My 1 year old furnace refuses to operate. Both the red and green LEDs are on solid and the yellow LED flashes 3 times. No power to the thermostat.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I have tried 3 different thermostats with no power showing to any of them Thought it may be the power supply since I replaced the 5A fuse.

Contractor's Assistant: Do you plan on doing the work yourself?

If it is not too complicated.

Contractor's Assistant: Anything else we should know to help you best?

I put a new fuse in but do not know how to test for 24V power

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
3/26/2018
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi, I'm Brian and I'll be happy to help with this.

Since you have lights on the furnace control board, the problem is not with the 24 volt supply. It's more likely a safety switch of some sort has tripped. If your furnace has a drain switch and the drain is plugged that may cause it. If you can give me the make and model number of your furnace, I can look up the fault code and give better information.

Thanks,

Brian

Ask Your Own HVAC Question
Customer reply replied 3 months ago
It is a Ducane 95G2E. I will check the drain, but guess that the problem is electrical. I was replacing the thermostat and may have shorted something out. It was not working well before that, but I thought it was just my Nest thermostat so I was going to replace it with a Honeywell. Now it won't turn on with either. The Nest says that there is no power to the 24V supply.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

Ah, you may have incidentally popped the 3 amp fuse on the furnace control board. It's a plastic fuse that is the same type used in cars. It should be purple or sometimes it's a 5 amp yellow one. It's located on the furnace control board itself behind the blower panel.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
That was my first guess. I replaced the fuse, but still no response. The new fuse seems to be holding.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

What lights are on the furnace control board after replacing the fuse again?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Same as before; the green and red stay on solid. The yellow one flashes 3 times then goes out. The fan starts to cycle but then goes off.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

When you say the fan starts to cycle, do you mean the combustion inducer fan or do you mean the main system blower?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I believe it is the blower fan.
Customer reply replied 3 months ago
No, I tried it again and it is the combustion inducer
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

Ok, the red led is the fault led, the green shows status of heat and the yellow (amber) one shows how much airflow is being called to run from the main blower. If there is a fault, it should show up as a blinking red led. Both red and green on solid indicates normal operation on high heat. After the combustion blower shuts off, does the red led blink a code or do the leds all go out or if other, please explain.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
The red and green stay on steady. The yellow goes out. The panel on the door indicates the red and green should stay lit. It does not say anything about the yellow.
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

I must have the wrong manual for your furnace then. Can you confirm the entire model number of your furnace? It should be something like 95G2UH110... etc or similar

Ask Your Own HVAC Question
Customer reply replied 3 months ago
It is a 95G2UH070BV12-60
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

Thank you for that, it will allow me to be sure I'm on the same page as you!

Ask Your Own HVAC Question
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

Ok I do have the right manual and the codes are still the same as the other one I was looking at. If the red and green led are on, the furnace should fire and stay on until the heat demand is satisfied at which time the green led goes out and the red stays lit (red should always be lit unless there is a problem then it's either out or it flashes). If the furnace doesn't fire, either the demand has been removed, red led on green off (heat no longer called for by thermostat) or there is a problem in the ignition sequence, at which point the red led should flash a fault code.

The yellow led is just an indication of the amount of airflow the main blower should deliver and any flashes indicate normal operation.

I don't understand why your thermostat would appear to have no power when the leds on the furnace indicate power is on and there is a call for heat (green led lit). There is a gremlin somewhere that's for sure.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Thanks for your efforts on my issue. I do believe that I will call in an exterminator (technician) to deal with the gremlin after all.Earl
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

I wish I could have been of more service to you Earl. Thanks for using Just Answer. Best of luck to you sir.

Thanks,

Brian

Ask Your Own HVAC Question
Customer reply replied 3 months ago
No problem. It was worth a try. Best of luck
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 3 months ago

Thanks much,

Brian

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Trane XC80/XL19i system with a W/R 50v61-507
I have a Trane XC80/XL19i system with a W/R 50v61-507 control board on the furnace. initial sympton is a blown 5A low voltage (LV) fuse. If I remove the Honeywell TH8320V1008 thermostat from the wall,… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I've installed a replacement HZ311 zone board to my HVAC
I've installed a replacement HZ311 zone board to my HVAC unit following the failure of the unit. Now I cannot get cooling or heating … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I changed thermostats and now I can't get my AC to kick on.
I changed thermostats and now I can't get my AC to kick on. The blower blows but the condenser outside doesn't run.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My trane xv80 blower will not start since I installed my new
My trane xv80 blower will not start since I installed my new thermostat … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I was trying to install NEST thermostat and later NEST told
I was trying to install NEST thermostat and later NEST told me the R wire is no power. So I check the furnace control and found the fuse is broken. I replace it but it is still no power. Is there a sw… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a Trane xv 95 and a Trane xv ac I just switched to a
Hi I have a Trane xv 95 and a Trane xv ac I just switched to a Nest thermostat and it was working now I have no ac or heat… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I have a York 80 heater and my AC unit won't turn on when I
I have a York 80 heater and my AC unit won't turn on when I switch on the thermostat … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to install a RTF 9580WF Thermostat on a Trane
I am trying to install a RTF 9580WF Thermostat on a Trane HVAC system. I have confirmed a C wire is connected at the FAU. I am completing the install in basic method. Red-Red, Green-Green, White-White… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm looking troubleshooting information on a furnace,
I'm looking for some troubleshooting information on a furnace, red light will not come on. I have power coming to the board, checked reset switch, and fuse… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Billy I have a Lennox Diplomat Furnace model 80MGF2-45a-1,
Billy I have a Lennox Diplomat Furnace model 80MGF2-45a-1, the furnace is firing but I have a flashing LED1 light. I was just working with a Honeywell rep to install a new thermostat, they do not know… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL.
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL. CODE LIGHTS BLINK AT THE SAME TIME SLOW. WHEN THERE IS A DEMAND FOR HEAT THE LIGHTS BLINK FAST AT THE SAME TIME. AFTER A FEW MIN. THE LEFT LI… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have a trane xv95 furnace utilizing a honeywell vision pro
i have a trane xv95 furnace utilizing a honeywell vision pro IAQ thermostat with an equipment interface module. I disconnect the thermostat from the wall for about 5 hour inorder to prep the wall for … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Lennox ac system fuse blows when system starts. Why?
I have Lennox ac system and the fuse #3 amp in blue wire keeps blowing. If jumped system would start and function fine. Now even a 5 amp fuse blows when system starts. Model #CB29M-41-2P AIR HANDLER.… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Air conditioniong unit not running. Reset 3 amp breaker. Power
Air conditioniong unit not running. Reset 3 amp breaker. Power trips breaker again. What to check next.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
intermittent Carrier Weathermaker 9200 displays a continuous
intermittent Carrier Weathermaker 9200 displays a continuous red led light. What does this mean? How do I know if it is red light 1 or red light 2? Thanks!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a propane gas furnace. I installed a outside wood boiler
I have a propane gas furnace. I installed a outside wood boiler type stove. I am trying to wire my thermostat where the fan will cycle automatic without the propane gas firing up. Then i want the prop… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
honeywell focus pro 6000 series with yellow,white,green,blue,red
honeywell focus pro 6000 series with yellow,white,green,blue,red what wires connect to carrier a/c unit wires yellow with blue stripe and brown with yellow stripe… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Question on a Carrier Weathermaker 8000 gas furnace. I replaced
Question on a Carrier Weathermaker 8000 gas furnace. I replaced the air filter and now the thermostat is blank. I followed the instructions on the front of the unit to turn off the power to the unit, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x