I need to integrate some airflow alarms we are installing…

I need to integrate some...
I need to integrate some airflow alarms we are installing with the fan motor controllers, so that there is no alarm when the fans have stopped.
I was told to connect the relay coil in parallel with the fan controller M coil. Then put an NO contact in parallel with the NO airflow sensor so that when fan is turned off, the relay contact will close and bypass the sensor input. I have a sketch of what I believe should be happening if someone could review, I would really appreciate it.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
3/19/2018
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 976
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified

Hi I'm Brian and I'll be happy to help with this!

Yes, by all means attach your sketch using the "Attach Files" button in your reply dialog window (next to the send button).

Thanks.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
thanks and dont laugh at me

No, no worries at all! I get the jist of your plan but for me, there's one piece of the puzzle missing. What specifically is the 'alarm'? Is it in input to some type of building control or automation system? Is it just a local audible or visual alarm?

Also, in the picture with of your fan motor with a circle around it and a coil or winding inside, is that representing the coil of the fan motor contactor or starter and not the fan motor itself?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
its a dynalec airflow sensor

Thanks for that. Let me research it a bit and I'll be back shortly with more info. Thanks for your patience!

Ask Your Own HVAC Question

Ok, having read through the IO manual for that Dynalec control, it is designed to monitor airflow in a system that runs at all times and alarm if the airflow drops below a level set in an alarm trip setpoint in the control itself. The control receives inputs from a temperature sensor and an airflow sensor. Both of these sensors are analog inputs and vary their input to the control based on air temperature and air volume in feet per minute. The sensors are logic level varying inputs and specific to the controller. The airflow sensor is not a contact type signal, it is an analog signal and as such can't be overriden with any type of contact closure across its signal to the control.

Further, the control doesn't offer any type of external input to it to stop the alarm trigger when desired. Again, the control is meant for continuous operation of the monitored airflow.

It appears to me, the only way to stop this alarm panel from outputting an alarm when the system airflow is purposefully stopped is to remove the 115Vac input power to the controller itself. This could be done with the relay you reference that would have its coil in parallel with the fan motor contractor or starter. Then the added relay, through one of its normally open contacts, would interrupt power to the Dynalec controller.

I don't really see any other way to prevent an alarm from that control beside cutting the power to it. Let me know if you have questions about this.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
couldn't I just alter my sketch to run wire from NO contact of relay to the NC of the air flow indicators "run relay" or whatever cuts its power

If by "airflow indicator" you mean the Dynalec alarm control itself, then yes. You would select a relay like perhaps a 90-290Q or if you wanted a simple to install relay a RIB-U1C relay in a box type. Note, these are both 24Vac coil relays, if your motor contactor has a different coil voltage you would select a relay with the same coil voltage. Then you would wire the added relay in parallel with the coil of the blower contactor so it energizes every time the blower is called to run. Then with the NO contact points on the added relay, run the input power hot wire through that relay contact so the controller shuts down if the blower contactor is deenergized.

Ask Your Own HVAC Question

If you need me to, I can draw up a quick diagram to show the wiring. Let me know...

Ask Your Own HVAC Question
Customer reply replied 1 month ago
please

Very good, this will take a bit of time but I'll have it done today. Thanks much!

Ask Your Own HVAC Question
Customer reply replied 1 month ago
thank you

You're very welcome!

Ask Your Own HVAC Question

Ok, Click Here for a schematic of how to wire your system as we discussed. Let me know if you have problems viewing it or any questions about it. You don't need to sign up for Dropbox, just click the view now button at the bottom of the dropbox window. If you have no further questions, please remember to rate positively (3 stars or better) before leaving as it's the only way I get paid for helping you.

Thanks much,

Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 976
Experience: I have been an HVAC/R mechanic/technician for 30+ years.
Verified
Brian HVAC Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?
Ask Brian HVAC Guy Your Own Question
Brian HVAC Guy
Brian HVAC Guy
Brian HVAC Guy, HVAC Technician
Category: HVAC
Satisfied Customers: 976
976 Satisfied Customers
Experience: I have been an HVAC/R mechanic/technician for 30+ years.

Brian HVAC Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

976 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I want to power a single speed circulator pump from a 120ac
I want to power a single speed circulator pump from a 120ac gfi outlet through a honeywell r8285a control center and a honeywell ct33a thermo- … read more
Dales-Electronic
Dales-Electronic
1,033 satisfied customers
I have a Plus 90i gas furnace and was told there was no
I have a Bryant Plus 90i gas furnace and was told there was no filter installed. When I opened the door to find where to put a filter, I see no where to install one. Can you help?… read more
David Bowden
David Bowden
Owner
764 satisfied customers
We have a Rheem Model RTGH-95DVLN, it has been in use for 13
We have a Rheem Model RTGH-95DVLN, it has been in use for 13 months with no issues,. the P1 error code was flashing and the burner not firing up. I flushed the system with vinegar and cleaned the smal… read more
canuck the pro
canuck the pro
253 satisfied customers
Heil-McLain Cg 25 thru 8 Valve P/N VR8300C-4100, Tonight.
Tonight. The “controller circuits” are making a call because I have 24 VAC at the Honeywell valve. The pilot light stays on and when I disconnect 1 of the VAC drive connections to the valve I hear an audible “click.” The valve body is warm, but not excessively. The main burners do not light. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I bought a blower motor for my heat pump and it didnt have
i bought a blower motor for my heat pump and it didnt have any wires for the blower relay which means the blower stays on all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I have a garland strarfire series 48" wide stove. i am
i have a garland strarfire series 48" wide stove. i am looking for new dials … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
I have an A.O. 50 gallon natural gas promax hot water
I have an A.O. Smith 50 gallon natural gas promax hot water heater. After running 15 or 20 minutes the gas valve iidicats excessive exhaust back pressure and shut the burner off. I checked the intake … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Your answer to my pilot light problem was that my flame
Your answer to my pilot light problem was that my flame sensor rod was dirty. Do I need to remove the burner assembly to clean this rod?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
Is this a refrigerant leak on my outdoor a/c unit? When I
Is this a refrigerant leak on my outdoor a/c unit? When I click the thermostat to Cool /Auto the outdoor unit clicks one time and then does nothing (no humming sound or anything)and warm/room temp air… read more
Bill
Bill
Service Mgr
82 satisfied customers
I have a Honeywell T3 thermostat and a heat pump. The heat
I have a Honeywell T3 thermostat and a heat pump. The heat comes on no matter what the setting is. I need help. … read more
hvacdave84
hvacdave84
53 satisfied customers
How to hook up Honeywell pro 3000 series thermostat to ruud
how to hook up Honeywell pro 3000 series thermostat to ruud rqpm 14 seer 2-4 ton series … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
976 satisfied customers
Live in apt bldg. central air Heat pump FHP MFG EC060-1HZC.
Hi. