We had a neighborhood power outage 2 Fridays ago. When the…

Customer Question
Hi we had a...

Hi we had a neighborhood power outage 2 Fridays ago. When the power came back on a few hours later the AC did not blow cold. I called a company out but the guy was super shady didn't want to even look at the other things we wanted estimates for (clean coil bc it's been sucking in hot attic air from the small drywall around the supply that feel in from condensation on the copper pipe running from air handler to condenser thru the attic , etc) he put in a new capacitor and hard start to test and the compressor came on but he wanted 700$ when I told him if already ordered a replacement capacitor on Amazon for 9.61$ & the hard start was 15$& takes 5 mins to install both. We declined when he woukdn t troubleshoot further or say how long it would last. Well when he left (with old capacitor in and no hard start) the AC came on and blew cold for 24hrs or so then stopped again it wouldn't go below 78. I installed a hard start and it ran for a bit but still wouldn't cool right. Now it won't blow cold at all. I was told a few yrs ago that the contactor needed to be replaced. I tried cleaning the pads and saw it is pitted on one side of the contactor pad, I hear a slight buzzing from the contactor now also. I replaced both capacitors and thoroughly cleaned the outdoor unit and indoor coil. Only other issue is our thermostat has gone blank a few times recently including during that time, I changed the batteries, it looks like one leaked bc ther es corrosion on terminals. Now another AC guy says he tested and since the line on the contactor to compressor spikes to 68 that the compressor is dead and we should let him install a 2006 trane donde sir he has in back of his truck that he took from a job last week where the lady replaced inside and out. I kept asking if a mismatch system would be okay and he swears it will get us cold air today but I don't want a shoddy job that breaks again in a week. He quoted 400$ to install the used condenser, repair ceiling inside and cut out/pull& clean coil inside (this was before I cleaned it also) & reinsulate the line going thru attic. Frankly he seemed shady. Also our condenser we had the whole system installed in 2004..payne heat pump it says max amps 25 the trans says max 30..some other differences also and the trane is a 3 ton while our system is 2.5ton. He says that is fine. We are in a settlement on the home and moving in 3 months so don't want to put a ton $ in at this point. Could the. Contactor and or thermostat have been fried by the storm? Is there any other alternative and is his suggestion a good idea? He wasn't very thorough either and appears to sub for an had company as he says he can only come after work/430pm.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I do hear a slight increase then decrease in power to the condenser like the compressor or something is getting a signal to come on then doesn't. I replace the fan motor in June 2014 myself and the blower motor and squirrel cage the same time the thermostat is over 10yrs old

Contractor's Assistant: Do you plan on doing the work yourself?

There's no filter in currently and the thermostat comes and goes it flashes cool on and I changed the settings tried turning it off 24hrs etc this has been ongoing 1 week

Contractor's Assistant: Anything else we should know to help you best?

If I can do the work I will otherwise I'll go with the had guy unless you think he sounds shady I'd rather call another one if so

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
4/3/2018
HVAC Technician: Bill, HVAC Technician replied 3 months ago
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
Experience: Service Mgr
Verified

Hello,

I apologize for the delay. Do you still need assistance?

Bill

Ask Your Own HVAC Question
Customer reply replied 3 months ago
the guy tested and showed me.that the contactor has 240 on both sides and then tested the compressor and it spiked at 86 amps which meant it was dead bc the LEA is 73
HVAC Technician: Bill, HVAC Technician replied 3 months ago

I agree the compressor is locked/bad.

What concerns me is the 3 ton outdoor and the 2.5 ton indoor. It is ok to have a larger unit inside, but not outside. His price is exceptionally good....but the unit for replacement I am not comfortable with.

