I have a 50a50-142 it cycles the hot surface igniter on a…

Customer Question
I have a white...

I have a white rogers 50a50-142 it cycles the hot surface igniter on a few times then flashes a 4 flash code

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Couple days

Contractor's Assistant: Do you plan on doing the work yourself?

Yes ... I cleaned the flame sensor and it worked last night but this morning was back to not working so I started checking it when I got home from work

Contractor's Assistant: Anything else we should know to help you best?

If I unplug the molex connector or turn the power off at the breaker it will sometimes light run for a few min then fault out again

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
looking at the wiring diagram and the flash codes it would appear to be limit switch issue. id this a cleanable item like the flame sensor? or is it a replace it ?
Answered in 2 hours by:
3/28/2018
HVAC Technician: gotoman for ac, HVAC Technician replied 4 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. How is filter I furnace. What is model umber of furnace.

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 4 months ago

Something causing the furnace to overheat. Filters o possible bad limit. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a Comfortmaker furnace Model G9MXE0801716A installed
We have a Comfortmaker furnace Model G9MXE0801716A installed new in May 2015. The furnace keeps shutting off intermittently (mostly during the night when the temperature drops) with Error codes 4 and … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trane XB is not firing up. Igniter fires, hear a click, but
Trane XB is not firing up. Igniter fires, hear a click, but no flame. Checked gas, have gas. Did the suck trick on the hose to pressure switch, still no flame, any suggestons… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Buderus Logamax plus 142. Approx 10 days ago the system
I have a Buderus Logamax plus 142. Approx 10 days ago the system shut down with a display of fault code 3c. After 3 resets without success, the burner finally kicked back on with the 4th reset. The sy… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Boiler , propane gas . model HE-4 with White Rogers 50E47-170
Boiler , propane gas . model HE-4 with White Rogers 50E47-170 ignition control . was given model 1013-200 intergrated boiler control . Will this work and is there a wire sketch ?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Gibson kg6rc 100c-16b natural gas furnace that will
I have a Gibson kg6rc 100c-16b natural gas furnace that will ignite for a few seconds then shut off. The control board flashes a constant red light. the fault code is for a false flame or gas valve re… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
TRANE FURNACE: Call for heat. Ignitor lights. Flames come
TRANE FURNACE: Call for heat. Ignitor lights. Flames come from tubes but will not stay lit. After several attempts, the blower comes on, no heat. All of the system sequences appear normal, ie. pre-fan… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Trane xe80 TDE080A945KO I am trying to troubleshoot an intermittent
Trane xe80 TDE080A945KO I am trying to troubleshoot an intermittent stoppage on my Trane xe80 gas furnace. Once or twice a day (beginning 4 days ago) the unit fails to function with an LED trouble cod… read more
type2technician
type2technician
253 satisfied customers
I have a train unit with a white rogers controller. 50A50-571.
I have a train unit with a white rogers controller. 50A50-571. The troubleshooting code is Rapid flashes which indicates normal operation. It starts normal until the flame comes on but only for a few … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Help! I have a Trane XE 90. White Rogers 50A50-474 controller.
Help! I have a Trane XE 90. White Rogers 50A50-474 controller. I had to replace the blower motor because the wheel fan was banging around as the bolt wore out the motor shaft. All else was working fin… read more
johnincolorado
johnincolorado
8 satisfied customers
I have a coleman furnace installed in 1994 model #DGAT090BDD.
I have a coleman furnace installed in 1994 model #DGAT090BDD. The green light is steady flashing which does not match any of the fault codes. I can get the light to remain steady by turning the power … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
HI, i have a Goodman gas furnace thats about 3 years old model
HI, i have a Goodman gas furnace thats about 3 years old model CHPF3642C6AA and the problem im having is the high limit switch. The unit keeps blinking 4 flashes, when the thermostat call for heat, th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi. I have an Armstrong Ultra SX80 gas furnace. It will occassionally
Hi. I have an Armstrong Ultra SX80 gas furnace. It will occassionally stop firing the main burners before the thermostat turns it off, say once every few days, and only after it has been burning for a… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Carrier Weathermaker 8000. After initially heating
I have a Carrier Weathermaker 8000. After initially heating the house from 64 to 69 degrees in the morning , the unit shuts off fine. Its when it tries to start back up within 5 minutes after that fir… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a coleman evcon model DGAT090BDF (in a mobile home).
I have a coleman evcon model DGAT090BDF (in a mobile home). Sometime during the night, the furnace went off. This morning I tried the ignition sequence listed on the instruction label. The combustion … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my furnace isnt working right it was just blowing cold air
my furnace isnt working right it was just blowing cold air last night when i turned it off waited 5mins and turned it on it would work for a little bit but then the warm air turned cold again today th… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a White Rodgers 50A50-473 control board. When trying
I have a White Rodgers 50A50-473 control board. When trying to heat the burner initially ignites then extinguishes. The controller flashes steady 4 times indicating thermal protection device open. Thi… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my white-rodgers 50a50-142 gives me a flame detected when
my white-rodgers 50a50-142 gives me a "flame detected when no call for heat " fault and will not start. Why?… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Hi I have a concord forced air furnace that will ignite for
Hi I have a concord forced air furnace that will ignite for a couple seconds a few times then flash the diag. light seven times to signal that its in lockout due to no ignition. It does ignite for a f… read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x