I need to troubleshoot why my furnace won't fire up. I've…

Customer Question
I need to troubleshoot...

I need to troubleshoot why my furnace won't fire up. I've had trouble with the fan only coming on for 15-20 seconds at a time in the past, which was annoying but it still heated my garage ok. But now the burner and the fan won't come on. Any suggestions ?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

This is an overhead heater, no filters. I shorted out the thermostats terminals to over ride the mercury switch.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

The pilot flame is on. I tried to wire brush the capillary tube I don't know if I was successful. I suspect That is why it won't ignite

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 25 minutes by:
3/22/2018
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,718
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. Stand next to the furnace, Listen to it when it tries to start, you should hear the following sequence

1. Small inducer fan should start

2. You should hear a faint click next, within 3 seconds of the inducer fan starting

3. In 20 to 40 seconds you should hear two more faint clicks

4. You should hear the burners fire

5. in 40 to 90 seconds the main blower should come on

6. it should keep running, if it stops after 2 to 10 seconds, its flame sensor rod is dirty

.

To go further than that test you will need a multi meter and some skill with it and I will need"

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and I will mark them up with trouble shooting instructions.

.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

If the inducer fan starts but nothing else happens, no faint clicks, then the pressure switch needs service or is bad.

.

If the inducer fan does not start at all, then the thermostat, inducer fan, printed circuit board or 24volt caontrol circuit is the problem, you will need a multi meter to discover that, i will coach you.

.

If any or all of that is beyond your skills set range, then tell me which direction you are from the center of the nearest city and i will locate a well rated service outfit for you.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,718
9,718 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,718 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
See your discussion below on your websit - I have the exact
See your discussion below on your websit - I have the exact same problem - The igniter lights the burners - they go for about 8 seconds then on again over and over - then the Limiter opens - turns off… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My name is ***** *****. I have a steam furnace that also has
Customer: Hi my name is ***** *****. I have a steam furnace that also has a hot water zone with a circulation pump. This year the furnace refuses to start. At the honeywell RA832A I have 110vac and 24… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have an old Rheem RRGG model. The capillary tube broke off
I have an old Rheem RRGG model. The capillary tube broke off the mercury flame sensor that plugs into the the old gas valve. Can I replace that valve with a standing pilot gas valve and standard therm… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi Kelly I am still having trouble with my Rinnai Royale inbuilt
Hi Kelly I am still having trouble with my Rinnai Royale inbuilt gas heater, I removed glass and cleaned /vacuumed out fire box, removed 'burner tubes ' and cleaned them, heater worked twice then back… read more
Kelly
Kelly
Owner/Technician
High School or GED
146 satisfied customers
got an early 80s luxair gas furnace it is short cycling when
got an early 80's luxair gas furnace it is short cycling when heat is called for,burners come on, blower comes on then blower shuts off (burners stay on)about 20 seconds, then blower starts again repe… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Furnace breakdown: Comfortmaker about 16 years old with very
Furnace breakdown: Comfortmaker about 16 years old with very little use. Thermostat turned up to 90, Pilot light lit, buzzing sound, blower on but burners won't fire. Last time you helped me the solut… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have a reznor air makeup unit the is not firing. The blower
I have a reznor air makeup unit the is not firing. The blower runs and there is a pilot but no burner flame. How do I troubleshoot. It seems like the gas valve is not opening.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an older Carrier outside package unit with an intermittent
I have an older Carrier outside "package unit" with an intermittent pilot ignition system that quit working. The system powers up, the fan turns on and the pilot lights, but the main burner won't igni… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Heil model NUGK075DG07 gas furnace Troubleshooting
Troubleshooting Heil model NUGK075DG07 gas furnace. Fan, exhaust blower, interlocks: flue temp, rollout, fan control, pressure switch all test ok. Igniter comes on, ignites puff of gas, then goes out.… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have a Peerless boiler with a Honeywell S8610F ignition control
I have a Peerless boiler with a Honeywell S8610F ignition control module. The pilot lights but the burner does not fire. Could this be due to a faulty module?… read more
Rick
Rick
Supervisor
24,233 satisfied customers
where can i obtain a troubleshooting manual for a robert shaw
where can i obtain a troubleshooting manual for a robert shaw 780-715-U ? I have one that fires my propane torches and the pilot light won't come on. I need to trouble shoot to see if it's the control… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Sterling natural gas overhead garage heater 155,000
I have a Sterling natural gas overhead garage heater 155,000 BTU that does not heat my 30' X 40' garage. The exhaust blower comes on first, after about 20 seconds the main blower comes on, and then th… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have a Coleman furnace giving me trouble and no heat. Blower
I have a Coleman furnace giving me trouble and no heat. Blower fan and pilot come on.The burner ignites and turns off too or three times then stays off. After that all we get is cold air blowing throu… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
9,718 satisfied customers
Bard Furnace. Small exhaust fan comes on, igniter starts sparking
Bard Furnace. Small exhaust fan comes on, igniter starts sparking with what looks like a good spark to me, but 70% of the time it won't light the natural gas. Gas flow is then shut off and small exhau… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
Working on older Ruud unit with White Rodgers gas valve and
Working on older Ruud unit with White Rodgers gas valve and mercury sensor. Pilot fires ok off spark ignitor. No main burner fire. Checked Centrifugal switch on vent motor, checked fan limit control. … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a hanging modine heater in garage. has rob.shaw. ignition
i have a hanging modine heater in garage. has rob.shaw. ignition control. unit is not firing .i have gas at the gas valve, auto sparker is sparking, no gas coming out pilot tube. ( i took off tube at … read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have a Janitrol furnace. I am trying to turn on the heat
I have a Janitrol furnace. I am trying to turn on the heat for the first time this year. When I turn up thermostat and switch to heat, nothing happens. If I turn fan to auto, it comes on but blows coo… read more
Rick
Rick
Supervisor
24,233 satisfied customers
Hello, My Furnances Main Burners wont ignite. I hear
Hello, My Furnance's Main Burners won't ignite. I hear a small fan start, The Pilot turns on, the flame ignites, then a few 30 seconds later or so the main Furnace fan turns on - But the main Burners … read more
Rick
Rick
Supervisor
24,233 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x