The spark ignitor is fairly new when inducer motor comes on…

Customer Question
The spark ignitor is...

The spark ignitor is fairly new when inducer motor comes on i can hear clicks in the board click but ignitot dosnt come is that a failed board?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Yesterday for me but another tech put in a spark about 6 months ago .. i tried to jump out the pressure switch did not see one so tried where the wires went into the board

Contractor's Assistant: Do you plan on doing the work yourself?

Yes im a hvac serv tech but have never worked on a coleman

Contractor's Assistant: Are you an HVAC professional?

Yes graduated in 2000

Contractor's Assistant: Anything else we should know to help you best?

Well i think it is the board but like i said tring to diagnose inducer

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
3/20/2018
HVAC Technician: airheatman, HVAC Technician replied 5 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
Experience: Furnace, A/C and heat pump specialist.
Verified

1.What is model on furnace
2.Do you get an error code on board when it fails?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
dgat075bdd .. just green light blinking..did not see error code listings any where
Customer reply replied 5 months ago
im sorry what do i do right now
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

My manual is showing the igniter to be a hot surface igniter not a spark. Can you verify which you actually have?My name is ***** ***** I am happy to be able to work with you on this today.Please be patient as I respond as sometimes it takes me a few moments to gather proper manuals and specifications on your equipment in order to provide accurate answers.Please wait until we are finished to rate my answer.Just to let you know, the website will be offering a live phone call for an additional fee. Due to my current work load and responsibilities I may not be available for the live phone call .Please note that there is an additional cost for the service and if a technician calls it may be a different technician. However we can continue here as long as needed .

Ask Your Own HVAC Question
Customer reply replied 5 months ago
i could be did not take it three wires going in one green two white
Customer reply replied 5 months ago
did not see a pressure switch just two wires going into board from inducer
Customer reply replied 5 months ago
my talent is with carrier 90 percent
Customer reply replied 5 months ago
but if not igniting on carrier i can check power going to inducer from board to see if it is the board
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Your ignitoer is going to be inside the firebox on this furnace.Look through peep hole and seei if you have a glow bar or spark.See pictures in links above

Ask Your Own HVAC Question
Customer reply replied 5 months ago
i did not see anything glowing or lighting up
Customer reply replied 5 months ago
the inducer would run then a couple of clicks board then nothing ..no glow
Customer reply replied 5 months ago
i think it is the board but could it be inducer motor?
Customer reply replied 5 months ago
i do but not at property right now
Customer reply replied 5 months ago
no home computer
Customer reply replied 5 months ago
im sorry that is supposed to be "on"
Customer reply replied 5 months ago
can i get ahold of you guys when i get there
Customer reply replied 5 months ago
at home right now
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Yes just come back to site when at the unit.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
are you doing ohms on hsi
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

You can do ohms or you can unplug and check the 120v at plug from board to igniter

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I'm checking off the board where the plugs in to hsi it is bouncing around 14.5 to 19
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Got meter on ac volts?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
vac
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

OK and this is after the exhaust motor comes on and the centrifugal switch should close yes?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Got them plugged in to both plugs that go into hsi
Customer reply replied 5 months ago
Inducer comes on then board clicks
Customer reply replied 5 months ago
Looked at hsi didn't see any flaws
Customer reply replied 5 months ago
How does this inducer motor signal work with no pressure switch?
Customer reply replied 5 months ago
What is the best way too that I only know carrier pressure switch
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Follow those blue wires to locate it.It is basically the same thing as the pressure switch you are familiar with.Vent motor pulls a vacuum closing contacts.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Yeah I did that yesterday they go in to to plastic cover 250 fuses
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Make sure we are getting continuity through that switch on the 2 blues

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Ok.. no continuity
Customer reply replied 5 months ago
Replace inducer?
Customer reply replied 5 months ago
Right
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Next lets try with thermostat calling for heat and vent motor running?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
That's what I'm doing
Customer reply replied 5 months ago
Sorry you while checking con..yes it worked
Customer reply replied 5 months ago
We have con while running
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Does igniter ever get 120 and glow ?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Tell me about the blinking light. How many blinks between pausing

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Three
Customer reply replied 5 months ago
I can't find codes anywhere
Customer reply replied 5 months ago
Never glows
Customer reply replied 5 months ago
never read 120 from board
Customer reply replied 5 months ago
Do you have codes... what does three mean
Customer reply replied 5 months ago
Are you still with me
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

LOoking. Manual says red light not green.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Found it. Te 3 flashes means the pressure switch failed to close.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

Says this could be caused by: faulty inducer / blocked vent pipe / broken pressure switch / faulty pressure switch".

