I have a Lennox 2-zone system in my house, less than 6 years…

Customer Question
HI. I have a...

HI. I have a Lennox 2-zone system in my house, less than 6 years old. For the last few months, when I turn on the heater in zone 1 (downstairs), hot air also blows out the INTAKE vent in zone 2 (upstairs). No work of any kind was done in the house, and no ducting was disturbed. What could it be?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters are a month old. Thermostats were both set on heat. Both zones were set at 67, but because of the hot air blowing out the intake vent in zone 2, temp there reached 77 without the heater in zone 2 ever working.

Contractor's Assistant: Do you plan on doing the work yourself?

Well, I don't know what's causing this. That's why I am here asking questions.

Contractor's Assistant: Anything else we should know to help you best?

No, that's it. I pretty much described the issue.

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 15 hours by:
3/29/2018
HVAC Technician: Michelle-mod, Moderator replied 3 months ago
Michelle-mod
Michelle-mod, Moderator
Category: HVAC
Satisfied Customers: 12
Experience: Moderator
Verified
Hello:
I'm Michelle, the moderator for this category. I'm so sorry that an Expert has not connected with you yet. I wanted to reach out to see if you still needed assistance with your question? Please use the reply box below to let me know if you'd like to continue or cancel.
Thank you!
Michelle~Moderator
Ask Your Own HVAC Question
Customer reply replied 3 months ago
I still need assistance with my question. I was hoping for a quicker response from your experts.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 921
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

I think there might be a section of duct from both zones that are over laping and air is transfering somehow fron a loose or dislodged duct joint or panel.

Onsite visual inspection will be required to locate problem area.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Hello again. My house is less than 6 years old. Until a couple of months ago the HVAC system worked flawlessly. No work of any kind was done at my house, so no air ducts could have been moved or dislodged. I am guessing something is malfunctioning internally, and I was hoping one of your experts could have an idea what it could be.
HVAC Technician: Gaztech, HVAC Technician replied 3 months ago

That is a job that needs onsite inspection. I will let the question open for other technician....

Best regards ***** ***** luck..

Gaztech1

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
On the top floor, cool air is coming from the vents only on
On the top floor, cool air is coming from the vents only on one side of the house. The other side of the top floor is not getting any air from the vents.I have a 2 story house with each floor having i… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a lennox c33 with separate upstairs/downstairs zones.
Hi, I have a lennox c33 with separate upstairs/downstairs zones. Both zones are blowing but only the upstairs is blowing cold. Both zones are set to cool/on and the thermostats are set to 72. Upstairs… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have 2 zones, gas furnace, downstairs works fine. upstairs
i have 2 zones , gas furnace , downstairs works fine. upstairs i got no heat, the thermostat clicks but no hot air is blowing in the upstairs rooms … read more
Michael Elgin
Michael Elgin
Technical Management
We have a multilevel home wih central air AC problems such
We have a multilevel home wih central air AC problems such as the need for diferent temps. When on , Central air only blast cold over the whole house. In not wanting to buy a overly expensive mini duc… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Upstairs heat works, blows air. downstairs doesnt. if i turn
Customer: upstairs heat works, blows air. downstairs doesnt. if i turn off the upstairs heat and turn on the downstairs, air blows out of the upstairs vents, even though the upstairs heat is off. I sh… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
i have two thermostats one upstairs one down and gas furnace
i have two thermostats one upstairs one down and gas furnace in the attic. it is cold downstairs and unbearably hot upstairs… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My thermostat is running after it's reached the set temp. Example:
My thermostat is running after it's reached the set temp. Example: It's set at 67 and is reading 77 in the house (and still running).… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Honeywell Thermostat CT3200. Yesterday the lower level
I have a Honeywell Thermostat CT3200. Yesterday the lower level zone would not turn off at the set temperature level (66); I caught it at 73 and turned the thermostat off. Later in the day I turned th… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Is there a way of combining my 2 zones in a Carrier system.
Is there a way of combining my 2 zones in a Carrier system. I want all the cool air from the downstairs zone to get blown upstairs, and vice versa. My house has no AC, but 2 stories, and the lower lev… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
My home was built 5 years ago and I have my honeywell thermostat
My home was built 5 years ago and I have my honeywell thermostat programmed to adjust temperatures at different times during the day when I'm home and when I'm away. However, I often just turn it off … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have zoned thermostats, one downstairs, one upstairs. Honeywell
I have zoned thermostats, one downstairs, one upstairs. Honeywell T8132C model. Furnace in the attic. Just recently, when I turn on the thermostat downstairs, the air (heat in this case) blows upstair… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just moved into a home that has one central air conditioning
I just moved into a home that has one central air conditioning unit but there are two controls - one upstairs and one down (main floor, not a basement) and they are both programmable. I can't seem to … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Hi. I have a single AC unit on the roof. The house was
Hi. I have a single AC unit on the roof. The house was built in 1990, the AC replaced about 2 years ago. The AC unit works really well blowing cold air. My problem is that the upstairs is not getting … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
If I have a HVAC unit that is operating just fine but its
If I have a HVAC unit that is operating just fine but it's too small to keep the upstairs cooled in the heat of the summer can I have an additional small unit installed to cool the upstairs separately… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
HVAC technician diagnosed refrigerant leak in evaporator coil
HVAC technician diagnosed refrigerant leak in evaporator coil (Lennox air handler & compressor outside unit that is over 10 yrs. old). We are planning to stay in the house another 3 to 5 years. We liv… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have 4 bedrooms in the 2nd floor, which includes my master
I have 4 bedrooms in the 2nd floor, which includes my master bedroom. When I turn on the heat, it comes out on the vents ONLY in the master bedroom. NO hot air or no air comes out at all in the other … read more
Randy
Randy
HVAC Technician
Vocational, Technical or Trade Scho
36 satisfied customers
I have a carrier 58 sta with 3 zones attached to it. The heater
I have a carrier 58 sta with 3 zones attached to it. The heater seems to be running too hot or too long, woke up to my house at 81 when all thermostats were set to 68! Could this be a dampener problem… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Central heater not blowing hot air. Need help fixing this.
I have a 2 story home. The upstairs appears to be heating fine. Warm air coming out of the vents and the temperature is fine. Downstairs, cold air coming out of the vent and it's not changing the temp… read more
Patrick
Patrick
Bachelor's Degree
1,269 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x