I have a carrier model 58PAV090-14 furnace that is showing a…

I have a carrier...

I have a carrier model 58PAV090-14 furnace that is showing a code 12. The blower motor comes on for about 90 sec then shuts off. Then the exausht motor kicks on then the glow igniter comes on but no gas comes on to ignite then the furnace just shuts down. Can you please help the wife is freezing?

Contractor's Assistant: Did you check the furnace's filters?

Yes just changed them

Contractor's Assistant: Do you plan on doing the work yourself?

I hope so I have been able to fix every other problem just need help with the diognostics.

Contractor's Assistant: Anything else we should know to help you best?

Furnace is over 20 years old

Show More
Show Less
Ask Your Own HVAC Question
Answered in 12 minutes by:
3/27/2018
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE when we are done. this will credit me for assisting you.

Code 12 is normal after power is interupted, main blower will run 90 sec before restart when t-stat is calling for heat.

This time put t-stat to off then reset power then set t-stat to heat, raise temperature, wait till it fails, THEN get the true error code. It will be either 31, 33, or 34

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Same code 12 before and after. I have attempted to send a video but it just locks up the website and won’t let me send it

OK, when hot surface glows, mesure voltage for 24Vac at gas valve to see if theres power, you should even hear the gas valve do a clicking sound when it energized.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Spiked to 24v when exhaust motor kicked on then stayed at 18v until end of cycle

Good, it goes down to 18 because of amperage draw.

Does Gas valve click when energized?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
No

OK

Its getting power, selenoid valve is drawing but not opening.

Sorry but It would appear to be a defective gas valve.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Does the whole gas valve need to be changed?

Yes, no parts sold seperately

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Damn! Thank you!

Best regards!!

Don't forget to rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
It was not the gas valve. Same damn problem

You said it was getting 24 v on demand ?

so gas should come out if gas valve is good.

Did you check gas pressure inlet pressure? is there any gas coming out?

If its propane, it may be empty tank or bad regulator, or a valve is shut off

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Yup checked all. I am changing the circuit board! I am mentally exhausted.

OK..........

Ask Your Own HVAC Question

There is a inlet and outlet gas pressure tap on the gas valve to check pressure. I would check that before installing a new control board.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 937
937 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im getting an error code of 12 on my carrier furnace, trying
im getting an error code of 12 on my carrier furnace, trying to figure out how to fix it … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have been without heat for more than 24 hours. The
We have been without heat for more than 24 hours. The furnace blower keeps going off. What are error codes 34 and 14? … read more
Gaztech
Gaztech
HVAC Technician
Vocational, Technical or Trade School
937 satisfied customers
I have a Carrier 58 rav furnace/ac unit in the attic, circa
I have a Carrier 58 rav furnace/ac unit in the attic, circa 1995. Honeywell Chronotherm III stat. When calling for heat furnace won't start. But, sometimes it will start normally. I read led codes (21… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Rheem 80 furnace in a rental unit. Renter called
I have a Rheem 80 furnace in a rental unit. Renter called today because furnace fan was only blowing cold air. When I arrived, I cycled the furnace at which point the induction motor and main blower m… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Have a Carrier Infinity Furnace 58CVA110 that is cycling
Have a Carrier Infinity Furnace 58CVA110 that is doing something strange. The t-stat is set for "heat" mode and is set for a few degrees above where the temp is now (it's a Totalline P374-1100FM t-sta… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
we have a Carrier 58mya080 furnace serial #0398a003a get codes
we have a Carrier 58mya080 furnace serial #0398a003a get codes 12 and 13. At call for heat, pre blower comes on for 90 seconds, no gas, no ignition, especially on damp days after heat not used for day… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
intermittent Carrier Weathermaker 9200 displays a continuous
intermittent Carrier Weathermaker 9200 displays a continuous red led light. What does this mean? How do I know if it is red light 1 or red light 2? Thanks!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Payne PG8UAA060135ABJA furnace where the big blower
I have a Payne PG8UAA060135ABJA furnace where the big blower fan comes on instead of the litter exhaust fan that generally comes on just before ignition. What should I do to trouble shoot?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Carrier 58PAV090 (from 2002) furnace stopped coming on a
My Carrier 58PAV090 (from 2002) furnace stopped coming on a few days ago. I have read that it could be that the igniter is not working properly, and I was working to figure out how I can re-light the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
unit comes on but no heat . blows cold air. this is a new
unit comes on but no heat . blows cold air. this is a new house . it's worth mentioning that the maid was here yesterday and changed the settings. we have re set the thermostat but unit blows cold air… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Carrier 58MXA080 Gas Furnace. The furnace will run
I have a Carrier 58MXA080 Gas Furnace. The furnace will run and heat properly for about 5 minutes or until it gets to the temperature setting on the thermostat. I have replaced the ignitor and flame s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier weathermaker 8000 58wav and it shuts down
I have a carrier weathermaker 8000 58wav and it shuts down after running properly for about 5 minutes or so. I then get an error LED blinking message as follows: short blink, long blink, short blink, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace the furnace will not kick on. I have
I have a Carrier furnace the furnace will not kick on. I have replacd the circuit board and nothing. If you pull the 3amp fuse out then the fan will kick on. But the furnace will not ignite or run. Wh… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
carrier furnace 58m code 33 then code 13 jumped rollout
carrier furnace 58m??? code 33 then code 13 jumped rollout to test switch same issue....exhaust blower never comes on ??????… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
150 series carrier furnace, 1999, model 58PAV090-14, serial
150 series carrier furnace, 1999, model 58PAV090-14, serial 2299A07962, unit operates fine only once after interupting 115V power. 2nd call for heat goes to code 34 ignition proving failure, then code… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Carrier gas furnace model 58pav111-20. Control board not calling
Carrier gas furnace model 58pav111-20. Control board not calling for induced draft. Diagnostic code # XXXXX Checked induced draft, pressure switch, blocked vent shutoff switch, flame sensor & rollout … read more
Zev Simfukwe
Zev Simfukwe
High School or GED
23 satisfied customers
Hi there, I have a Carrier Weathermaker 8000. From 1994.
Hi there, I have a Carrier Weathermaker 8000. From 1994. My LED diagnostic light is blinking but I do not have an error code legend on my furnace, so I do not know what the flashes mean. Help!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x