My ignition control mod is flashing 6 x off 2 sec. Over

My ignition control mod...

My ignition control mod is flashing 6 x off 2 sec.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Over night

Contractor's Assistant: Do you plan on doing the work yourself?

I just replaced it at the end of nov.

Contractor's Assistant: Anything else we should know to help you best?

Yes i checked the system over night. All switches are good . I do not get power to pv Or mv/pv i do get 12.8 @mv

Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
3/21/2018
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,384
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

What's the brand and model of your control?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Honeywell , g26 series

That's not a Honeywell model number

Ask Your Own HVAC Question
Customer reply replied 3 months ago
What does the six flashes indicated

I need the Honeywell model number

Ask Your Own HVAC Question
Customer reply replied 3 months ago
S8670k
Customer reply replied 3 months ago
R u still there

Looking up specs. Have a little patience

Ask Your Own HVAC Question

a 6 flash is an internal control error. Power the system down, wait a minute then power it back up. If the same error comes up replace the control.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I did that several times 1am . Do you think there is a additional problem to cause the 4.5 month old module to go out

The module is self diagnostic. If it's repeatedly giving you the same internal failure error it needs to be replaced. It should have a 1 year warranty if you bought it new from an authorized dealer.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Thank you
Customer reply replied 3 months ago
What model # stat do you recommendfor a residential furnace

Thermostat?

Ask Your Own HVAC Question

Any Honeywell 24 volt thermostat is a good choice except the CT87.

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,384
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,384
24,384 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My pilot lights turns on but the main burner does not. FPSE
my pilot lights turns on but the main burner does not. FPSE 75 234 all worked find yesterday and for years. but not today EASTER Sunday. … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
I am replacing the gas control valve in my G26Q3-75-1
I am replacing the gas control valve in my G26Q3-75-1 furnace with a white rodgers 36H series valve. Can you tell me the correct wiring connections? It is not a direct swap. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox G16. The gas valve would open and shut
I have a Lennox G16. The gas valve would open and shut quickly. The system would shut down and restart. I replaced the ignition board, the flame sensor, and the gas valve. Now the inducer fan kicks on… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a rheem RRGG - 10e31jkr & the gas pack will not ignite
I have a rheem RRGG - 10e31jkr & the gas pack will not ignite the burners. Blower above unit comes on and I hear a spark but cycles start Sequence but no ignition.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
furnace wont light after pilot comes on, fan comes on and runs
furnace wont light after pilot comes on, fan comes on and runs about 45 secs then shuts down… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
we just got a used Series 2 Model ESC Spark Ignition Pool and
we just got a used Series 2 Model ESC Spark Ignition Pool and spa Heater Natural gas heater,175 BTU I installed the heater with 3/4 black iron pipe for gas supply line, I cleaned out the unit with air… read more
Rick
Rick
HVAC Supervisor
24,384 satisfied customers
Steve from Magitek Service in Hamilton Indiana......I have a Burnham L
Steve from Magitek Service in Hamilton Indiana......I have a Burnham LPB Model P-204PV-WPI.....the auto pilot sequence works and pilot flame stays lit ok but the main burner valve does not open when t… read more
Rick
Rick
HVAC Supervisor
24,384 satisfied customers
G20 with 2yr. old Honeywell ignit. control. Pilot on, no main
G20 with 2yr. old Honeywell ignit. control. Pilot on, no main burners on, fan on for cycle then retry. 2 blink code.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Working on 1989 model Heil "NRGF48FDBO 2" gas pac. I replaced
Working on 1989 model Heil "NRGF48FDBO 2" gas pac. I replaced the ignition module and in doing so pulled the wire loose from the TH-W spot on the module where it connects on the opposite end. Now I ca… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Why we we have 24V coming in and only 12v coming out going
Why we we have 24V coming in and only 12v coming out going to the gas valve? All wire continuity checks out --- all connections are correct… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Heil model NUGK075DG07 gas furnace Troubleshooting
Troubleshooting Heil model NUGK075DG07 gas furnace. Fan, exhaust blower, interlocks: flue temp, rollout, fan control, pressure switch all test ok. Igniter comes on, ignites puff of gas, then goes out.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Peerless boiler with a Honeywell S8610F ignition control
I have a Peerless boiler with a Honeywell S8610F ignition control module. The pilot lights but the burner does not fire. Could this be due to a faulty module?… read more
Rick
Rick
HVAC Supervisor
24,384 satisfied customers
I am replacing a Honeywell S8600M Ignition Control on a Rheem
I am replacing a Honeywell S8600M Ignition Control on a Rheem Power Vent hot water heater with a Robertshaw HS780 17NL-304A Ignition Control and the wiring terminals are different and I cannot find a … read more
THEFIXER1966
THEFIXER1966
High School or GED
12 satisfied customers
I have a Gas Furnace with an automatic pilot and a white-rodgers
I have a Gas Furnace with an automatic pilot and a white-rodgers 1F80-261 thermostat. The pilot comes on when heat is called for but burners do not come on. Once or twice burners did operate two weeks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
HVAC - I have a Lennox furnace that will not ignite the burners
HVAC - I have a Lennox furnace that will not ignite the burners even though the pilot light is lit and working fine. In December I had problems with the burners cycling on and off. I replaced the flam… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a G11E-200V-3 furnace. It has a Robertshaw Model SP735L
I have a G11E-200V-3 furnace. It has a Robertshaw Model SP735L Lennox Part No.(NNN) NNN-NNNNboard. There is a pigtail 6 hole female jack, with only four prongs used, but it does not plug in anywhere, … read more
BARRY
BARRY
owner
Associate Degree
56 satisfied customers
Have Janitrol Mod. WHE 30 heater in garage (think it was installed
Have Janitrol Mod. WHE 30 heater in garage (think it was installed in 1989). Getting spark but not igniting. Probably the regulator? is it still available? Jim… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Pilot will light but not the burner.I replaced the igniter/
Pilot will light but not the burner.I replaced the igniter/ sensor pilot unit.How can I determine if its the valve or control unit… read more
HVAC22
HVAC22
Residential Service Team Supervisor
High School or GED
32 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x