Last year I had to replace the integrated furnace controller…

Customer Question
Hello. Last year I...

Hello. Last year I had to replace the integrated furnace controller in my Rheem furnace. The replacement I was shipped is a Model 1012-920A. It works fine except when the power goes out and I'm trying to run from a standby generator. When the blower attempts to start, the blower load causes the generator's output voltage to sag, I think it was down to 105 VAC. When that happens, the board seems to reset. The blower runs for not quite a minute, then shutdown. Then the board restarts the ignition process but when the blower is started, the flame goes out. lather, rinse, and repeat. Before changing the board. it worked okay. Any ideas about how to resolve the problem? I have the old board, but the components on the damaged corner are too badly singed to read the color codes and device numbers, so I can't repair it.

Contractor's Assistant: Did you check the furnace's filters?

Yup, new last month

Contractor's Assistant: Do you plan on doing the work yourself?

I opened the access, jumped the safety so that the blower could pull directly from the room. No difference.

Contractor's Assistant: Anything else we should know to help you best?

I didn't measure the frequency change, only voltage, which averaged 124, I think with a low of 105.

Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
I will probably do it myself.
Answered in 1 hour by:
3/22/2018
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello. what is the full load amp rating on the generator,, and its brand and model number...and tell me in great detail how its grounded. So far it sounds like the generator may be slightly undersized.

.

We can go from there.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It's a 4 kw Generac portable that I've been using for nearly 20 years. It's always run the furnace before. Connected via 4 prong 30 amp cordset to a sub panel. Mating plug from the generator has the ground connection tied to a ground bus bar which is independent from the neutral bus. Both the neutral and ground bus bars are connected via 6 ga solid copper wire to two 8' grounding stakes set 12' apart. Ground connections are clean and tight with little measurable resistance between the plug connector and the ground stake.The generator formerly ran the furnace, both refrigerators, and some lights previous to installing the 62-24084-02 Model 1012-920A furnace control board. I shutdown every circuit in the generator's sub panel except for the furnace, which is on a dedicated circuit, and control board still turned off the gas valve when the blower motor started. The PWR LED remains lit at all times. The OK LED remains lit during the purge, ignitor heating, ignition cycle until the the blower tries to start. When the blower tries to start the gas valve closes and the OK LED blinks.
HVAC Technician: Phil, Mechanical Engineer replied 4 months ago

Thanks, just replacing the printed circuit board, even if the board was not operating correctly should not have causes the generator to stall out. ... unless the blower motor wire connections put power to both its low and high speed windings at the same time.... IF that were the case however, then the furnace would run on utility company power either.

The problem is with the furnace drawing too many amps at start up (due to a bad blower motor, or possibly just a bad run capacitor on the blower motor)... OR a problem with generator output. We should dig into those issues deeply and ignore any real or coincidental issue related to replacing the board for now... (making more than one assumption at a time can lead is in to the all weeds so to speak, so we will test these one at a time).

.

Use a clamp around amp meter to measure amperage draw at your 120v furnace power supply while on city power.. ahead of its transformer or at its breaker in the house control panel, if the motor draws its listed LRA, (locked rotor amperage) for more two seconds when it starts, then the blower motor has a problem... if you see that amperage, then check it on the Neutral wire that feeds the blower motor to be sure that its not a problem with the other furnace components.

Let me know how that goes.

--------------

If the furnace runs well on utility company power, and its blower motor draws LRA for less than 2 seconds, and does not exceed its FLA (full load amperage) the problem is with the generator itself or its wire connections... In that case we will do various load tests on the gnerator independent of the furnace connection using both volt and amperage draw meters,