While the price is good I fear it would be lost money. Best case scenario is the unit works ok with a undercharge in it but will be problematic. I know you would like to get fixed, but I would recommend having another contractor look at it...OR have him replace both the indoor and outdoor unit

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Bill Your Own Question
Bill
Bill
Bill, HVAC Technician
Category: HVAC
Satisfied Customers: 111
111 Satisfied Customers
Experience: Service Mgr

Bill is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My ac compressor works fine but the condenser fan will
Hello, my ac compressor works fine but the condenser fan will sometimes not start automatically, especially in the morning, evening or at night. The condenser fan starts fine during the day. When it d… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My ac was making a high pitch noise that I could hear from
Hello, My ac was making a high pitch noise that I could hear from inside. When I went outside to investigate the condenser fan was not turning. I turned the unit off and waited approx. 15 mins and res… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Outside unit on concept 1000 not coming on. Checked breaker
Outside unit on concept 1000 not coming on. Checked breaker box. All is well there. No fan movement in outside unit … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have a carrier central air unit. The fan on the outside
I have a carrier central air unit. The fan on the outside unit stopped working so I put a new fan motor in it. That did not do the trick so I put a capacitor in it and the fan started working but the … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Frozen compressor. Thawed out working again, haven't been able
Frozen compressor. Thawed out working again, haven't been able to check if the compressor and outdoor fan keeps running after the thermostat cooling setting is reach, possible due to a shut contactor;… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have the intertherm 3 ton with a copeland compressor, the
We have the intertherm 3 ton with a copeland compressor, the lead wire coming from the breaker side has shorted where the wire comes into the metal fuse box mounted on the outside of the house. Has do… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 5 Ton Rheem AC, installed just under 8 years ago.
I have a 5 Ton Rheem AC, installed just under 8 years ago. Recently, it appears the compressor doesn't always start when the system cycles. I notice there is no refrigerant flow and the air handler ju… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have 7 R22 4 year old condensing central air conditioner
i have 7 R22 4 year old condensing central air conditioner units that were flooded during sandy. to replace the air handlers and condensers is cost prohibitive. my in house guy recommends just replace… read more
Mike
Mike
High School or GED
14 satisfied customers
I have a 12 year old Trane Model TTB08C4100A4 AC. I just had
I have a 12 year old Trane Model TTB08C4100A4 AC. I just had a service technician from the installer here for a service call. The fan is operating, but no cooling. He said everything checks out OK ele… read more
joeydelia
joeydelia
HVAC-R Tech supermarket refrigeration
182 satisfied customers
I have a split system air conditioning system. Its a Goodman,
I have a split system air conditioning system. It's a Goodman, model CK30-1T (installed in 1997). Hot air was blowing from the air handler, so I checked the condenser unit which is located on my roof.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman AC unit. it works great for a couple hours,
I have a Goodman AC unit. it works great for a couple hours, then it will shut off (indoor fan still working/running) for a couple hours before getting down to temp. It will come back on after a coupl… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Having a problem with my home central AC. the thermostat is
Having a problem with my home central AC. the thermostat is working OK (can hear click to turn on system), the inside air handler fan runs (can hear and feel air coming from registers), the condenser … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,027 satisfied customers
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press
Have a Trane Voyager WCD060 voltage to contactor is 22.6. press contactor compressor comes on with indoor blower evaporator fan does not relay clicks no operation,contactor good any suggestions would … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My rheem RGFD had an above-mounted A-coil. The a-coil was
My rheem RGFD had an above-mounted A-coil. The a-coil was old and fouled with rust and schmutz. I noticed recently that condensation was forming where it usually doesn't, and that the condensate drain… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
My condensing unit will not run, found the condenser fan motor
My condensing unit will not run, found the condenser fan motor very hot, took it out hooked it up gave it a spin it started and kept running. Put it back in gave it the unit a start call the compresso… read more
Doug Scott
Doug Scott
Owner/Service Technician
Bachelor\u0027s Degree
42 satisfied customers
Own a CPLE36-IC air conditioning unit. Neither the fan nor
Own a CPLE36-IC air conditioning unit. Neither the fan nor the compressor kick in when the thermostat is lowered to a setpoint to activate the unit. The fan and air delivery unit in the attic are work… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have a Trane heat pump that is almost 22 years old. Have
I have a Trane heat pump that is almost 22 years old. Have never had a problem until recently when the compressor started running even though turned off at the thermostat. Once running, the unit would… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
my carrier model #38yr outdoor unit will not run neither fan
my carrier model #38yr outdoor unit will not run neither fan or compressor. indoor unit runs… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less