I have a Honeywell R7184P control. My burner will start and…

I have a Honeywell...

I have a Honeywell R7184P control. My burner will start and run and then haphazardly shut off and blink green. I have held it down for the 30 seconds but it is not continuously keep the house warm. Any suggestions?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

2 months. I have a wood burning stove and just use the boiler as back up.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

The boiler seems to run fine at times. It kicks on at 140 degrees and shuts down at 180 degrees. The pump runs and the water pressure is around 15-20 psi

Contractor's Assistant: How long has this been going on? And how severe is the problem?

It's a pain. In the morning the house is cold and I have to go reset the control button. Can't figure out why it doesn't restart on its own or shuts off before house is heated

Show More
Show Less
Ask Your Own HVAC Question
Answered in 17 minutes by:
3/26/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,383
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

When was the last time the burner was tuned up? Does it shut down with burner flame present?

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,383
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 3 months ago
A year ago on the tune up. I don’t know if it shuts down with burner flame present because I am sleeping. I have watched the unit start at 70 degrees. Get up to Q 180 degrees. The burner stops. The pump keeps going.
Phone call session started
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,383
24,383 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a question regarding the boiler temperature setting,
I have a question regarding the boiler temperature setting, water pressure and room thermostat. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
Have a buderus gas boiler and an outside woodmaster boiler
have a buderus gas boiler and an outside woodmaster boiler the who installed said he set to come on at 140 so it would only run if the wood got too low outside outside boiler is set at 170 on 180 off … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I am trying to determine what a normal setting is for the
I am trying to determine what a normal setting is for the weil mclain Gold gas boiler water temprature limit switch is? … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a 25 year old Weil McLain Gold GV6 Boiler. I live in
I have a 25 year old Weil McLain Gold GV6 Boiler. I live in the Chicago area and the winter has been unusually mild. i.e. 37 degrees today. But arctic air is coming so I went to double check my boiler… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I'm installing a Heatmor CSS 100 (used) burning boiler
Hi, I'm installing a Heatmor CSS 100 (used) wood burning boiler outside of my house. The boiler is rated at 100,000 BTU's. I have a water baseboard heating system with 2 zones in the system, 1st floor… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Hi ,My name is***** boiler was installed 97 . It was lieakingfrom relief valv
Hi ,My name is***** boiler was installed 97 . It was lieakingfrom relief valve and was under 20psi. I installed a new one . watching it after start up temp stopped at 130 degrees ,pressure went to 30p… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
We have a Burnham Propane Boiler, model Minuteman II, 105,000
We have a Burnham Propane Boiler, model Minuteman II, 105,000 BTU at one of our properties. It's been cleaned, and it still seems to be short cycling. The burners light, the flame is good color, yet i… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Weil Mclain Ultra oil series 2 oil-fired-----setting high limit--seems
Weil Mclain Ultra oil series 2 oil-fired-----setting high limit--seems boiler was pe-set to 140 degrees. I want to set it to 180, when I turn up the high limit to 180 it stills shuts down at 140. It t… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
i have a weil-mclain furnace i had installed in my house in
i have a weil-mclain furnace i had installed in my house in 1978. i did not use it much for heat because of a wood burner. now i stopped burning wood a few years ago and use the oil furnace for the ho… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Hi I have a Weil McLain Oil fired boiler (wgo). The temp of
Hi I have a Weil McLain Oil fired boiler (wgo). The temp of the boiler is running up to 225 degrees. When the temp comes down to around 200 the boiler kicks on. The temp then falls to 180. It rises to… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a Weil Mclain boiler that began blowing water out the
I have a Weil Mclain boiler that began blowing water out the relief valve Sunday. Technician came out and replaced valve, but after running awhile in the morning, started blowing water again, though n… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
HAVE A CROWN GAS HEATING BOILER MODEL ABF-070SPD TEM IN HOUSE
HAVE A CROWN GAS HEATING BOILER MODEL ABF-070SPD TEM IN HOUSE STAY LOW GAUGE ON BOILER READS 140 RAISES TO 150 THAN BUNRER SHUT DOWN THEROSTAT IS IN HOUSE SET TO 80 BUT NEVER GO ABOVE 72. HOW DO I SET… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
ive got an outside wood burning system,open loop water with
i've got an outside wood burning system,open loop water with a circulating pump .it supplies my furnace with 180 degree water into a radiator for my house heat.i'm wanting to drop the water temp.down … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
How is a Honeywell Outdoor Reset Control adjusted in order
How is a Honeywell Outdoor Reset Control adjusted in order to control the on and off recycling of the boiler. The particular model is a Type T475A. There is a temperature bulb attached to the boiler's… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a 25 year old Burnham oil burner that the temp is going
I have a 25 year old Burnham oil burner that the temp is going to 220 degrees and shutting down, all the exterior parts have been replaced -regulator, pressure regulator, air bleeds, expansion tank, a… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a weil-mclain HE II gas fired boiler I need to replace
I have a weil-mclain HE II gas fired boiler I need to replace the aquastat part # XXXXX the honeywell part # XXXXX XXXXX 1135 2 Is there a nother part # XXXXX is under? Where can I get a replacement p… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
L8124A in service and working ok 12 years. LO set 120, HI set
L8124A in service and working ok 12 years. LO set 120, HI set 180,Differential set 12. Burner has been shutting off 135-140 reading on boiler thermometer. Recently started shutting off at 180. Reset H… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Every time the outside temperature drops to the single digits
Every time the outside temperature drops to the single digits or below, our Burnham 2PV seems not to keep up. The inside temp cannot attain the temperature set on the thermoststat. One would expect th… read more
Robert
Robert
Associate Degree
161 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x