Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES. COMPRESSOR OHMS…

Customer Question
Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES...

Copeland CR53KQE-PFV-970 COMPRESSOR ISSUES. COMPRESSOR OHMS ; C/S 2.5, S/R 3.1, C/R .7. 239 VOLTS. CONTACTOR KICKS IN AND COMPRESSOR DOES NOT START [CAP CHECKS OK BUT CHANGED ANYWAY]. SOMETIMES KICKS INTERNAL OL ON COMMON BUT KICKS RIGHT BACK AFTER SHUT DOWN AND OHM RE CHECK. SOMETIMES DOES NOT KICK OL. UPON ATTEMPT TO START PULLS 51 AMP BUT DROPS IMMEDIATELY TO 10A AND QUICKLY TO .7 A.INITIAL DIAGNOSIS IS BAD 4 MONTH OLD COMPRESSOR. TWO HOURS +- owner of walkin cooler turns power on, unit starts and cools room rather quickly to 38 deg. ??? VOLTAGE CHECKED AT COMP. TERMINALS 239V.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

T- STAT NA, CONTACTOR KICKS IN. NO FILTERS IN WALKIN COOLER.

Contractor's Assistant: Do you plan on doing the work yourself?

DID MOST OF CKS ALREADY. WANT TO KNOW ABOUT COMPRESSOR ISSUES. THIS ACTS LIKE POWER TOOL OR MOTOR WITH BAD SPOT IN ARMATURE. STARTS SOMETIMES NOT OTHERS. NEVER HAD COMPRESSOR DO THAT.

Contractor's Assistant: Anything else we should know to help you best?

ONLY WHAT COULD CAUSE COMPRESSOR TO DO THIS. WEEKENDS ARE BAD TIME TO CALL COPELAND .

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 24 minutes by:
4/1/2018
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, your ohm readings are off, most likely because of poor contact at the test probes, however if those are good ohm readings they are off ( C/S 2.5, S/R 3.1, C/R .7. 239 )

.

c/s and c/r should add up to the r/s reading... if that is not the case, then there is something wrong with one of the motor windings, and that would be the problem.

.

Double check those ohm readings,

,

The drop to 10 amps then .7 amps points directly to partially shorted windings... so in this case the compressor almost certainly bad, except that when the owner turned the system it ran and cooled properly... all of this taken together points to metering errors on your end,...

.... OR possibly a faulity 240volt power switch problem Make sure the 240v is constant,

.

A note about metering errors: I have been in the business for 58 years, I make metering errors all the time, and that is why I always keep taking measurements until I get constant and stable readings ...I never take one measurement and assume its correct. Problems revolve around poor contact with the test probes.

.

Having said all of this ... it is easily possible that you are correct and the problem is intermittent motor winding problems inside the compressor,

.

Triple check all of this, stay in touch without any time limits

.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
c/s 2.5 + c/r .7 = 3.2. s/r = 3.1 seems ok. I think we should ck all [ not many] elect connections and bypass or replace contactor although cu fans run may not have good enough contact for compressor. we did have constant power at compressor terminals but 239v reading doesnt always mean you have power, just volts if you know what I mean.
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

Hello, your thinking is good on the contactor contacts passing some trace voltage, however if that were the case the fan motor would not be running, its till possible but its a real long shot.

.

you should measure the amp draw on each leg of the compressor wiring when its trying to start...use a clamp around type amp meter,

$50 for a cheap one at a big box store ,$25 at harbor freight, about $140 for the lowest priice Fluke a rugged almost indestructible instrument.

.

click here for some pictures

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

Keep working with it, eventually you will discover whats going on. Stay in touch,

.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
9,793 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,793 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have had a new Copeland r22 5 tin scroll compressor
Have had a new Copeland r22 5 tin scroll compressor installed. It will not start. Checked wiring ok and per diagram. New capacitor. Good voltage. New contactor. Air fan comes on and runs fine (shares … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I have just installed a new copeland compressor ( model
I have just installed a new copeland compressor ( model zr48k53-pfv-7me)and it won' start. Looks like it is wired right. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Fedders A6Q10F2A-A Fedders A6Q10F2A-A, This season. Within
Compressor will not run (fan ok, no cooling.) Main cap reads 7.55/36.6 mf. Auxillary cap reads 179 mf. Motor run winding 1.0 ohm; start winding 3.0 ohm. OL seems to have continuity.… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
Carrier unit tripping out contactor when high voltage
Carrier unit tripping out contactor when high voltage applied an condenser tries to start … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
What are acceptable impedance readings on a Copeland scroll
What are acceptable impedance readings on a Copeland scroll compressor between the three winding pins 3 ton. Model. ZR32R5 PFV… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
463 satisfied customers
My trane xl15i a/c wont start... with the contactor in I get
my trane xl15i a/c wont start... with the contactor in I get a buzzing noise no fan … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
My central air unit runs but none of my copper lines are
My central air unit runs but none of my copper lines are cool and the air is not blowing cold … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I just installed a zr42k5epfv800 comp. in a customers heat
I just installed a zr42k5epfv800 comp. in a customers heat pump on Friday. After the vaccuume held for four hours I weighted the charge in. The comp. did not sound right and it would not pump. The cha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I just purchase a doublw wide home. The compressor internally
I just purchase a doublw wide home. The compressor internally cycles on off as soon as unit is turned on. I replace cap. Its resistance is 1 ohm, and 2ohm… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We are a Rheem dealer in the Austin, Tx area. On June 15th,
We are a Rheem dealer in the Austin, Tx area. On June 15th, a a customer requested service to his Rheem heat pump which he said was not cooling very well. The unit is Rheem heat pump model RPQL 036 je… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a trane xe80 with a trane xe1000 ac compressor. On a
I have a trane xe80 with a trane xe1000 ac compressor. On a call to cool, the compressor doesn't start. inside blower runs fine. When you manually push in the contactor, the compressor kicks in fine a… read more
Expert
Expert
I have a Carrier 38TDB Compressor that is not starting with
I have a Carrier 38TDB Compressor that is not starting with control board Alternating code 6 fault. I replaced the start relay, compressor relay, fan relay start capacitor, compressor capacitor 7 cont… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
I have a good man CPH24-1AB unit that stopped cooling last
I have a good man CPH24-1AB unit that stopped cooling last night. I checked for 240v to unit, contactor is good, capacitor is good, compressor does not attempt to start. I have 240v between yel & blk … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My AC was blowing but the output wasnt cold. I confirmed
My AC was blowing but the output wasn't cold. I confirmed that the condenser unit outside wasn't kicking in. I could hear a "click" when it was supposed to turn off and on, but the fan wouldn't spin u… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Goodman Package unit model PGB024075-1 purchased new
I have a Goodman Package unit model PGB024075-1 purchased new in 1993. A good unit and not used that much. Ran good last year but this year she wont cool. I set the thermostat to cool and lowered the … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,793 satisfied customers
My compressor wont stay on and we have replaced the kickstart
My compressor wont stay on and we have replaced the kickstart and the start capacitor. Do you have any idea as to whats the matter it?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
have old ptac heat pump, maybe 20 yrs old, made by hqco, but
have old ptac heat pump, maybe 20 yrs old, made by hqco, but sold by either fredriech or fedders, had not been run in a while, started up twice, now wont start, getting power to compressor, run capcit… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Rheem Central Air Conditioner which blew 40 Amp circuit
I have a Rheem Central Air Conditioner which blew 40 Amp circuit breaker in electric panel last night. I reset breaker but it immediately blew again. I turned off breaker and went outside to pull disc… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x