Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES. COMPRESSOR OHMS…

Customer Question
Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES...

Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES. COMPRESSOR OHMS ; C/S 2.5, S/R 3.1, C/R .7. 239 VOLTS. CONTACTOR KICKS IN AND COMPRESSOR DOES NOT START [CAP CHECKS OK BUT CHANGED ANYWAY]. SOMETIMES KICKS INTERNAL OL ON COMMON BUT KICKS RIGHT BACK AFTER SHUT DOWN AND OHM RE CHECK. SOMETIMES DOES NOT KICK OL. UPON ATTEMPT TO START PULLS 51 AMP BUT DROPS IMMEDIATELY TO 10A AND QUICKLY TO .7 A.INITIAL DIAGNOSIS IS BAD 4 MONTH OLD COMPRESSOR. TWO HOURS +- owner of walkin cooler turns power on, unit starts and cools room rather quickly to 38 deg. ??? VOLTAGE CHECKED AT COMP. TERMINALS 239V.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

T- STAT NA, CONTACTOR KICKS IN. NO FILTERS IN WALKIN COOLER.

Contractor's Assistant: Do you plan on doing the work yourself?

DID MOST OF CKS ALREADY. WANT TO KNOW ABOUT COMPRESSOR ISSUES. THIS ACTS LIKE POWER TOOL OR MOTOR WITH BAD SPOT IN ARMATURE. STARTS SOMETIMES NOT OTHERS. NEVER HAD COMPRESSOR DO THAT.

Contractor's Assistant: Anything else we should know to help you best?

ONLY WHAT COULD CAUSE COMPRESSOR TO DO THIS. WEEKENDS ARE BAD TIME TO CALL COPELAND .

Submitted: 19 days ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 24 minutes by:
4/1/2018
HVAC Technician: Phil, Mechanical Engineer replied 19 days ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,309
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, your ohm readings are off, most likely because of poor contact at the test probes, however if those are good ohm readings they are off ( C/S 2.5, S/R 3.1, C/R .7. 239 )

.

c/s and c/r should add up to the r/s reading... if that is not the case, then there is something wrong with one of the motor windings, and that would be the problem.

.

Double check those ohm readings,

,

The drop to 10 amps then .7 amps points directly to partially shorted windings... so in this case the compressor almost certainly bad, except that when the owner turned the system it ran and cooled properly... all of this taken together points to metering errors on your end,...

.... OR possibly a faulity 240volt power switch problem Make sure the 240v is constant,

.

A note about metering errors: I have been in the business for 58 years, I make metering errors all the time, and that is why I always keep taking measurements until I get constant and stable readings ...I never take one measurement and assume its correct. Problems revolve around poor contact with the test probes.

.

Having said all of this ... it is easily possible that you are correct and the problem is intermittent motor winding problems inside the compressor,

.

Triple check all of this, stay in touch without any time limits

.

Ask Your Own HVAC Question
Customer reply replied 18 days ago
c/s 2.5 + c/r .7 = 3.2. s/r = 3.1 seems ok. I think we should ck all [ not many] elect connections and bypass or replace contactor although cu fans run may not have good enough contact for compressor. we did have constant power at compressor terminals but 239v reading doesnt always mean you have power, just volts if you know what I mean.
HVAC Technician: Phil, Mechanical Engineer replied 18 days ago

Hello, your thinking is good on the contactor contacts passing some trace voltage, however if that were the case the fan motor would not be running, its till possible but its a real long shot.

.

you should measure the amp draw on each leg of the compressor wiring when its trying to start...use a clamp around type amp meter,

$50 for a cheap one at a big box store ,$25 at harbor freight, about $140 for the lowest priice Fluke a rugged almost indestructible instrument.

.

click here for some pictures

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 18 days ago

Keep working with it, eventually you will discover whats going on. Stay in touch,

.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,309
9,309 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,309 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a evcon dgato56bdd that the circuit broad blinks
I have a evcon dgato56bdd that the circuit broad blinks continuous and does not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
232 satisfied customers
My central AC unit shuts off soon after it turns on. 5-30
My central AC unit shuts off soon after it turns on. 5-30 seconds … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 10 years old home. From day 1, this house has
I have a 10 years old home. From day 1, this house has always been rented out. Now that the tenant has moved out and I am ready to sell the house. I called a company to clean the vent return only, ins… read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
The screen on my icomfort wifi has gone dark. Since
It came on again on its own and then went dark again… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 9 year old 58mcb060 and it has stopped working. I
We have a 9 year old 58mcb060 and it has stopped working. I reset it 2 times and both times it started. First time it had to grinding noises and shutdown after 1 hr and the 2nd time it made one grindi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have Rheem Classic 90 plus dual comfort control furnace and
Hi Pearl Have Rheem Classic 90 plus dual comfort control furnace and Honeywell RTH 7600 RET 97C themostat. Need to know correct wiring to get 2 speed operation of furnace. Thanks *****: Just to clarif… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I installed a honeywell rth8500 today and it worked and now
hi I installed a honeywell rth8500 today and it worked and now its not … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I had an Thermostat that had the cables in line from the
I had an Thermostat that had the cables in line from the second hole starting with white the second was green orange blue yellow and red in line now I bought a Therm... that is RTH5160 that bring the … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
My A/C unit stopped blowing cold air last night. Checked the
my A/C unit stopped blowing cold air last night. Checked the outside unit and it is humming but fan not going. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
System not working. i threw breaker and rested it. wall
system not working. i threw breaker and rested it. wall display woke up, but system not working … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
I have a weil-mclain cgm-6 natural gas boiler flame not
I have a weil-mclain cgm-6 natural gas boiler flame not shutting off and the circulator pump not turning on. … read more
Rick
Rick
Supervisor
23,596 satisfied customers
I have a model #82v52-2 that is leaking from the plastic cap
i have a model #82v52-2 that is leaking from the plastic cap on top can this be fixed? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How does the belt go back on? Since last night. A picture
How does the belt go back on? JA: I'll do all I can to help. How long have you been dealing with this? Customer: Since last night JA: Do you plan on doing the work yourself? Customer: Yes JA: Anything… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have model AH16X20BA air handler. We know the heat pump
We have coleman model AH16X20BA air handler. We know the heat pump is bad and just want EM heat to come on. Thermostat batteries are good . Power to the heat strips but no fan operation or heat.HELP? … read more
Bill
Bill
Service Mgr
79 satisfied customers
I have a Raypak -055-EN heated that runs for 5 minutes then
I have a Raypak B-055-EN heated that runs for 5 minutes then shuts off. I have replaced the filter, geotherm, pressure sensor switch, cleaned burner and orifices. Do you have any advice? Thanks Tim Mc… read more
Bill
Bill
Service Mgr
79 satisfied customers
I have a question about my condos heating/cooling system.
Hello, I have a question about my condos heating/cooling system … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I need to replace a TRANE Weathertron XT 500 thermostat with
I need to replace a TRANE Weathertron XT 500 thermostat with a HoneywellRTH/2300/RTH221 … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We were painting downstairs for couple days and our HVAC
we were painting downstairs for couple days and our HVAC stopped working and was giving "FVS lockout" code we aerated the basement and tried resetting the HVAC again. it worked for few hours and now s… read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x