I have new carrier compressor with three high wall units. 1…

I have new carrier...

I have new carrier compressor with three high wall units. 1 unit has worked fine for over 9 months the other 2 will begin to run but will shut down within 30 to 45 sec after they start then they display 2 small green lights in the middle of the cover.....what is wrong with the 2 units

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Brand filters and the thermostats are set on auto

Contractor's Assistant: Do you plan on doing the work yourself?

Depends on how extensive and what I might encounter they were installed by a local installer

Contractor's Assistant: Anything else we should know to help you best?

Not at this point

Show More
Show Less
Ask Your Own HVAC Question
Answered in 46 minutes by:
3/20/2018
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it sounds like the system has a refrigerant leak and is shutting off those two circuits when the low pressure switch trips, You will need a set of refrigeration service gauges to verify that... its quite a bit of a specialized skill, If you have those skills I will coach you on doing the test, If not, tell me which direction you are from the center of the nearest town or city and I will locate a well rated service outfit that can arrive and do the diagnosis and repairs,

If you can give me the full model number of the unit that sits outside I can pull the manual on it for you as well,

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I was planning on contacting the installer and have them check the units over. I had a feeling that was what the problem might have been since everything check out thanks for your time and answer.

You may or may not have competent installers, especially if there turns out to be a leak, in that case installers with integrity will fix the leak for you at no cost,

.

.....less than competent installers will fix the leak then tell you "your wiz-bang failed, that will be $490 please"...some will not even fix the leak, but will add refrigerant, then tell you "your doo-hicky has failed....that will be $572.51 please"

.

.

Its time to rate my input for the day, that gets me paid, locate the "finish and rate your expert" link near the top of the page and click on it. I will appreciate that very much.

I am in every day from 9 am to 11 pm west coast USA time to do any follow up needed.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 4 months ago
Thank you for your help
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
9,701 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,701 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 5 yr old goodman heat pump. the fan was replaced I
I have a 5 yr old goodman heat pump. the fan was replaced I month ago under warranty, two weeks later the installer added a starter because the lights in the house blinked each time the unit came on, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox 14ACX HVAC system brand new. Used twice since Aug.,
Lennox 14ACX HVAC system brand new. Used twice since Aug., 2015 install (*unit is @ our vacation home). We are located in Central Texas. Tonite, indoor temp is 77° in house. System has been off since … read more
HvacmanSean
HvacmanSean
Owner
HVAC
233 satisfied customers
Hi Phil, Since the compressor out, what are my options
Hi Phil, Since the compressor burnt out, what are my options to get back AC for the rental unit? Replace a compressor only? Everyone seems to say that this is not a good option. What do you think? How… read more
Phil
Phil
Mechanical Engineer
9,701 satisfied customers
Heat pump at my Moms house in Western NC. Condensor keeps
Heat pump at my Mom's house in Western NC. Condensor keeps icing over when it's cold. Local place charges a lot to chip and ice, tells her to leave emergency heat on. Is there a better solution? What … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Culprit: Trane TWA 120A, (10 ton) Unit We had seven brand
Culprit: Trane TWA 120A, (10 ton) Unit We had seven brand new units installed at the same time on our new building 2 years ago. The original subcontractor replaced the compressor in unit #2 3 times ju… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Why is the timer light blinking on my Panasonic AC?
Why is the timer light blinking on my air conditioner and it is not working? Optional Information: Brand: Panasonic Model Number: CS-E24GKR What have you tried so far?: resetting the air conditioner a… read more
V12Tech
V12Tech
252 satisfied customers
just bought a house with a knight boiler makes rumbling noise
just bought a house with a knight boiler makes rumbling noise from time to time and then sometimes blowes steam-water out pressure reliefe the systeam is four years old the company that installed it w… read more
Phil
Phil
Mechanical Engineer
9,701 satisfied customers
What is your opinion on Goodman AC systems. What is the justification
What is your opinion on Goodman AC systems. What is the justification for going with a Carrier system that is almost 2 X the price of Goodman?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have heat pump & installed hard start cap to get compressor
Have heat pump & installed hard start cap to get compressor going. It ran, shut down again in 10-15 sec, then restarts. BUT, high and low side pressure begin to drop until it begins to pull a vacuum o… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
pump down 3.5 ton condensing unit. closed liquid line valve
pump down 3.5 ton condensing unit. closed liquid line valve pushed in contactor compressor high presure internal relief valve opens within 30 sec. R410A what am I doing wrong?… read more
N4IEA
N4IEA
Customer Service
Associate Degree
227 satisfied customers
We have a Unionaire HVAC system for guest bedroom. Seven years
We have a Unionaire HVAC system for guest bedroom. Seven years old Always rather "blinky". And especially so when guests are using the room. Current problems: (1) Rattling when unit runs (in any mode)… read more
Phil
Phil
Mechanical Engineer
9,701 satisfied customers
I was directed here for Admiral room air conditioner. Can you
I was directed here for Admiral room air conditioner. Can you answer questions re. a 5000 BTU window unit.Thanks,Joseph The unit cycles the compressor for several seconds but never moves into the next… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
145 satisfied customers
I have a trane A/C unit, which also has heating. The manual
I have a trane A/C unit, which also has heating. The manual says its for 2ttr2, 2ttr1 and 2ttro. Not sure which one is mine. I have installed a Hunter 44360 thermostat. In heat mode, no matter what I … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Heat pump was off 2or3 weeks and was in cooling mood and working
Heat pump was off 2or3 weeks and was in cooling mood and working fine. Started it up in heat mode after that peroid of down time. The compresser kicks on and shuts off after 30 seconds or so. Then it … read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
I have a Bryant 598AN048-B Two Speed Unit. I understand that
I have a Bryant 598AN048-B Two Speed Unit. I understand that it is an older model. It worked perfectly until this week. Fan & compressor work. Outdoor temp sensor malfunctioned, and the unit cuts off … read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Need an approximate 36,000 BTU Central Air for the upstairs
Need an approximate 36,000 BTU Central Air for the upstairs zone of my house. What product would you recommend and approximately what should it cost. Already ducted, replacing a 20 year old unit.… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
I have model nuber FD260ALAH000B Whole House Air cleaner. Everything
I have model nuber FD260ALAH000B Whole House Air cleaner. Everything has been working fine. Today the top three red LED lights have come on and the red pre filter has also come on. Some cycles the sin… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I purchased a Carrier 48XP 13 SEER gaspack (2-5 ton) unit on
I purchased a Carrier 48XP 13 SEER gaspack (2-5 ton) unit on Feb 6, 2009. The company that installed it did so without reading the instructions regarding the necessary clearances for safe/optimal usag… read more
Josh
Josh
Service Technician
High School or GED
30 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x