I have a Carrier 58RAV090-115LC that won't stay lit. I just…

Customer Question
Hi Pearl. I have...

Hi Pearl. I have a Carrier 58RAV090-115LC that won't stay lit. I just had a new roof put on and my furnace hangs horizontally from the roof rafters, so I'm sure it got jostled. Anyway, at first, all 4 burners would come on, then I could see the bottom two oscillating from being lit to not being lit. After about 5 seconds of this, the furnace would kill the gas valve and the flames would go out. The flames would light I heard hissing and found a leak in the flex connection. Put a new one one.

Contractor's Assistant: Have you talked to a roofing professional yet?

Yes.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes. I found a leak in the flex connection and fixed that this morning. Now all 4 burners light consitently but the gas gets cut about 20 or so seconds after the house blower turns on. I cleaned the flame sensor, but believe it was working due to the gas getting cut when only 2 burners were active.

Contractor's Assistant: Anything else we should know to help you best?

The purge blower seems to be running just fine. I've reset all the limit sensors (although none seem to have needed it). I haven't checked for exhause pipe blockages, since that check must have passed to have the flames run until the house blower turned on.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
4/4/2018
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

You will likely get a computer generated offer for a phone call but I am not set up for that currently so disregard.

There is a light on the circuit board visible through a small view port in the blower door..what does this light do when it shuts down?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
No view port. I have the side panels off and can see the LED just fine. I get a 34 code. I have cleaned the flame sensor, and now the flame is on long enough for the house circulation blower to start and run for 20-25 seconds. I believe the flame is sensed or this wouldn't happen. Is that right?
Customer reply replied 4 months ago
I'm good with this interface as I'm now at work and will be able to communicate from either here or home via this chat.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

was any wiring compromised...like the ground to furnace maybe?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Also, I might add, that I check how the flames going into the heat exchanger look every fall when I first start up the furnace. They look the same as they always have now that I've fixed a small leak in the flex connection.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

and adding to the ground question....is the flame staying in contact with the flame sensor consistently?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I will check the GND to furnace when I get home. Do you know exactly where the GND line connects to the furnace?
To answer your last question, I noticed the flame may be pulling away from the venturi a bit, but the sensor is always in blue flame.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

The ground is in the main supply to the furnace. Hot, neutral and ground

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Thanks. I'll check it. I can also connect a current meter up to the flame sensor to see what it's doing after the blower turns on. That should tell me if that's what's shutting the system down. If the gas is lighting past the flame sensor, does that mean there's too much air flow through the venturi?
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

The best way to check is to actually use a manometer and attach to recessed allen head test port on leaving side of gas valve. If natural gas we want 3.5 " wc...if propane 10.5" wc.

Just doing a roof should not have changed microamps on the flame sensor...but if the ground was compromised...it will act like a dirty flame sensor.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Agreed.
HVAC Technician: BillyHvac, Journeyman HVAC Tech replied 4 months ago