.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Current draw doesn't seem to exceed 15A. Just for fun I wired the 30amp connector on the generator directly to the furnace. The controller board won't start at all. Searching the internet makes it look like this is not an uncommon problem and it appears insoluble without either replacing the furnace or the generator. Yet another case of bad engineering where the design team made too many assumptions about the operating environment, in this case, line power.I might try figuring out the value of the resistor that burned on the old board and try repairing it.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My Gas fired furnace comes on ok but shuts the gas off
hello, My Gas fired furnace comes on ok but shuts the gas off before the house is heated and keeps the blower turned on. The flame lasts for about 5 minutes. I have replace the furnace flame … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Carrier 58gfa100 blower quite running last night. pulled
carrier 58gfa100 blower quite running last night. pulled blower and tested with 120v on all speeds runs well/ … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My 23 year old ***** ***** furnace runs 15-20 minutes. It
Customer: My 23 year old ***** ***** furnace runs for about 15-20 minutes. It turns off even though not to temp. Check thermostat voltages and the voltages on the wires are red 27v, white 27v, yelow 0… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
, I have a Carrier Comfort 92 furnace and use it to heat
Hello, I have a Carrier Comfort 92 furnace and use it to heat a hot yoga studio to 112 degrees for several classes throughout the day. The heater was installed about 7 years ago and it has begun to ha… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Carrier 58PAV that is short cycling. The furnace will
I have a Carrier 58PAV that is short cycling. The furnace will work fine for several minutes, burner is killed and furnace goes into shutdown (blower motors runs for x amt of time after burner cuts ou… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My house is under construction and we just converted from oil
My house is under construction and we just converted from oil to NG. Bought a new NG HE boiler by Burnham, an Alpine 150. Then Sandy hit, and I ended up trying to run the boiler off of my Coleman Powe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Can a Lennox Harmony zone system be hooked up to a Carrier
Can a Lennox Harmony zone system be hooked up to a Carrier Vari. speed furnace with a two speed cond.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Phil, The reason I didnt reply before is that the problem
Phil, The reason I didn't reply before is that the problem mostly went away when I replaced the controller board, and I wanted to give it more time before replying. It might be related to the thermost… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Rheem S/N FY5D70F390309955 furnace which is making
I have a Rheem S/N FY5D70F390309955 furnace which is making a "groning noise" when the main blower starts. It has always made this noise but of late it is getting louder. At times the valve will chatt… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Rheem Criterion II furnace in my garage. I have an
I have a Rheem Criterion II furnace in my garage. I have an A/C unit outside. The A/C unit utilizes the furnace blower to cool the house. When I turn on my A/C from the thermostat the unit outside tur… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My arcoaire gas furnace (H9MPV125L20B1) will not start the
My arcoaire gas furnace (H9MPV125L20B1) will not start the combustion blower, stopping the startup procedure at the beginning. I can cycle the circulating air blower on and off with the thermostat whe… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Trane XL80, 2003yr, Have a power outage. Tried to run the furnace
Trane XL80, 2003yr, Have a power outage. Tried to run the furnace with a Honda generator. LED flashes (9) times = check ignitor. Furnace acts like it tries to come on--blower comes on and stays on; th… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Lennox G50UH(X) series furnace that now will not run
I have a Lennox G50UH(X) series furnace that now will not run on standby power. The generator is large enough to run the entire farm and will run the furnace for another house that is the same furnace… read more
Craig
Craig
Electrical Director
Electrical Automation Technician
2,133 satisfied customers
I have a RHEEM model RGDG-05EAUER SERIAL # BR5D302 F1692 5130
I have a RHEEM model RGDG-05EAUER SERIAL # XXXXX F1692 5130 Ac unit and natural gas furnance. The circuit board is a model 1012-920A. The indoor blower motor will not come on when the fan is set to au… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
i have a heil gas furnace with trolatemp zone control, the
i have a heil gas furnace with trolatemp zone control, the exhaust motor runs continually and the furnace has quit firing ,ithink the motor has finally quit because it was hot to the touch when i unpl… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
HVAC fan blows weaker at vents. Is the fan adjustable?
Our house hvac fan does not blow very strong. Gets weaker at vents the further out from the attic unit. Is the fan output adjustable? I turned on the fan only switch to check this. Same output if on h… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Im located in Eddyville Kentucky and we have just had a major
I'm located in Eddyville Kentucky and we have just had a major ice storm. I have no electricity, but i do have a portable generator. i need to heat my home with my furnace. I have a Coleman BCU0712A w… read more
Unavailable
Unavailable
Vocational, Technical or Trade Scho
18 satisfied customers
I have a Lennox Elite G 26 series. It will not ignite when
I have a Lennox Elite G 26 series. It will not ignite when hooked up to a generator. Blower moter runs in the fan on position. Are the electronics to sensitive voltage output of the generator. Ihave e… read more
Al
Al
Master Service Technician
Votec, College, Master Electrical S
24 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x