If I have a 1800 square foot home 8' ceilings. If I have a 4…

Customer Question
If I have a...

If I have a 1800 square foot home 8' ceilings. If I have a 4 ton heat pack unit on the roof what should I have coming out of the registers CFM's with regards ***** ***** and AC

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

The filters are new and the thermo is new Honeywell digital.

Contractor's Assistant: Do you plan on doing the work yourself?

Its already when the heat kicks on it seems to throw out room temperature air for about 10 minutes.

Contractor's Assistant: Anything else we should know to help you best?

We have two registers supply lines we added another one when we placed the new unit on the roof, 16x20 and 20x30"

Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 30 minutes by:
3/19/2018
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,317
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, air flow requirements vary moderately with the design of the equipment, and vary further with the climate... beyond that air flow varies in some multiple speed blower systems with how loaded with dirt (restricted) the air filter is.

.

To put some perspective on it, in cooling mode air flow requirements range between 350 and 500 cfm per 12,000 btu. hr of cooling capacity.... and 30 to 40% less air flow in the same unit for gas fired furnaces...the air flow being a little higher for high efficiency condensing furnaces.

The specifications for the equipment will call out the required minimum air flows for that equipment.... it was never perfect. Until lately with the variable speed blowers and two stage or variable gas flow gas valves... driven by a micro computer (IC chip) in the furnaces printed circuit board... that senses air temperature and humidity differentials as they change and adjusts the air flow accordingly... so that no fixed measurement means very much.

If your system produces room temperature air for 10 minutes when first going into heat mode, then the time delay circuit in the furnaces printed circuit board is bad, Or the thermostat is wired to run the blower at high speed as soon as heating is called for, I suspect the latter.

.

Take close up, exceedingly well focused photo's of the wiring diagram glued inside the furnace/air handler door, and the printed circuit board mounted on the blower, , that shows where the thermostat wires connect, and a photo of the thermostat sub base after you pry the thermostat from it, and the brand and model number of the thermostat, and I will mark them up with trouble shooting instructions.

Use the 'add files' link next to your send button to get the photo(s) to me.

.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed .

.

When we finally get the situation solved, please select the 'finish and rate your expert link' near the top of your page and click on it.

.
My goal is to give you the best experience possible!
I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Honeywell Pro TH3110D
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Thanks, click here for the manual on the thermostat you have

Ialso need to see how the thermostat is actually wired as mentioned earlier, that thermostat you have can be wired in many differnt ways, in some ways it will run the blower whenever the heat is called for and that will produce the cold drafts you are mentioning.

I still need the photo of the furnace wiring diagram or at least the furnace brand and model number from a sticker inside the same furnace compartment as the gas valve, that will tell me if you have a variable speed furnace or not, and from that I can pull the manual on that furnace that will have the air flow specifications.

That however is not relevant to your furnace blowing cold air for 10 minutes prior to the heat coming on, for that I need the wiring diagram asked for and you will need a multi meter and some considerable skill to perform the diagnostic steps I define.

-------------

If you do not have any of these skill, tell me which direction you are from the center of the nearest town or city and I will get you a short list of well rated service outfits that will arrive and correct the wiring errors,

Ask Your Own HVAC Question
Customer reply replied 1 month ago
On the 4 ton gas pack unit which is what we have, and based on the 1800 Sq. foot home 3 bedroom etc. can you give me what should be a typical CFM reading coming from the registers on heat and AC?
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Hello again, yes, generally 1200 cfm under a call for 100% heat output, and less if you have a variable speed blower and the thermostat is set at 70F with room only at 68F, then in that case the air flow will drop to around 900 CFM.... thats IF you have a variable capacity heating system.

Standard design velocity for registers is in 500 feet per minute under low heat output conditions and 750 fpm under a call for high heat.

.

A bit about myself, I am 77 years old, semi retired, earlier in my career I owned my own HVAC company and built it to 27 staff, we did projects in the $50,000 to $200,000 range at the high end. then in 1989 I sold the company and began consulting nationally, for fortune 500 companies, on projects generally between 5 and 100 million dollars, I became known for my ability to turn failed projects around and to that end was called to assist the US dept of Energy with problems they were having in our nations nuclear weapons labs... in 1994 I testified before the US congress on related issues for 2 hours. I still consult privately and answer questions for Just Answer

click here to get an idea of a typical project, this was 400 tons of minus 60F blast freezer equipment aboard the Hawaiian princess, I did all of the engineering, drawings, piping and electrical controls.

.

