I have a carrier model # 48ES A6011530TP. it won't come on…

Customer Question
I have a carrier...

I have a carrier model # 48ES A6011530TP . it won't come on heat or cool, help!!!

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I changed the filters ,and put new batteries in the thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

When I turn it on at the thermostat, I hear a click like its coming on , but nothing happens

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 hours by:
3/27/2018
HVAC Technician: Michelle-mod, Moderator replied 4 months ago
Michelle-mod
Michelle-mod, Moderator
Category: HVAC
Satisfied Customers: 12
Experience: Moderator
Verified
Hello:
I'm Michelle, the moderator for this category. I'm so sorry that an Expert has not connected with you yet. I wanted to reach out to see if you still needed assistance with your question? Please use the reply box below to let me know if you'd like to continue or cancel.
Thank you!
Michelle~Moderator
Ask Your Own HVAC Question
Customer reply replied 4 months ago
Yeah michelle, i would like to hear from a tech, still having trouble. Thank you
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, the click you hear if its coming from the furnace/ air handler indicates that there is good control power to the thermostat...and that the problem is with the printed circuit board inside the air handler or another problem with the controls.

.

If the click you hear is from the thermostat itself, then there could be a power failure to the furnace/air handler or a blown fuse in that printed circuit board.

.

We can do some tests.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible!
I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,793
9,793 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,793 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
New batteries installed. Thermostat indicates that heat is
New batteries installed. Thermostat indicates that heat is on, but air coming through vents is cold. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a new carrier unit. The drsin line got clogged and
I have a new carrier unit. The drsin line got clogged and the drain pan fulled with water the Drivetstech cc-1 float switch shut tbe system down. Ive cleared the line and emptied the pan of water. The… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier a/c. After a short power outage this
I have a carrier a/c. After a short power outage this morning, my a/c won't come on. The thermostat seems to be stuck. There is a display, but it can't be changed. … read more
Michael Ferryman
Michael Ferryman
110 satisfied customers
How do I adjust the heat to what I want! I press the up and
How do I adjust the heat to what I want! I press the up and down buttons but it won't adjust my heat! … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My AC isn't kicking on. The batteries were low in the
My AC isn't kicking on. The batteries were low in the thermostat so I replaced them but now it won't come on. The thermostat will click on then right back off again. We also replaced the fuses in the … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
3,335 satisfied customers
I have a older white -rodgers thermostat 1F92W-71, it won't
I have a older white -rodgers thermostat 1F92W-71, it won't stop beeping erraticly … read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I changed the batteries on my new carrier thermostat and my
i changed the batteries on my new carrier thermostat and my entire ac system will not run, it comes on for about 30 seconds and then fizzles out, it is a new system by BGE… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Just installed RTHL221. Fan runs but screen will not clear
Just installed RTHL221. Fan runs but screen will not clear when I hold up and down buttons simultaneously. I DID NOT shut off power to furnace during installation. After checking all connections with … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have the Vision PRO TH8000 Series from Honeywell. Our heat
We have the Vision PRO TH8000 Series from Honeywell. Our heat is not working downstairs and when I turn it on it initially says Heat on, then switches to Aux heat and no heat is coming on.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hello-I have two carrier units (one upstairs, one down) and
Hello- I have two carrier units (one upstairs, one down) and Carrier thermostats. Yesterday we had a power surge and the downstairs unit is no responding. I get a code HP when I turn it to Auto mode a… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I have a VisionPRO TH8000 series thermostat. Yesterday it
I have a VisionPRO TH8000 series thermostat. Yesterday it seemed to be cool in the house and so I checked the termostat and it said LO BATTERY so I changed the batteries as they were... I still do not… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a carrier furnace (natural gas) Made in 2000. MDL #
I have a carrier furnace (natural gas) Made in 2000. MDL # XXXXX The furnace will run about five minutes and then the display for the thermostat will go blank. The furnace continues to run. Changed ou… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
MI CENTURY HEAT AND AIR IT WANT LET ME CHANGE FROM HEAT TO
MI CENTURY HEAT AND AIR IT WANT LET ME CHANGE FROM HEAT TO COOL BUT IT LET ME TURN TO THE FAN ON IT BUT IT WAS ALSO CHANGING BY ITSELF… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a carrier a/c unit with a programmable thermostat.
I have a carrier a/c unit with a programmable thermostat. i came home to find nothing on the display. i replaced the batteries and now the a/c won't turn on. what do i do?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a white-rodgers 1F78 thermostat that isntworking.
I have a white-rodgers 1F78 thermostat that isn'tworking. I replaced the batteries and it still doesn't work. It is 4 years old. Why and what can I do to fix it?????????????????… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
We recently moved into a house with a Carrier Cool Share thermostat.
We recently moved into a house with a Carrier Cool Share thermostat. There is nothing in the manual about changing batteries, so I assume this is hard-wired. Is this correct?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My thermostat display on Carrier heater/AC unit is blank. It
My thermostat display on Carrier heater/AC unit is blank. It is electric, not gas. I checked the breakers, they are fine. The filter was dirty, so I changed it. The display does not use batteries. How… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My furnace quit turning on today. I looked at the thermostat
My furnace quit turning on today. I looked at the thermostat and it indicated the batteries were low so I replaced them. I also replaced the filter as it was quite dirty. Now, it appears there is no p… read more
Bill
Bill
High School or GED
318 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x