Hi, I have an older Bryant furnace. It only has 1 LED indicator. It's flashing 1 short and 2 long.

Contractor's Assistant: Did you check the furnace's filters?

Yes, I replaced the filter, the blower motor is clean, I checked the limit switch and it ohms out at 0.1ish

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

If I can.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 29 minutes by:
3/25/2018
HVAC Technician: Brian HVAC Guy, HVAC Technician replied 4 months ago
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi, I'm Brian and I'll be happy to help with this. Is the main circulation blower running when the 12 flash code is indicating? Also, if you start from power up, does the combustion air inducer fan start to run at all?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a model 340m340mav036080 furnace and it's not staying
hi I have a Bryant model 340m340mav036080 furnace and it's not staying on or giving much heat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,974 satisfied customers
I have a furnace model 350MAV. The main blower motor runs
I have a Bryant furnace model 350MAV. The main blower motor runs but the furnace does not get a call for heat, the igniter does not glow. The hot surface ignition pilot does not heat up. I cleaned the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I'm trying to figure out how to light the pilot on my
Hi. I'm trying to figure out how to light the pilot on my bryant furnace. Seems it went off. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a 310AAV furnace, installed new last year. It's on
I have a Bryant 310AAV furnace, installed new last year. It's on and warm around furnace but doesn't seem to be heating house. Any ideas? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Armstrong High Efficency Furnace. Furnace starts burners run
Armstrong High Efficency Furnace. Furnace starts burners run for about 2 minutes, blower does not run, furnace shuts down on high temp limit. Code flashes 4 times for hight temp limit open circut. Hig… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a furnace with no heat. The blower motor comes on
I have a Bryant furnace with no heat. The blower motor comes on before the inducer motor which is backwards from the way it is designed… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a York Model P3DNB12N08001E. I replaced a flame sensor
I have a York Model P3DNB12N08001E. I replaced a flame sensor today and the two air filters and checked the flue for cleaning. I am getting four red flashes from the error code light. I pulled out my … read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
We Have Bryant 350MAV hot air, automatic ignite gas furnace.
We Have Bryant 350MAV hot air, automatic ignite gas furnace. The furnace was running fine, but then we lost power. We shut off the main breaker (as the electric company told us to) and when power was … read more
Nathan Marshall, MP
Nathan Marshall, MP
Master Plumber,HVAC Tech,Tradesman
Vocational, Technical or Trade School
275 satisfied customers
I have a York Affinity 9.V series and the blower wont come
I have a York Affinity 9.V series and the blower won't come on (neither in heat nor ac mode). Everything else works OK, gas lights, vent motor on and after a few minutes the furnace shuts down. Red li… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi i have a 80+, 90+ upflow furnace 703956A. the problem with
hi i have a 80+, 90+ upflow furnace 703956A. the problem with the unit is that when i turn on the unit and set it to a temp of 75. the unit fires up and goes up from the current room temp of 60 to abo… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Bryant Model 395CAV042075 ACJA gas furnace. The blower
I have a Bryant Model 395CAV042075 ACJA gas furnace. The blower runs but the gas does not fire. Neither the inducer motor or the hot surface igniter is getting power. Are there any interlocks which co… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Payne Furnace PG8UAA060135 and the heat has stopped
I have a Payne Furnace PG8UAA060135 and the heat has stopped working in the house. The LED's are flashing a pattern - one short and three long. I don't have a troubleshooting code decryption manual to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Bryant Plus 90 furance model 398AAVV036080 Fan stays on constantly,
Bryant Plus 90 furance model 398AAVV036080 Fan stays on constantly, heat is not on. Disconnected tstat and fan still stays on LED on circuit board flashes 3 short flashes, then 3 long flashes circuit … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a elite model ghr26q3-75 My problem is that the furnace
I have a elite model ghr26q3-75 My problem is that the furnace will start and run for a bit then shut down it shows a error code of left led on right led slow flash I cleaned filter and then removed f… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I have a Carrier HVAC model 58sta090 and am getting 3 short
I have a Carrier HVAC model 58sta090 and am getting 3 short and 3 long flash on the problem light. Pilot light comes on and burners are ignited for about 1 1/2 minutes. Can you please advise possible … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Lennox G40UHX series furnace, and its not working.
I have a Lennox G40UHX series furnace, and it's not working. The LED #1 red indicator is flashing slow, and the LED #2 indicator green is solid.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have spoken to M Ogalsbee (sp ) about our heater. Had to sign
Have spoken to M Ogalsbee (sp?) about our heater. Had to sign off before we resolved it. It is a carrier 58 STA/STX. The problem seems to be intermitant. Everything triggers fine but there is no flame… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
We have a Bryant central gas furnace that is virtually brand
We have a Bryant central gas furnace that is virtually brand new but has never worked right since we moved into our house. It will come on for a while but then shut itself down and then it will not re… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x