My remarks regarding variable air flows that will be seen with your equipment, lacking model numbers, are about as accurate as possible... air flow however is not the problem in your case, its the time delay controls that are supposed to keep the blower OFF until the burners warm the furnace up.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Its time to rate my input for the day, that gets me paid, locate the "finish and rate your expert" link near the top of the page and click on it. I will appreciate that very much.

I am in every day from 9 am to 11 pm west coast USA time to do any follow up needed including coaching on a full diagnosis of the cause, you will need a multi meter and some skill with it, plan on 2 to 4 hours, there is no additional charge.

Ask Your Own HVAC Question
HVAC Technician: Phil, Mechanical Engineer replied 1 month ago

Some background information, all furnaces of any type feature adjustable air flows in a range of plus or minus 30% from a mean, thats a lot, this is selectable by the installing contractor via dip siwtches in variable air volume systems and by choosing with speed among 3 or 4 that the blower motor is wired for.... then even with those selected and set, air flow will vary with how the air ducts have been sized... smaller ducts (very often too small) will restrict air flow.

In order to be complete, cooling air flows are 50 to 70% greater than heating air flows where gas fired furnaces are concerned, and only slightly less for heat pump applications.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,317
9,317 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,317 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a large hot water heat system with 8 zones using
I have a large hot water heat system with 8 zones using wired thermostats all connected to 2 Caleffi ZVR104 relay panels. Each wired thermostat is connected via 2 wires (R and W) on the ZVR's thermost… read more
hvacdave84
hvacdave84
53 satisfied customers
Furnace blowing cold air,Filter is good,burner is on.
Furnace blowing cold air,Filter is good,burner is on … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,700 satisfied customers
I can't get the boiler to ignite. The heating system has
Hi I can't get the boiler to ignite. The heating system has been operating continuously for probably 6 months now. This is unusual for me. I normally only use the system for hot water for washing etc.… read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I have a Goodman heating system and it is not heating
I have a Goodman heating system and it is not heating properly. The burner starts for about 3 seconds and then it goes off. The blower keeps blowing air, but not warm enough. Any ideas what it could b… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am having a problem with my heating system, the unit will
I am having a problem with my heating system, the unit will start up and the heat will ignite and there is flame but after a few minutes the limit switch opens and shut down, is the vent blower causin… read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
The heating system seems to be on a hold for one day that I
Second opinion] The heating system seems to be on a hold for one day that I cannot chnge Help!… read more
Bill
Bill
Service Mgr
83 satisfied customers
My boiler (forced hot water heating system) has been running
My boiler (forced hot water heating system) has been running when no zones have been calling for heat. Why?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I own a Payne heat pump air conditioning/heating system
Hello. I own a Payne heat pump air conditioning/heating system that's been in my home for 10 years or more. I'm sure it replaced the unit originally in my home. There's an air return in the largest ro… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,700 satisfied customers
The heating system seems to be on a hold for one day that I
The heating system seems to be on a hold for one day that I cannot chnge Help! … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
XR80 Trane furnace, no heat. system powered, blower starts
XR80 Trane furnace, no heat. system powered, blower starts as normal, observed igniter glow, but glow shuts off in 10 seconds with no ignition. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Lennox rooftop heating system. For some reason, it
I have a Lennox rooftop heating system. For some reason, it is not working. I have had 3 contractors out that have replaced almost every part (gas valve, igniter, etc and the thermostat). It is still … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
We had a new heating system put in this fall, and the
We had a new heating system put in this fall, and the contractor has been back 6 times trying to get the T6 thermos. working right. The down stairs thermo. operates a heat pump until the temp gets to … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
We had a new heating system installed a month or two ago and
We had a new heating system installed a month or two ago and the is a terrible squeling whenever the heat comes on. Our apartment maintence crew has tried eerything they know and it is still there. Wh… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Carrier Infinity 96 gas furnace blowing cold air
I have a Carrier Infinity 96 gas furnace blowing cold air with yellow blinking light … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Heating system working but is making a buzzing type sound
Heating system working but is making a buzzing type sound every minute or so. It sort sounds like it's trying to start but it's already running. You can hear the sound at the electrical panel inside o… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an electric heating system with a heat pump, and a
I have an electric heating system with a heat pump, and a Totaline thermostat model P274-1200. I received a NEST Pro thermostat that I would like to install. I want to make sure I have the wiring corr… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My York gas furnace blows cold air every now and then. I
My York gas furnace blows cold air every now and then. I turn down the thermostat to shut it off. I wait about 30 seconds then turn up the thermostat and 9 out of 10 times it blows warm air when it co… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Why does my furnace blow cold air? it is set to 70 and it is
why does my furnace blow cold air? it is set to 70 and it is now 64 in the house … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x