keep me posted on what you find.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Hi Billy.All 3 wires that come in from the power line are connected. The bare copper wire is connected to the junction box with a sheet metal screw - that one is ground right?I verified the flame sensor is putting out about 4 to 5 microamps when the burners are on. It was not intermittent, but very solid.The burners are lighting and stay on until after the house circulation blower turns on. At that point, and at random times, the gas is shut off by the controller. I've checked the limit switches, the pressure switches, etc. I'm wondering if it's a problem with the vent/flue - since that would have been affected by the new roof. The cap on the vent pipe is a different type than I've ever had before.
Customer reply replied 4 months ago
Oh, I'm getting an LED error code of #34. For a while today, I was getting #31, but now it's #34.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,154
23,154 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a rheem 43vb40E2 gas water heater. When it comes on,
i have a rheem 43vb40E2 gas water heater. When it comes on, pilot light will light, then the burner will light, and then i hear a bit of a hissing noise and the burner goes back out. The electric wate… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Rheem Criterion II. Just replaced blower motor. Now, with
Rheem Criterion II. Just replaced blower motor. Now, with furnace control off the blower runs just fine. But (!) with the furnace turned on, the blower won't start. The pre-purge starts and clears the… read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
Inducer motor runs, HSI glows for several seconds, then no
Inducer motor runs, HSI glows for several seconds, then no gas (gas valve doesn't open). Pressure and switch checkout, roll out switches check out for continuity. Already replaced the control board. I… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Gibson KG6RC080C-16B furnace that is not heating... It
I have a Gibson KG6RC080C-16B furnace that is not heating... It uses Nordyne 624631-a control board and a 904081 gas valve. I am getting a constant flash from the red led on the control board. After r… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How do I get my gas to stay lit instead of going out after
How do I get my gas to stay lit instead of going out after a short 5 second fire up? the error code is 6 flashes which says failure to ignite, which is true, but how do I fix this?… read more
Brian
Brian
Master Electrician / Contractor
Vocational, Technical or Trade Scho
40 satisfied customers
I have a gas forced air furnace in garage (Fedders model CEG080N2CA
I have a gas forced air furnace in garage (Fedders model CEG080N2CA 80,000 btu) which has not been used for several years because previous owner never hooked vent back up after replacing roof. Now I w… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
My White Rodgers 36e gas furnace will not stay lit. Most of
My White Rodgers 36e gas furnace will not stay lit. Most of the time the gas will ignite for 4-5 seconds, then cut off. Occasionally it will not ignite at all. I've cycled the unit on and off several … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Carrier WeatherMaker 8000 that is giving me a code
I have a Carrier WeatherMaker 8000 that is giving me a code 34. I just went and bought a new thermostat because I thought it was the issue. Can anyone help me?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have RHEEM RGPJ-10EBRJR horizontal and up natural gas furnace
I have RHEEM RGPJ-10EBRJR horizontal and up natural gas furnace 7 years old. It worked fine until yesterday, I noticed that it blows cold air. Turning the system off with thermostat did nothing, the b… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a tempstar natural gas furnace model nug5075bfb1 with
I have a tempstar natural gas furnace model nug5075bfb1 with a S8600M ignition module that is giving me trouble. The furnace operates correctly most of the time but occasionally requires multiple trie… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
i have a Coleman dgaa070 bottom draft top burner that will
i have a Coleman dgaa070 bottom draft top burner that will not stay lit. When I light it, it stays lit for 20-30 seconds then shuts down like the flame sensor is not detecting a flame. replaced flame … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem Criterion II Gas furnace and we just had the
I have a Rheem Criterion II Gas furnace and we just had the blower and vents cleaned yesterday. Now the burner will not stay lit. It turns on and stays lit for 10-15 secs and turns off and then tries … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I Have A Ruud silhoute Thermostat tells unit to heat,purge
I Have A Ruud silhoute Thermostat tells unit to heat,purge comes on,then igniter lites furnce then fan comes on. After the fan blower is on for 10 seconds gas shuts off flames go out, blower still run… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My Coleman Evcon comes on for about 3-5 minutes and then goes
My Coleman Evcon comes on for about 3-5 minutes and then goes right back off, can trip thermostat and comes back on and does same, am freezing… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
My Trane xl90 will start up, heat up, then the gas goes off
My Trane xl90 will start up, heat up, then the gas goes off, the main blower stops but the smaller return air / exhaust motor will keep running till you turn off the furnace. If I reset it, most of th… read more
Dan Linger
Dan Linger
Lead Technician / Energy Consultant
Bachelor's Degree
62 satisfied customers
I have a rheem gas package unit. I woke up to house 58 degrees
I have a rheem gas package unit. I woke up to house 58 degrees yesterday. The blower was running and the thermostat was calling for heat but the burners were not lit. I put the system in a few years a… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Comfortmaker Gas furnace The call for heat gets following results.
Comfortmaker Gas furnace The call for heat gets following results. Inducer motor starts, gas valve clicks and gas for pilot flows. HSI ignites pilot gas. The main burners do not light. The HSI/Flame s… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,154 satisfied customers
Coleman Evcon Model BGU07512AX, SER. NBR. XXXXXXXXX Furnace
Coleman Evcon Model BGU07512AX, SER. NBR. XXXXXXXXX Furnace burners light but go out after 5 seconds. Happens when temperature is <50 F. When I heat the control module on the gas line inside the fu… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x