Last year I had to replace the integrated furnace controller…

Customer Question
Hello. Last year I...

Hello. Last year I had to replace the integrated furnace controller in my Rheem furnace. The replacement I was shipped is a Model 1012-920A. It works fine except when the power goes out and I'm trying to run from a standby generator. When the blower attempts to start, the blower load causes the generator's output voltage to sag, I think it was down to 105 VAC. When that happens, the board seems to reset. The blower runs for not quite a minute, then shutdown. Then the board restarts the ignition process but when the blower is started, the flame goes out. lather, rinse, and repeat. Before changing the board. it worked okay. Any ideas about how to resolve the problem? I have the old board, but the components on the damaged corner are too badly singed to read the color codes and device numbers, so I can't repair it.

Contractor's Assistant: Did you check the furnace's filters?

Yup, new last month

Contractor's Assistant: Do you plan on doing the work yourself?

I opened the access, jumped the safety so that the blower could pull directly from the room. No difference.

Contractor's Assistant: Anything else we should know to help you best?

I didn't measure the frequency change, only voltage, which averaged 124, I think with a low of 105.

Submitted: 2 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 2 months ago
I will probably do it myself.
Answered in 1 hour by:
3/22/2018
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. what is the full load amp rating on the generator,, and its brand and model number...and tell me in great detail how its grounded. So far it sounds like the generator may be slightly undersized.

.

We can go from there.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
It's a 4 kw Generac portable that I've been using for nearly 20 years. It's always run the furnace before. Connected via 4 prong 30 amp cordset to a sub panel. Mating plug from the generator has the ground connection tied to a ground bus bar which is independent from the neutral bus. Both the neutral and ground bus bars are connected via 6 ga solid copper wire to two 8' grounding stakes set 12' apart. Ground connections are clean and tight with little measurable resistance between the plug connector and the ground stake.The generator formerly ran the furnace, both refrigerators, and some lights previous to installing the 62-24084-02 Model 1012-920A furnace control board. I shutdown every circuit in the generator's sub panel except for the furnace, which is on a dedicated circuit, and control board still turned off the gas valve when the blower motor started. The PWR LED remains lit at all times. The OK LED remains lit during the purge, ignitor heating, ignition cycle until the the blower tries to start. When the blower tries to start the gas valve closes and the OK LED blinks.
HVAC Technician: Phil, Mechanical Engineer replied 2 months ago

Thanks, just replacing the printed circuit board, even if the board was not operating correctly should not have causes the generator to stall out. ... unless the blower motor wire connections put power to both its low and high speed windings at the same time.... IF that were the case however, then the furnace would run on utility company power either.

The problem is with the furnace drawing too many amps at start up (due to a bad blower motor, or possibly just a bad run capacitor on the blower motor)... OR a problem with generator output. We should dig into those issues deeply and ignore any real or coincidental issue related to replacing the board for now... (making more than one assumption at a time can lead is in to the all weeds so to speak, so we will test these one at a time).

.

Use a clamp around amp meter to measure amperage draw at your 120v furnace power supply while on city power.. ahead of its transformer or at its breaker in the house control panel, if the motor draws its listed LRA, (locked rotor amperage) for more two seconds when it starts, then the blower motor has a problem... if you see that amperage, then check it on the Neutral wire that feeds the blower motor to be sure that its not a problem with the other furnace components.

Let me know how that goes.

