We have a goodman acnf301016da trying to replace a lennox…

We have a goodman...

We have a goodman acnf301016da trying to replace a lennox thermostat with a honeywell rth111 thermostat the lennox had a common 24v wire that the honeywell said to not use but the unit will not come on

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

The old thermostat lost power so it may be a bad 24v power supply

Contractor's Assistant: Do you plan on doing the work yourself?

Yes i had my daughter install the new thermostat but it did not work can we jump the red and yellow wires to test and see if the unit starts without the thermostat

Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
5/3/2018
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE when we are done. this will credit me for assisting you.

You can jump G and R that will just start the indoor blower if your furnace still has power

Ask Your Own HVAC Question
Customer reply replied 3 months ago
nothing happened. about 6 months ago i had to replace the blower motor capacitor it had gone out

OK I am just checking wiring diagram to guide you..

Ask Your Own HVAC Question

Manual, check page 31, does not show that it has a fuse it unit, so check to see if furnace has 240Vac and then check transorfer output for 24 Vac

https://www.alpinehomeair.com/related/RT6121000R19%2011.2012.pdf

Ask Your Own HVAC Question
Customer reply replied 3 months ago
ok but will have to wait until this weekend its at my daughters house 90 miles from me right now

Bring volt meter and a universal transformer 240 v to 24v

Ask Your Own HVAC Question

OK....

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We are installing a Honeywell thermostat RTH111, the heat
we are installing a Honeywell thermostat RTH111, the heat works but the cool air of a/c doesnt turn on … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Replacing Lennox 36G7101 with Honeywell RTH6450. Need help
Replacing Lennox 36G7101 with Honeywell RTH6450. Need help with wire code for Honeywell Wire CODE CONNECTION LENNOX Y-YELLOW M-ORANGE F-GREEN V-RED R-BLUE… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
AC won't turn on. Not getting 24V signal to contactor . Unit
AC won't turn on. Not getting 24V signal to contactor . Unit runs if contacts are manually engaged. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I would like to install the Honeywell RTH6500WF thermostat.
I would like to install the Honeywell RTH6500WF thermostat. My heating system is a First Co 48HBQB. I turned off the breaker, removed the prior thermostat (Honeywell Pro 400) and labeled the 4 wires (… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a honeywell HZ221 and the heat LED is solid red, Fan
Hello, I have a honeywell HZ221 and the heat LED is solid red, Fan Zone 1&2 are green. However the blower will not turn on. I have a goodman heat pump. Do you have any suggestions?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox SLP98UH series furnace (installed 2014), and
I have a Lennox SLP98UH series furnace (installed 2014), and I have been trying to install a Honeywell wifi thermostat, which is not powering up. My 5 tstat wires are all connected properly and are ea… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550.
I am replacing a Robertshaw 9520 with a Honeywell RTHL3550. We are pretty sure we have all the wires in the correct spots but the compressor is not coming on. The fan comes on and runs fine. This is a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Honeywell TH3210D1004 with 7 wires, the O and B or my issue
Honeywell TH3210D1004 with 7 wires, the O and B are my issue with my new thermostat which B and O are together, I already have a common… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox g5ouh 4 years old. Whe t stat is off diagnostic lights
Lennox g5ouh 4 years old. Whe t stat is off diagnostic lights are in normal mode,when t stat to heat mode. Diagnostic lights both go off,,furnace will not light..fan blower works when switched to on..… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Im replacing a Maple Chase 9600 thermostat with a Honeywell
Im replacing a Maple Chase 9600 thermostat with a Honeywell TH 8320u 1oo8 thermostat.maple chase has 5 wires red white black green .Honeywell has red white yellow green and common. RCis jumpered with … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My daughters heat pump A/C is not running. Honeywell thermostat
My daughters heat pump A/C is not running. Honeywell thermostat is blinking and will not respond to attempted changes. Outside unit is a Lennox model HP263111P and inside is a Lennox model CB19412P. I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
goodman package unit. get cooling but no compressor or condenser
goodman package unit. get cooling but no compressor or condenser fan in heat mode. replaced thermostat and defrost module.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Honeywell Zone Valve head - gets very hot when wired in.
Honeywell Zone Valve head - gets very hot when wired in. Pipes at head, and valve itself are cool. Just the Honeywell Valve head is getting hot. Valve is not responding to Thermostat. The system has f… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi - I replaced my non-programmable Lennonx 51M32 with a programmable
Hi - I replaced my non-programmable Lennonx 51M32 with a programmable honeywell RTH230B. The unit displays time / day and temperature but the cooling / heating functions are not working. Basically the… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Janitrol HPT18-60 with the following wiring Y
I have a Janitrol HPT18-60 with the following wiring: Y= Yellow G= Green R=Red O=Orange W2=White E=Brown C=Blue I have bought a Honeywell RTH7400 and am trying to install it. I wired up to match the l… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I recently install a new 3.5 ton goodman condenser unit and
I recently install a new 3.5 ton goodman condenser unit and used my old lennox air handler as it had a new coil. This is a heat pump system. I also installed a universal thermostat. My problem is I ca… read more
JWetherbee
JWetherbee
High School or GED
2 satisfied customers
Goodman gas heater in hvac system wont run. Also, compressor
Goodman gas heater in hvac system won't run. Also, compressor won't run for cooling. Fan runs in manual.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
i installed a rite temp thermostat on a ICP commercial AC unit
i installed a rite temp thermostat on a ICP commercial AC unit Model AXB030FAC, and I am not getting power to the thermostat... Tech support for the thermostat said that most likely a fuse blown (said… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x