing a White Rogers thermostat which has and all were occupied. a C (weird because it has batteries and the thing didnt work without the C), L W2 , & R, G, O/B , Y. WITH a Honeywell Wifi thermost… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Is available??? I have a trane baystat 240...want to changer
I have a trane baystat 240...want to changer out to a honeywell rthl3550... … read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
Have honeywell 9000 wifi thermostat where do I put the w and
Have honeywell 9000 wifi thermostat where do I put the w and w2 wires. Already have emergency heat wire and o wire.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Our old 7 day programmable kenmore themostat stopped
Our old 7 day programmable kenmore themostat stopped working. Replaced today with wifi 7 day honeywell rth9580, which runs but no coolong. Still89 degrees in house. Fan works. I set systm for heat pum… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I am replacing the old Rodgers with a Honeywell RTH6500
I am replacing the old White Rodgers with a Honeywell RTH6500 Wi-Fi. The old one does not have a C wire. I connect the existing B wire to C terminal and the O wire to O/B and the rest of the wires as … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Greetings - I am attempting to replace my thermostats(Chromotherm
Greetings - I am attempting to replace my thermostats(Chromotherm III) primary and secondary with new WIFI Honeywell thermostats. The wires did not match up on the primary(R, B, Y G, W with another wi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Does the Black (X2) wire currently on the Trane XT500C thermostat
Does the Black (X2) wire currently on the Trane XT500C thermostat connect to the W (O/B) terminal (1st stage heating or reversing valve changeover) or the W2 (AUX) (2nd stage heating or 1st stage aux … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
I have a Bryant Thermidistat (about 10 yrs old) connected to
I have a Bryant Thermidistat (about 10 yrs old) connected to an AC/Heat Package. It was a high end Purion system with 2 stage compressor. The thermostat has failed and I would like to hook up a Honeyw… read more
jhvac
jhvac
2 satisfied customers
I have a RUUD Air Handler UHPL-HM4824JA and a heat pump. The
I have a RUUD Air Handler UHPL-HM4824JA and a heat pump. The wires it has wires for W1, W2, Y1, Y2, B, R, C and G. I replaced the old thermostat with a Honeywell RTH8580WF. It has connections for RC, … read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
purchased a Honeywell wifi thermostat model rth8580wf have
purchased a Honeywell wifi thermostat model rth8580wf have only 4 wires to old thermostat I can run a5th wir no problem. after looking at terminal board in furnace I see the 4 wires from the thrmstat … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a new rudd package heat pump with aux heat 3.5 ton 13
I have a new rudd package heat pump with aux heat 3.5 ton 13 seer trying to wire heat pump to honeywell stat focus pro th622od, The wire on the heat pump are b/w- g/b-y-blue-brown, letters on state to… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
I have a Trane wetherton thermostat #3AAT86B102 for a Trane
I have a Trane wetherton thermostat #3AAT86B102 for a Trane heat pump & cooling system. Wired as follows. B-W-R-Y-G-O-X2. How do I wire it to a Totaline Star Multi- stage wireless receiver. (Heat Cool… read more
hvac-technician
hvac-technician
Service Manager
Vocational, Technical or Trade Scho
62 satisfied customers
I just bought a new thermostat, Honeywell RTH6350/RTH6450 and
I just bought a new thermostat, Honeywell RTH6350/RTH6450 and the old thermostat (Carrier) has W O G R C Y connections. this does not match the honeywell model. Which of the old wires go to the connec… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
Hello, I have a Del-Air/Honeywell thermostat T841A 1670 (2665)
Hello, I have a Del-Air/Honeywell thermostat T841A 1670 (2665) that I want to replace with a Hunter model 44860. There are 7 wires coming out of the wall and are all used: W=white, B=light blue, R=red… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Last question I asked was answered by HVAC Mark Henley. He
Last question I asked was answered by HVAC Mark Henley. He said a Honeywell TH8320 would replace our Honeywell Class 2, LR1620, 8702, T874R1152, which he said is one stage of cooling and 3 stages of h… read more
gotoman for ac
gotoman for ac
HVAC Technician
Associate Degree
5,358 satisfied customers
In my home, I have a Nordyne ( Gibson on outside) Model GB3BM-048K-BB
In my home, I have a Nordyne ("Gibson" on outside) Model GB3BM-048K-BB Air Handler that is used with a Nordyne GS3BA-048KA Split System Air Conditioner for Outdoor Use. I am replacing a Honeywell wall… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My current thermostat has C, W, O, G, Y, G and R all connected.
My current thermostat has C, W, O, G, Y, G and R all connected. Nothing is labeled Aux and nothing has W1 or W2 etc. I can see to connect C, G, Y, O and R but where do I connect W? There is only 1 hol… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x