Trane XR80. Thermostat is from Honeywell. Everything was…

Customer Question
Trane XR80 . Thermostat...

Trane XR80 . Thermostat is from Honeywell. Everything was working till yesterday but suddenly now, thermostat restarts when trying to make heat a call.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes checked themorstat , no issues there. Also I purchased a thermostat 2 months back in a deal but never installed. I installed and tried that too. But same issues. THis new thermostat also restarts while making a heat call. Filters are cleaned. I took it out , cleaned thoroughly and reinstalled.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Note - I always keep spare and new parts of almost all HVAC system. I replaced high limit switch, circuit board and transformer with new ones. Issue still persist.

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 21 minutes by:
3/21/2018
HVAC Technician: airheatman, HVAC Technician replied 5 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,368
Experience: Furnace, A/C and heat pump specialist.
Verified

W hat do you mean it restarts? Is heater shirt cycling on and off? If so lets clean flame sensor.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Thermostat sends heat signal and then switches off. It starts again within 2 to 5 seconds, goes though initialization process ( like connect to wifi network etc ) and then after a min or so, try to initiate heat sequence again, it loses power and turns off again and this repeats.....! It repeated multiple times and finally blow off my circuit board fuse. I replaced the fuse but kept unit off till I figure out what is wrong here.I don't think so it is related to flame sensor since heat call itself is not starting. Though I will clean and reinstall that tomorrow morning first thing.Note - I also replaced old transformer ( 35 VA ) with a new one ( 35 VA ) . But no luck. May be I need to change to 40 VA or 50 VA ? Not sure.
There is no indication on circuit board red led. It blinks and shows normal operation. Let me know if there is anything I can check before calling a professional.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Just bought a new honeywell smart wifi thermostat rh9585 - i
just bought a new honeywell smart wifi thermostat rh9585 - i have the wiring as follows from the furnace. Y to y - G to g - R to r - W to w. I have removed the jumper because I have a C and RC wire co… read more
airheatman
airheatman
HVAC Technician
9,368 satisfied customers
I have an old Honeywell Round looking Mercury Thermostat and
I have an old Honeywell Round looking Mercury Thermostat and wanted to upgrade to the Honeywell Speaks ZWave thermostat, but my old only has 2 wires coming out from the wall, NO common wire, will this… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Installed Honeywell lyric t6 pro on train system hooked up
Installed Honeywell lyric t6 pro on train system hooked up blue common wire however the thermostat works fine till it calls for heat then it blacks out and blows the fuse wired correctly the old therm… read more
Bill
Bill
Service Mgr
114 satisfied customers
I have an RT9580 thermostat. An HVAC technician installed it
Hi, I have an RT9580 thermostat. An HVAC technician installed it and checked it, but this problem recurs and suggested I contact you. It restarts often when calling for heat, meaning it is losing powe… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a lashing red light and air conditioner is not
I have a lashing red light and air conditioner is not putting out cool air, what is … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
In the process of replacing an old analog, and want to install
In the process of replacing an old analog, and want to install new digital. I have a white and red on the front. On the connection to the back white is to white, and green is to red. The green is cont… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am trying to install a new smart thermostat but can't get
i am trying to install a new smart thermostat but can't get it working. My old thermostat didn't use a "C" wire, the new one does. There is an unused blue wire tucked behind the current install which … read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
We have a Trane XR80 heating & cooloing system installed by
We have a Trane XR80 heating & cooloing system installed by Hague Heating & AC in NJ. This system was installed brand new in Nov. 2013. It worked well through May 2015. Suddenly in late June, the AC w… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Have a Trane XB 80 installed 2002. Replaced circuit board
Hi, have a Trane XB 80 installed 2002. Replaced circuit board a couple of years ago after burn out with White-Rodgers 50A55-486 and added a Nest thermostat. Been working well but two days ago blower s… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am trying to install a new honeywell thermostat to my
I am trying to install a new honeywell thermostat to my system 2000. Although I have an extra cable for the "c" connection. It is not terminated on my 2000 and not sure where to connect that cable to … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
HI. just had a brand new HVAC unit (AC / heater / condenser)
HI. just had a brand new HVAC unit (AC / heater / condenser) installed. AC/Heater appears to be working fine, but condenser won't stay on. It tries to start, but won't stay active.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Can a certified TRANE tech help me? 5V fuse keeps blowing
Can a certified TRANE tech help me? 5V fuse keeps blowing on Trane XR80 Setup: -Trane XR80 model DD1C120A9541A Furnace -Trane 2TXCC049AC3HCAA sitting on top of the XR80 (49,000 btu?) -Carrier 38TKB048… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a trane XR80 ac/heating unit. The ac failed to turn
I have a trane XR80 ac/heating unit. The ac failed to turn on so I looked at the unit and there is a steadly blinking red light. After a few minutes the ac turned on but the light is still flashing. W… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
trane xr80 single stage cooling/heating. Cooling works heat
trane xr80 single stage cooling/heating. Cooling works heat doesn't. No error codes. Standard 'no call for heat'. Replaced thermostat (bypassed the wiring by taking the tstat to the furnace room and r… read more
airheatman
airheatman
HVAC Technician
9,368 satisfied customers
I have a Trane XR80. When I turn the thermostat up the ignitor
I have a Trane XR80. When I turn the thermostat up the ignitor heats for 1-2 seconds and then stops. Then the blower motor starts and the diagnostic light blinks 9 times (check ignitor). I have replac… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Ive got a Trane XR80 flashing the LED 4 times, indicating
I've got a Trane XR80 flashing the LED 4 times, indicating an open limit switch. I've cleaned the filter, shut down the unit (including breaker) and restarted it, and reseated the wires to what I thin… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane Clean Effects Air Filtration system installed
I have a Trane Clean Effects Air Filtration system installed on my Trane heating and cooling system installed just two years ago. For the past year, my Clean Effects unit has consistently displayed er… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
We have two XR80 Trane units in our home. The downstairs unit
We have two XR80 Trane units in our home. The downstairs unit has just started cycling on and off. It will just shut down after a few minutes, and not having reached the set temp. Starts again by itse… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x