I need to integrate some airflow alarms we are installing…

I need to integrate some...
I need to integrate some airflow alarms we are installing with the fan motor controllers, so that there is no alarm when the fans have stopped.
I was told to connect the relay coil in parallel with the fan controller M coil. Then put an NO contact in parallel with the NO airflow sensor so that when fan is turned off, the relay contact will close and bypass the sensor input. I have a sketch of what I believe should be happening if someone could review, I would really appreciate it.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
3/19/2018
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'll be happy to help with this!

Yes, by all means attach your sketch using the "Attach Files" button in your reply dialog window (next to the send button).

Thanks.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
thanks and dont laugh at me

No, no worries at all! I get the jist of your plan but for me, there's one piece of the puzzle missing. What specifically is the 'alarm'? Is it in input to some type of building control or automation system? Is it just a local audible or visual alarm?

Also, in the picture with of your fan motor with a circle around it and a coil or winding inside, is that representing the coil of the fan motor contactor or starter and not the fan motor itself?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
its a dynalec airflow sensor

Thanks for that. Let me research it a bit and I'll be back shortly with more info. Thanks for your patience!

Ask Your Own HVAC Question

Ok, having read through the IO manual for that Dynalec control, it is designed to monitor airflow in a system that runs at all times and alarm if the airflow drops below a level set in an alarm trip setpoint in the control itself. The control receives inputs from a temperature sensor and an airflow sensor. Both of these sensors are analog inputs and vary their input to the control based on air temperature and air volume in feet per minute. The sensors are logic level varying inputs and specific to the controller. The airflow sensor is not a contact type signal, it is an analog signal and as such can't be overriden with any type of contact closure across its signal to the control.

Further, the control doesn't offer any type of external input to it to stop the alarm trigger when desired. Again, the control is meant for continuous operation of the monitored airflow.

It appears to me, the only way to stop this alarm panel from outputting an alarm when the system airflow is purposefully stopped is to remove the 115Vac input power to the controller itself. This could be done with the relay you reference that would have its coil in parallel with the fan motor contractor or starter. Then the added relay, through one of its normally open contacts, would interrupt power to the Dynalec controller.

I don't really see any other way to prevent an alarm from that control beside cutting the power to it. Let me know if you have questions about this.

Ask Your Own HVAC Question
Customer reply replied 3 months ago
couldn't I just alter my sketch to run wire from NO contact of relay to the NC of the air flow indicators "run relay" or whatever cuts its power

If by "airflow indicator" you mean the Dynalec alarm control itself, then yes. You would select a relay like perhaps a 90-290Q or if you wanted a simple to install relay a RIB-U1C relay in a box type. Note, these are both 24Vac coil relays, if your motor contactor has a different coil voltage you would select a relay with the same coil voltage. Then you would wire the added relay in parallel with the coil of the blower contactor so it energizes every time the blower is called to run. Then with the NO contact points on the added relay, run the input power hot wire through that relay contact so the controller shuts down if the blower contactor is deenergized.

Ask Your Own HVAC Question

If you need me to, I can draw up a quick diagram to show the wiring. Let me know...

Ask Your Own HVAC Question
Customer reply replied 3 months ago
please

Very good, this will take a bit of time but I'll have it done today. Thanks much!

Ask Your Own HVAC Question
Customer reply replied 3 months ago
thank you

You're very welcome!

Ask Your Own HVAC Question

Ok, Click Here for a schematic of how to wire your system as we discussed. Let me know if you have problems viewing it or any questions about it. You don't need to sign up for Dropbox, just click the view now button at the bottom of the dropbox window. If you have no further questions, please remember to rate positively (3 stars or better) before leaving as it's the only way I get paid for helping you.