--------------

If the furnace runs well on utility company power, and its blower motor draws LRA for less than 2 seconds, and does not exceed its FLA (full load amperage) the problem is with the generator itself or its wire connections... In that case we will do various load tests on the gnerator independent of the furnace connection using both volt and amperage draw meters,

.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Current draw doesn't seem to exceed 15A. Just for fun I wired the 30amp connector on the generator directly to the furnace. The controller board won't start at all. Searching the internet makes it look like this is not an uncommon problem and it appears insoluble without either replacing the furnace or the generator. Yet another case of bad engineering where the design team made too many assumptions about the operating environment, in this case, line power.I might try figuring out the value of the resistor that burned on the old board and try repairing it.
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
LUX XT500E thermostat is flashing "FAN" and heater won't turn on
My LUX XT500E thermostat has been flashing the word "FAN" and my heater won't turn on because of it. I have tried online suggestions of restarting it and taking out the batteries, then putting them ba… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Why Does My Lennox Dual-Fuel System with Harmony III Go Into
Why Does My Lennox Dual-Fuel System with Harmony III Go Into 3-Hour Furnace Lock-in? My Lennox dual-fuel system with a Harmony III zone controller and 4 zones seems to work correctly with the one poss… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace (Rheem Classic 90 Plus) runs only if the panel is
My furnace (Rheem Classic 90 Plus) runs only if the panel is off. When the panel is replaced, the flame on the burners goes out and the system cycles every few minutes. when I re-set the system and op… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I, I installed a furnace control Board part # 62-24084-82.
I, I installed a furnace control Board part # 62-24084-82. It cycled once and will will not cycle again. all the controls are ok after checking them. any Ideas? … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
This is the same guy with the Goodman furnace control board
Hi, this is the same guy with the Goodman furnace control board / transformer. My plumber said what caused the board to fail was a short in the blower motor from water from AC unit backing up into blo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Goodman GMNTE120-5 It has a furnace/control board
I have a Goodman GMNTE120-5 It has a furnace/control board with this part number B1809925two of the wires have come off two connectors, and the wires are the same color - trying to determine if it mat… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently replaced my furnace control board. The furnace is
I recently replaced my furnace control board. The furnace is a Lennox G40-OUH and the control board was a White Rodgers 50-A65-121-07. The only replacement was a White Rodgers 50A65-843 Universal Boar… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an amana furnace control board with an led flashing 3
I have an amana furnace control board with an led flashing 3 times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I need help with my -Rodgers furnace control board 50e47-060
I need help with my White-Rodgers furnace control board 50e47-060 on a Trane furnace. It has a blinking red light. On the unit it says " steady red light- replace control, blinking red light-referred … read more
type2technician
type2technician
253 satisfied customers
I have a nordyne KG7TC-080D, with a furnace control board
I have a nordyne KG7TC-080D, with a furnace control board #624790/920916. this is a 2-stage upflow unit. Furnace ignites but goes out wihin seconds. flame sensor replaced, still the same issue. Has in… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I think that I may have a bad furnace control board. Trouble
Hello I think that I may have a bad furnace control board. Trouble shooting so far. Two different thermostats with the same behavior. Direct connection of the R&W&G wires make the furnace run continuo… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a frigidaire furnance installed last year and I have
I have a frigidaire furnance installed last year and I have no heat. The power is on the gas is on but the furnace is just blowing cold air. Any suggestions, thanks Bruce… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a RUUD unit and am looking to install a new Honeywell
I have a RUUD unit and am looking to install a new Honeywell thermostat from Costco. The install instructions require the C wire for 24V power. I removed my old thermostat and there are 4 wires (RGBW)… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Honeywell Smart Valve question...not getting 24 volt reading
Honeywell Smart Valve question...not getting 24 volt reading on limit or pressure switchs when calling for Heat. Control Board is rendered good, switches seem fine (actually just jumpered across them … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
Kelvinator furnace control board flashing red continuously.
Kelvinator furnace control board flashing red slowly. Fan is on circulating cold air, inducer blower on, too. No glow, no flame.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
display backlite not working on honeywell thermostat #TH6220D.
display backlite not working on honeywell thermostat #TH6220D. can this be fixed?… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Home furnace wont switch on Ive had a INternational Comfort
Home furnace won't switch on: I've had a INternational Comfort Products furnace in service for about 2 years. It worked fine up until the summer months when we switched the thermostat to "off". We jus… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x