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Thanks..we did get continuity across the blue wires when inducer.. would you recommend replacing inducer?
HVAC Technician: airheatman, HVAC Technician replied 5 months ago

I would probably replace the combustion motor and that switch.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,367
9,367 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Ruud HVAC unit model: URKA-A04JK06X dual fuel. It's
Hi, I have a Ruud HVAC unit model: URKA-A04JK06X dual fuel. It's just blowing cold air though, working fine a couple fo days ago. Older unit installed by a previous owner. Wondering if there's any bas… read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
Goodman furnace tries to start cycle but clicks off after a
Goodman furnace tries to start cycle but clicks off after a few seconds. … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I need to install a b2959000 draft inducer. I need to know
I need to install a b2959000 draft inducer. I need to know where the wires hook up … read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
The ignitor on my furnace does not ignite. Need help to fix it!
I just replaced my ignitor and my lennox G27 furnace still won't ignite. I checked the furnace filters, and cleaned the flame sensor. The ignitor doesn't even turn pink or warm up at all when I switch… read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
I have a Reznor Udap 75. Bought new & installed in '08. Has
Hi, I have a Reznor Udap 75. Bought new & installed in '08. Has always had a problem with igniter not wanting to light gas. It cycles and tries 3 or 4 times b4 giving up. But then other times it works… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi, i have a carrier weathermaker series 100. About a month
Hi, i have a carrier weathermaker series 100. About a month ago i noticed after the thermostat was satisfied and shut off but the inducer motor runs constantly. i have to shut the main power off to th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I HAVE A TRANE FURNACE. model TUD080R9V3K4 , 5/2004 THE DRAFT
I HAVE A TRANE FURNACE. model TUD080R9V3K4 , 5/2004 THE DRAFT INDUCER COMES ON, BUT NO IGNITION, the board flashes 4 which says open limit, I jumped out all 3 limits (two roll outs, and the high limit… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Payne heater model 376cav048075 that the blower turns
I have a Payne heater model 376cav048075 that the blower turns on, u smell gas, u hear it trying to light but nothing thereafter.… read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
I have a Carrier furnace mod 58SXC. The ignitor is not coming
I have a Carrier furnace mod 58SXC. The ignitor is not coming on during normal operation. Doing a test sequence all operations test o.k., no trouble code. I have cleared both vents including pressure … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi.. Ive got a Ruud Silhouette gas furnace model # XXXXX
Hi.. I've got a Ruud Silhouette gas furnace model # XXXXX with problems. Had friend determine thermostat was bad, replaced it and all worked fine for couple days. Now fan comes on, gas flows, but will… read more
airheatman
airheatman
HVAC Technician
6 years college
9,367 satisfied customers
Weatherking WGDG-07EAMGR from around 1996. Power went out yesterday
Weatherking WGDG-07EAMGR from around 1996. Power went out yesterday and when it came back on fan runs continously without firing the burner. Removed all leads on control board from t-stat and still ru… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have the following issue; the system board of my Coleman
I have the following issue; the system board of my Coleman furnace is shown a fault code that the pressure switch is stuck closed. I have checked the switch to see if the switch is opreable, which it … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Rheem Model RRKA8036JK08E (so the paperwork says).
I have a Rheem Model RRKA8036JK08E (so the paperwork says). It cools fine, but will not heat. I had a service tech (read that replacement artist) look at the furnace. First he said it was the gas valv… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello! My name is Eric, and I am an LP tech, NOT an HVAC tech!
Hello! My name is XXXXX XXXXX I am an LP tech, NOT an HVAC tech! Recently, I visited a new Bryant Evolution to inspect and record flow pressures. I tried to jump a t-stat circuit at a remote pannel th… read more
freon
freon
Owner
High School or GED
214 satisfied customers
NEW PROBLEM Mark Hendley, I talked to you before a week
NEW PROBLEM Mark Hendley, I talked to you before a week before Christmas. Weathermaker SX Carrier Product 58SXA080-101GG Model 58SXA080- GG Series 100 Serial 4589A06048 I had an issue where everything… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
I have a lennox 80MGF with a upgraded ECG-1 board that was
I have a lennox 80MGF with a upgraded ECG-1 board that was replaced 9 years ago. Never had any problems with unit. Ok now the sequence. Blower works fine, house had gas and gas line is ok as hot water… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I have a Coleman Evcon DGAT090BDE gas furnance in which the
I have a Coleman Evcon DGAT090BDE gas furnance in which the pilot light will not come on. There are also 4 flashing lights. What do you suggest?… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
Bryant Downflow furnace model # XXXXX Short in gas
Bryant Downflow furnace model # XXXXX Short in gas valve..replaced..gas valve..now furnace heat blower won;t start..replaced circuit board..still no fan.. found a short in 3 wire pilot assemb;y..repla… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x