Thanks much,

Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 1,024
1,024 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My low voltage transformer in the furnace is putting out 27v
My low voltage transformer in the furnace is putting out 27v as expected … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Trying to figure out the wiring on an old intercity unit
trying to figure out the wiring on an old intercity unit heater. The furnace flame cycles on the thermostat ok and when i hook up the fan timer relay by itself it cycles ok but I cant get the two to w… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi, I have a Honeywell Tru-steam humidifier. It is wired
Hi, I have a Honeywell Tru-steam humidifier. It is wired to come on only when there is a heat signal. This required putting a pressure switch in the plenum. I am a retired HVAC engineer with 30 years … read more
Expert
Expert
I have 2 oil fired appliances sharing one flue (HWH firing
I have 2 oil fired appliances sharing one flue (HWH firing .65 gph & Furnace .85 gph). I want to have the HWH to have priority over the furnace - therefore both will not run at same time. I have the H… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Furnance Model #EB23C -- electric furnace the furnance cyles
Furnance Model #EB23C -- electric furnace the furnance cyles through its heating cycle, then the blower shuts down, and the heating elements come back on but the blower doesn't come back on… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
Hi. Got a Lennox AM 30 unit. The blower fan stopped working,
Hi. Got a Lennox AM 30 unit. The blower fan stopped working, causing the evaporator coil to freeze. Turned off the power and thawed the coil. Tried the AC again and the fan still doesn't run, but the … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I just got an inline fan for some terrible ductwork to a room.
I just got an inline fan for some terrible ductwork to a room. How can I wire it so it comes on when the blower comes on in an xe80?… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
I have a Evcon mod EB20B furnace in my home. The fan continues
I have a Evcon mod EB20B furnace in my home. The fan continues to blow after the thermostat cuts off. The only way to make it stop is to throw the braker. We had a 6 hr blackout just prior to this sta… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Rheem RGRA - 09EZAJS turns on the blower every once in a while
Rheem RGRA - 09EZAJS turns on the blower every once in a while for about 20 to 120 seconds. The furnace operates properly by turning on when the thermostat calls for heat. It turns off when up to temp… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My tempstar hi ef furnace will not ignite. I talked yesterday
My tempstar hi ef furnace will not ignite. I talked yesterday to you folks and was unable to get my problem resolved.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
i have a goodman model ckl36-1h, the fan blows with the a/c
i have a goodman model ckl36-1h, the fan blows with the a/c on but it does not blow with the heat on... what can be the problem… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Bryant 350MAV furnace, about 8 to 10 years old, which
I have a Bryant 350MAV furnace, about 8 to 10 years old, which seems to work properly, except that the blower motor doesn't run. The burner fan turns on, the burners light, and then continue to burn f… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
replaced the fan motor last summer on a 10 year old Rheem furnace.
replaced the fan motor last summer on a 10 year old Rheem furnace. Recently turned on the gas furnce and everything lit and was gettign hot but no fan? so I turned on the fan using the manual position… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
My furnace does not blow air, I turned up the thermostat and
My furnace does not blow air, I turned up the thermostat and the pilot light went on in the furnace but its not blowing air. What causing it not to blow air… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Have problem with fan motor not turning on when compressor
Have problem with fan motor not turning on when compressor kicks in. I have what I think is a dual cap setup. Have checked for 210V at relay and is ok. 210V on output of relay ok. I hooked up power to… read more
tinman
tinman
n/a
Vocational, Technical or Trade Scho
171 satisfied customers
I have a Rheem RPKA-060JAS A/C HeatPump. The contactor got
I have a Rheem RPKA-060JAS A/C HeatPump. The contactor got stuck and the fan will not shut off. I replaced the contactor and the fan relay, but the fan will still stay on all the time except when the … read more
Charles
Charles
HVAC Technician
Associate Degree
91 satisfied customers
Im trying to use a W-R FCC 90-113 to control 2 fans. When one
Im trying to use a White-Rodgers Fan Control Center 90-113 to control 2 fans. When one goes on the other goes off and vice versa. Should work with SPDT or do I need DPDT? Having trouble figuring out w… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Bryant Preferred Series Fan Coil model FV4B. I would
I have a Bryant Preferred Series Fan Coil model FV4B. I would like to control the fan speed from a Johnson Control Metasys building automation system rather than a standard thermostat. I'm told this F… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x