My trane air circulator is not heating. I have checked all…

My trane air circulator...

My trane air circulator is not heating. I have checked all breakers and replaced the batteries in my thermostat. However, there is no "click" when I turn heat on. We had a similar problem last fall - I thought it was thermostat batteries because it started working again after I replaced them.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

New filter, thermostat is set to heat - 65F - it is 59 in the house right now. I'm not 100% sure the new thermostat batteries are good, but it lights up and seems to be working. It's a buttonless touchscreen model.

Contractor's Assistant: Do you plan on doing the work yourself?

I'd like to.

Contractor's Assistant: Anything else we should know to help you best?

I checked out the circulator itself. There is a single breaker and no fuses that i could find.

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
The air circulator is a electric multispeed model from 2008. The thermostat is a Honeywell touchscreen with no buttons
from the same time.
Customer reply replied 4 months ago
I can turn the fan on/off from the thermostat. We usually have it on all the time to circulate heat throughout the house. When I switch to Fan AUTO and set the temp higher to turn on furnace nothing happens.
Answered in 25 minutes by:
3/21/2018
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 924
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE when we are done. this will credit me for assisting you.

Do you mean you have a electric AIR HANDLER?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
with a heating coil.

will comunicate by text for now, as I need some important info from you.

To assist you I need to know what is make and model of your thermostat, and also your furnace.

if you want to attach pictures that is really helpfull, especially if you are not familiar working on this equipment.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok, let me get all the info for you.
Customer reply replied 4 months ago
The air handler is a TRANE 4TEE3F31B1000AA with electric heater from 2008The Honeywell thermostat is all touchscreen from the same era
Customer reply replied 4 months ago
Still there?

Yes, helping 3 cust right now

Ask Your Own HVAC Question

OK here we go

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok!

Trying to reteive file on that unit

Ask Your Own HVAC Question

Put R-red and W-white together

Ask Your Own HVAC Question
Customer reply replied 4 months ago
do i need to turn the furnace breaker off first?

If you want its only 24 V

Ask Your Own HVAC Question
Customer reply replied 4 months ago
nothing - no spark either.
Customer reply replied 4 months ago
I should mention that the thermostat has batteries. Would the batteries have to be connected to make it work?

NO

OK, now go do the same thing at the furnace control board

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok...back in a few minutes.

You might have a bad wire connection at the W1 terminal,

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It didn't do anything. Just a note - There is a humming near the breaker. I noticed it earlier as well. Goes away when the breaker is off.Is the W1 where the red wire is connected at the furnace?
Customer reply replied 4 months ago
Is the hum a normal "power on" sound?

Thermostat wires connect to the control board

R is red, 24v

W is white for heat

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Cfm led rapidly blinking, the stops and repeats.

Thats cause blower is turning and showing at what speed its turning, 1 blink per 100 CFT

Ask Your Own HVAC Question
Customer reply replied 4 months ago
What about the300 v fuse? How to tell if it is blown
Customer reply replied 4 months ago
What else to try?

Furnace fan would not work if fuse was blown.

So you bypassed R an W and no heat elements came on just fan?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
No fan either. But the led stopped blinking

Bypass R and G at the furnace to see if fan starts

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Nothing

I thougt you said at the begining that if you set to fan on it would start

Ask Your Own HVAC Question

wiring diagram shows fuse is in fuse holder. red wire

Ask Your Own HVAC Question

Hello???

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok, so the fan no longer turns on from the thermostat. That green blinking led on the furnace stopped bliking when I was bypassing the red and white.
Customer reply replied 4 months ago
The fuse was white.

does terminal R and W have red and white wire?

You may have touched the B terminal and burnt fuse.

Test fuse with ohm meter to see if blown

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ok.can I contact you again tomorrow? Hardware store is closed. I will replace fuse and pick it up again tomorrow if that's ok.

Ok get a couple of 5 amp fuses

Ask Your Own HVAC Question
Customer reply replied 4 months ago
5amo 300v?

Shure, same as what it had

Ask Your Own HVAC Question

You never answered

does terminal R and W have red and white wire?You may have touched the B terminal and burnt fuse.
Ask Your Own HVAC Question
Customer reply replied 4 months ago
W = white wire
RC = red wire

At the furnace

Ask Your Own HVAC Question
Ask Your Own HVAC Question
Customer reply replied 4 months ago
I have changed the fuse and am up and (kind of) running again. Still no heat. What should I try next?

Hi..

Ok bypass R terminal and W terminal at the furnace control board.

MAKE SURE YOU DOT TOUCH B terminal with any of the 2 wires or you will blow fuse again

Furnace should start blower and engage elements.

If not, then it will be either a bad relay or control board

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Just to confirm - just connect R and W?

