I have a Ruud Furnance/Heat Pump system. Heat Pump is

Customer Question
UPLA-031JAZ. Air Handler is UBHA-17J11NFAA...
I have a Ruud Furnance/Heat Pump system. Heat Pump is UPLA-031JAZ. Air Handler is UBHA-17J11NFAA. Original thermostat is Rheem part number 41-20804-15. The thermostat will consistently read 5-10 degrees warmer than the air in the house really is. I even installed an Ecobee and a Honeywell Lyric T5 with the same results. The air temp is 5-10 degrees cooler than the stat will read. When I put my hand on the stat it's warm. When I take the stat off the wall the wires and wiring cradle are warm. What causes this heat and how can I eliminate it?
Submitted: 4 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
3/20/2018
HVAC Technician: airheatman, HVAC Technician replied 4 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

If the stat is reading higher than room temp there has to be something generating the heat.It can be coming from attic air down wall .Remove thermostat and stci a thermometer in the whole in wall and see if the air is hotter than room temp.If so, use foam insulation to seal whole in wall where wires come through.

Make sure there is no light or heat source near thermostat also.I had one once that installer mounted too close to a wall scone and was giving it a false reading.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I took my Fluke with a temperature probe wire and stuck it through the drywall into the cavity. It reads 1 degree F cooler than the hallway. There are no lights, switches, appliances or anything like that on or near or around it. Behind this wall is a staircase to the upstairs.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

When you say,the thermostat is reading warmer than room temp in the house, are you taking the room temp right beside the thermostat with the Fluke?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I have a thermometer in the main part of the main floor. It reads 64 degrees. I move it to the hall and it reads 64 degrees. I take the fluke and the thermometer attachment and it reads 64 degrees in the main part of the house and the hallway. I stick the attachment (which is a high temperature thermometer wire probe) through the hole where the wires come out of the wall and it reads 63 degrees. But, the thermostat (Rheem, Ecobee and Honeywell Lyric T5) all read between 72 and 75 depending on the device. I take the device off the wall and let things cool off. When I put them back on the wall and hook things up again, the temperature on the device reads correctly. After being connected for a few minutes, the temperature spikes.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sounds very strange.Three different thermostats all read high but the fluke reads correctly in hallway. ONly thing I could imagine is something to do with the load through the thermostat control wires. Touch the Fluke probe against the wires and see if it also climbs

Ask Your Own HVAC Question
Customer reply replied 4 months ago
The wires read about three degrees above room temperature right after I take the stat off the wall. They read ambient temp when things have cooled off. There's no difference in temp across the different wires.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

If you have an amp meter clamp around wires while thermostat is connected but everything off and see if there is any load on the wires.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I'll have to get a clamp accessory for that test. I'll get one later tonight.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Not thinking of any reason for those wires to be warm unless there is a load on them

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Okay. I'll let you know what I find out. So many things miswired on this system. Thanks for your patience as we get it sorted out. I replaced the main breaker cuz it quit holding itself closed. And the slot next to it was melted from another breaker failure. It looks like this system has had issues for a while.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Just a thought.Is the thermostat wire 18 gauge (not thin phone wire)?

Ask Your Own HVAC Question
Customer reply replied 4 months ago
It's proper 18 gauge thermostat wire. That's one of the first things I checked when we were trying to determine which wire went to the heat pump vs the stat.
HVAC Technician: airheatman, HVAC Technician replied 4 months ago

Sure would like to know what we determine in the end.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Okay. I've taken an AC voltage detector and checked each wire at the stat for voltage higher than 24. None of them are carrying anything higher than 24 volts.
Customer reply replied 4 months ago
I think I found the problem. The heat strips will occasionally run without the blower turning on. The heat will then come up the return air duct and exit right under the thermostat.
HVAC Technician: airheatman, HVAC Technician replied 3 months ago

