I Have a Rheem Split Package AC Unit. 4-ton RHLA HM4821JA.

Customer Question
I Have a Rheem...

I Have a Rheem Split Package AC Unit. 4-ton RHLA HM4821JA. Air handler blower runs continuously. No issues with thermostat or wiring. Motor runs even when control board is not connected

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filter is new. Blower runs with thermostat totally disconnected'

Contractor's Assistant: Do you plan on doing the work yourself?

I would like to troubleshoot, narrow down and repair if basic

Submitted: 29 days ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 hours by:
3/24/2018
HVAC Technician: hvacdave84, HVAC Technician replied 29 days ago
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 92
Experience: ARI and EPA certified
Verified
Hello. There are a few things to check. Have you checked to see if any of the furnaces limit switches are open? This would cause the blower to run as a safety precaution. If you check the limits and find a tripped rollout switch, evaluation by a licensed professional will be necessary as the heat exchanger could be compromised. If the heat is running ok and the blower still won’t stop it sounds as if the relay that powers the motor is failed in the closed position. If the blower is wired directly into the control board, a new board will be needed. If it is powered by a contractor, check to make sure the contractor is not stuck closed
Ask Your Own HVAC Question
Customer reply replied 25 days ago
I have been out of town and unable to check the limit switch(es). The Heating and Cooling both appear to cycle correctly. The Blower runs appropriately during those cycles but seems to operate randomly in between the heating or colling cycles. The X13 blower motor is connected directly to line voltage (230 V) and is controlled by 24 Volt from a control board.I swapped the control board with a new one and still have the same issue with the blower motor. I will have an opportunity to check the limit switches this weekend.
Customer reply replied 24 days ago
Got home early and did some testing. I was able to check the limit switches. They are closed and register 0 ohms resistance. I unplugged the heater terminal PL1 on the control board and blower fan still runs. The board is not giving 24v output to turn on fan. I disconnected the low voltage (control) wires from the control board to the X13 motor and blower still runs. I checked the low voltage taps on the X13 motor and there is 0 voltage. What other items should I check? I believe I have traced it back to the X13 motor or motor control module....
HVAC Technician: hvacdave84, HVAC Technician replied 24 days ago
If there is no 24v control input to the x13 control wiring and the motor still runs then the control module on the lead end of the motor is failing. If you are sure that the motor is an X13, there are many aftermarket options, that are made to be used in a wide array of applications. The Emerson rescue line of motors is one example (make sure you’re getting an x13 replacement) I personally have had good luck with the Mars Azure Digimotor. I believe evergreen has an x13 product as well.
Ask Your Own HVAC Question
HVAC Technician: hvacdave84, HVAC Technician replied 24 days ago
This is an X13. No other issues could be at the heart of it. If you remove control wiring completely and the motor still runs, the control module on the motor is failing.
Ask Your Own HVAC Question
HVAC Technician: hvacdave84, HVAC Technician replied 24 days ago
GE • Genteq Evergreen 3/4 HP 230 Volt Replacement X-13 Furnace Blower MotorIf you search this ^^^ you should be able to find a suitable replacement
Ask Your Own HVAC Question
Customer reply replied 24 days ago
Can the control module be repaired? Do I replace the entire control module or do I need to replace the whole motor?
HVAC Technician: hvacdave84, HVAC Technician replied 24 days ago
In order to replace the control module, you would have to contact a Rheem dealer in your area and have it ordered. The X13 replacements, as long as the HP and Voltage are compatible, would be a sufficient repair option that could possibly be more cost effective than having the OEM motor control module replaced
Ask Your Own HVAC Question
Was this answer helpful?
Ask hvacdave84 Your Own Question
hvacdave84
hvacdave84
hvacdave84, HVAC Technician
Category: HVAC
Satisfied Customers: 92
92 Satisfied Customers
Experience: ARI and EPA certified

hvacdave84 is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Furnace blower will kick on for a minute or two then stop.
Furnace blower will kick on for a minute or two then stop. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Oil furnace blower comes on, no flame or ignition. I buy the
oil furnace blower comes on, no flame or ignition JA: Did you check the furnace's filters? Customer: yes JA: Do you plan on doing the work yourself? Customer: I buy the parts JA: Anything else we shou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
How to clean heat exchanger coils, filters have been clean
filters have been clean recently and I am getting an airflow alarm on the thermostat … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
HVAC, 30 year old natural gas furnace, blower starts and
HVAC, 30 year old natural gas furnace, blower starts and heater relay on circuit board immediately clicks off. Does not trip circuit breaker. Thinking bad relay or over amp load condition, maybe dead … read more
Bill
Bill
Service Mgr
80 satisfied customers
Damper stuck closed. How can I remove cover? A couple week -
a couple week - had service out on 1/30 said damper working fine, just stuck … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem furnace blower runs on low but will not run on high
rheem furnace blower runs on low but will not run on high furnace goes off on high heat limit … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
My Rudd furnace blower vibrates the entire house. Research
My Rudd furnace blower vibrates the entire house. Research indicates a motor/fan set screw may need tightening, but I can't see one. Where is it found? Can it be adjusted without removing the motor?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Goodman GVC9 furnace: blower will turn on, but no heat.
Goodman GVC9 furnace: blower will turn on, but no heat. Checked intake and exhaust, they look ok. Flashing code 4 so replaced the filter which needed replacing. Limit switch in middle of unit shows no… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
It seems that one of my TACO zone valve is stuck closed. I
It seems that one of my TACO zone valve is stuck closed. I tried to open it manually by pushing the manual lever up (toward the pipe) all the way, but nothing is flowing. The other zone valve is fine … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My RUUD furnace blower is not turning on. The circuit board
My RUUD furnace blower is not turning on. The circuit board says its a "Limit Switch Open" error. How can I fix this?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x