I have a Weil Mclain Ultra 2000 boiler that won't stay lit.

Customer Question
I have a Weil...

I have a Weil Mclain Ultra 2000 boiler that won't stay lit

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A few months. But this morning I can't get my usual tricks to work.

Contractor's Assistant: Do you plan on doing the work yourself?

If I can, yes.

Contractor's Assistant: Anything else we should know to help you best?

Can't think of anything.

Submitted: 3 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 3 months ago
Sorry...Ultra 200 series, not Ultra 2000
Answered in 1 hour by:
3/25/2018
HVAC Technician: Rick, HVAC Supervisor replied 3 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

What do you get for an error message when it shuts down?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
No error messages. It simply cycles through purge, ignition, run...over and over
Customer reply replied 3 months ago
It's been doing this for some time. I can usually convince it by choking the air intake and getting a good solid ignition. But not any more.
HVAC Technician: Rick, HVAC Supervisor replied 3 months ago

When was the last time is was serviced?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I serviced it last year with a WM servicing kit (gasket, ignitor, etc). I've had it open this morning and cleaned it again. Took some emery cloth to the ignitor. There was significant moisture in the chamber so I dried it out with a hair dryer, something I've had to do before.
HVAC Technician: Rick, HVAC Supervisor replied 3 months ago

Sounds like a clogged condensate drain

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I checked it. It's not.
Customer reply replied 3 months ago
At ignition I see flame in the window. If I choke it I can get a more robust flame. But then it goes out.
HVAC Technician: Rick, HVAC Supervisor replied 3 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Sounds good. Thank you.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a ultra 155 weil mclain boiler, the background screen
I have a ultra 155 weil mclain boiler, the background screen stays gray all the time, never changes to a blue screen. is it in a lockout mode boiler is running fine please help brian … read more
hvacdave84
hvacdave84
53 satisfied customers
Code 996 then 630 on weil mclain ultra, This month, no--Have
no--Have several Ultra's and Gold Stars--Installer died and new company servicing me-could not find in manuals code, but see from you note to replace control module … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Phil we need to relace our boiler and they the company
Hi Phil we need to relace our boiler and they the company recommended a wg09 weil mclain water boiler with beckett burner - how do I know if this is the best weil mclain and most efficient? … read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
Our unit thermostat is set at 74 degrees but the temp on the
our unit thermostat is set at 74 degrees but the temp on the thermostat shows 66 degrees. There is little or no heat emitting from the exhaust vent. We live in Big Timber Montana. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have 10113-200 module in VHE furnace, it worked okay last
I have 10113-200 module in VHE furnace, it worked okay last night this morning no heat no green light lit on module. … read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
Weil mclain boiler won't ignite and co2 alarm went off
Customer: weil mclain boiler won't ignite and co2 alarm went off … read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
hello my ultra 105 boiler has a blue screen...when demand is
hello my ultra 105 boiler was working fine this morning. im in Philadelphia pa and temps dropped dramatically....the thermostat is sending signal to boiler for demand...boiler has a blue screen...it c… read more
Expert
Expert
Honeywell Gas valve type VK8115V 1275 on a Weil Mclain Ultra
Honeywell Gas valve type VK8115V 1275 on a Weil Mclain Ultra 105 boiler. Boiler not staying lit. Goes thru cycle, fires for a short time then produces a low vibrating sound and cuts off. My diagnosis … read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have issues with my boiler when we turn on the radiant heat
I have issues with my boiler when we turn on the radiant heat zones, the boiler will randomly shut off and then we have no hot water. It will reset but it happens again a few days to a week later- we … read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I need the replace the boiler in my home in St. Louis, Missouri
I need the replace the boiler in my home in St. Louis, Missouri which has hot water heat and radiators. My home is a two-story, single-family residences, built in 1918, and has about 3,000 square feet… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
Our church has a Weil-McLain cast iron sectional forced draft
Our church has a Weil-McLain cast iron sectional forced draft gas fired hot water boiler M#BG578 (641 MBH input/521 MBH heating capacity output). How old is this boiler? What is the model year? If the… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
Weil Mclain Energy Star XXXXXXXXX 0809) recently installed
Weil Mclain Energy Star XXXXXXXXX 0809) recently installed in our new construction. We do not have the paperwork or specs on this furnace. We need this for the local plumbing inspector for a certifica… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I have a two year old weil mclain ultra series 3 boiler which
I have a two year old weil mclain ultra series 3 boiler which is given me the ignition fault message.… read more
Rick
Rick
HVAC Supervisor
24,414 satisfied customers
I have a crew coming tomorrow to install a new Weil-McLain
I have a crew coming tomorrow to install a new Weil-McLain PUO#3 Ultra oil boiler with a Beckett NX flame retention burner. I just discovered it has an AFUE rating of only 86%, which makes it ineligib… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I programmed my weil mclain boiler but it stays in standby
I programmed my weil mclain boiler but it stays in standby mode. How do I correct that to accept the priority 3 settings… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I h ave an ultra 105 lp boiler and i need to connect a taco
I h ave an ultra 105 lp boiler and i need to connect a taco sr503 switching relay to run the circulators can you tell me where to connect the wires that usually go to t t terminals on the aquastat?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Weill McLain Ultra-105 boiler and its companion Ultra
I have a Weill McLain Ultra-105 boiler and its companion Ultra Plus 40 hot water heater. They were installed seven months ago. My question is about the hot water heater. The thermostat on the hot wate… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Im a contractor and Im working in a weil Mclain boiler the
I'm a contractor and I'm working in a weil Mclain boiler the Ultra 230, series 2, it supplies domestic hot water to an store, the control board display is showing the word E 28 do you know what does i… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x