Let,sget that issue corrected(replace sequencer or whatever is causing strips without blower) and see if issue goes away.That one definitely sounds far fetched.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
9,213 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Can not get a new Honeywell lyric t5 thermostat to work
can not get a new Honeywell lyric t5 thermostat to work properly … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Three bits of data requested on heat pump. Ruud upla-031jaz.
Three bits of data requested on heat pump. Ruud upla-031jaz.What is the lowest temperature it is designed to operate in? 35, 40 or 45 degrees?Can it run concurrently with emergency heat?Is the reversi… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
Are you able to help me troubleshoot why the low voltage
Are you able to help me troubleshoot why the low voltage fuse instantly blows when the ayat calls for heat? Ruud ubha-17j11nfaa mated with a heat pump … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I need help with the wiring for a Honeywell lyric T5 and a
I need help with the wiring for a Honeywell lyric T5 and a Rheem Heat Pump. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
HVAC problem. Wired two new Lyric T5 thermostats. I wired in
Wired two new Lyric T5 thermostats. I wired in the O configuration. When the unit is in cool, it blows hot. When the unit is on heat, it blows cool. When I switch the mode to B, it blows hot in heat but will not shut off once the setpoint is hit.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Converting a honeywell ct70a (with 7 wires) to a t5
Converting a honeywell ct70a (with 7 wires) to a t5 thermostat. I believe I've wired correctly but system won't turn on.… read more
Iohn Keffer
Iohn Keffer
HVAC Tech
Associate Degree
73 satisfied customers
I am trying to replace an old mercury thermostat with
I am trying to replace an old mercury thermostat with Honeywell RTH6350D. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
, I have a RUUD UBHC-14J11NFD which I'm hooking up to a
I have a RUUD UBHC-14J11NFD which I'm hooking up to a Nest thermostat, replacing an old Honeywell t-stat. Have a question on the wiring. … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I had an older thermostat and a heat pump system. I wired it
I had an older thermostat and a heat pump system. I wired it the way I thought it should go but it wont actually blow heat when i turn it on. There was no O wire, only a blue wire. And the new thermos… read more
jhvac
jhvac
2 satisfied customers
Trying to install a Honeywell programable thermostat. Heat
Trying to install a Honeywell programable thermostat. Heat kicked on shortly and then kicked off (it wasn't blowing warm air). My wiring to old thermostat doesn't match any of the directions in the in… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, I have a 6-year-old Carrier system (2 stage heat/2 stage
Hi, I have a 6-year-old Carrier system (2 stage heat/2 stage cool) with an Infinity Control thermostat (older model, not the newer touch display). I would like to replace the thermostat with a Lyric o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell T8775c digital t-stat. I wanted to upgrade
I have a Honeywell T8775c digital t-stat. I wanted to upgrade to a focus pro th6110D1005 programmable t-stat. When I installed the th6110d & even though it was set at the same temp as my Digital Round… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,027 satisfied customers
I have a ruud model UBHA-J06NFDAI AIR HANDLER NO THERMOSTAT
I have a ruud model UBHA-J06NFDAI AIR HANDLER NO THERMOSTAT WAS ATTACHED ned to attach a thermostat no wiring diagram need help… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
Hi, I have a 3 ton heat pump system for my mobile home.The
Hi, I have a 3 ton heat pump system for my mobile home.The air works fine but the heat onle blows cold air unless you put the therm. on emergancy heat Someone told me about a revers flow valve.Can you… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Lennox 4 ton heat pump ( XP19-048 compressor CBX32MV-048
I have a Lennox 4 ton heat pump ( XP19-048 compressor CBX32MV-048 variable speed air handler) with a Honeywell VisionPRO TH8000 series programmable thermostat. Is it efficient to program the thermosta… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
My Carrier Air V Heat Pump while on heat, starts blowing heat
My Carrier Air V Heat Pump while on heat, starts blowing heat but after 4or 5 hours in 50 degree F slowly starts blowing cooler and cooler air, does not turn off and turn on furnance?… read more
Andrew
Andrew
Master\u0027s Degree
37 satisfied customers
Hi, my AC contractor installed a heat pump in my cottage about
Hi, my AC contractor installed a heat pump in my cottage about a year ago and I don't think it is functioning properly. When it is either very warm (90s) or very cold (30s) when the temperature gets t… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
What is typical cross over outdoor temperature (Heat Pump to
What is typical cross over outdoor temperature (Heat Pump to back up heat) for Trane model TWRO36C100A2 (new 1996). My unit is switching to Back up heat in mid 30's while performance curves heating su… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x