I will call you

Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 924
Experience: Owner at Gaztech
Verified
Gaztech and 87 other HVAC Specialists are ready to help you
Ask your own question now
Phone call session started

Justanswer uses a secure, third party phone system to connect your call but it is not working for some reason???

I want you to use a small wire or paper clip etc to jumper between R and W

Ask Your Own HVAC Question

Just hold jumper firmly on the W and R terminal screws to engage heating

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Sorry about that wait. Had to get the panel off. Ok, so connecting. R and W does nothing.

Best of luck!

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It looks like all the relays are on the board. The board is only $65 from Amazon, so I'm going to give that a shot first. Thanks again for your help!

Good job!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 924
924 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a honeywell TH9421C1004 thermostat in my home. The
I have a honeywell TH9421C1004 thermostat in my home. The settings function on the touchpad is not responding and I can't switch to the heat pump/air conditioner … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
My Honeywell THermostat continues to run the blower even if
My Honeywell THermostat continues to run the blower even if the System is off, and the fan setting is Auto - not Circulate? Is this correct?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a W8835 envirazone panel system with four zones, with
I have a W8835 envirazone panel system with four zones, with TrueSteam humidifier system. Then I have Visionpro IAQ thermostats. In both cooling and heating settings, my furnace fan will come on for n… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
My fan is stuck on the "ON" position on my touchscreen (P)X4146
My fan is stuck on the "ON" position on my touchscreen (P)X4146 programmable thermostat. How do I get the screen to respond to my touch again?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Trane touchscreen thermostat partially stopped working.
My Trane touchscreen thermostat partially stopped working. The heat will not go up, but will go down (it's currently set at 66 degrees). I can't switch it back to cool either. The bottom buttons still… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hello. I just installed a new Honeywell RTHL 2310/RTHL 221
Hello. I just installed a new Honeywell RTHL 2310/RTHL 221 Series thermostat to operate my Trane heat pump. When I turned the AC on, the motor, fan, and blower operate, but it blows ambient temp air, … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
My heating system is not working- I have a 2 zone Honeywell
My heating system is not working- I have a 2 zone Honeywell MZone (?) the thermostat seems to be working- the system is on (showing heat) and the fan is set on auto but very little air flow is coming … read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
the fan on my air conditioner does not turn off, it does not
the fan on my air conditioner does not turn off, it does not cool, seems the fan is "stuck ON" the only way I can turn it off is by turning off the main breaker. thermostat had "low battery" warning, … read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Trane XL90. When it should be cooling, the outdoor
I have a Trane XL90. When it should be cooling, the outdoor unit runs, but the circulating fan in the furnace part does not start. I've tried it in "Auto", "Circulate" and "On" fan modes on my thermos… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
we have a honeywell T8411R 1002 (2) thermostat and we tried
we have a honeywell T8411R 1002 (2) thermostat and we tried to turn on the heat but it would not turn on. when we first looked at the thermostat it was blank, we pulled it out from it's housing and pl… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Thermostat Set Point Temperature Is Never Being Reached.
Thermostat Set Point Temperature Is Never Being Reached. I will set the Set Point Temp to 72F, but the furnace will only kick in if the room temp get below 65F. When the furnace does kick in, it will … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
On my Honeywell thermostat what does the CIRC fan feature do?
I have a programmable Honeywell thermostat installed by BGE. When I turn the system to OFF the fan indicates Auto and does not operate. After a few hours the fan also goes to ON and begins to blow eve… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
have a Heil furnace model 7000 NULK075dG06 75000 btuh purchased
have a Heil furnace model 7000 NULK075dG06 75000 btuh purchased in 1993. A Trane rep said if we had an automatic lower capacity return air blower running continuosly our heat would be more even throug… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I am replacing a Honeywell 3611 programable thermostat for
I am replacing a Honeywell 3611 programable thermostat for a heat pump, because the display went blank and heat not coming on. I am replacing it with a Honeywell RTH7600 programmable thermostat. When … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a honeywell thermostate - part of the front says FAN
I have a honeywell thermostate - part of the front says FAN then it says auto and then on - how is the best way to set that? The rest I understand such as cool heat off emergency heat and the degrees.… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a Trane heat pump. Our heat was off for 10 hrs with
I have a Trane heat pump. Our heat was off for 10 hrs with very cold (Zero) conditions and I cannot get the house warm. When I click on Emergency Heat, it does not seem any different. How do you get t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
How to wire Honeywell TH1110D thermostat to gas fireplace?
I'm trying to wire a Honeywell TH1110D thermostat to my gas fireplace. The wiring diagram for my fireplace can be found on page 23 of this manual: http://www.empirecomfort.com/EMPIRECOMFORT/pdf2009/ma… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane 10000 outside and an indoor furnace connected
I have a Trane 10000 outside and an indoor furnace connected to it, I believe just for distribution of heat/cold through underhouse ducts. There are no controls on furnace, just a breaker. Thermostat … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x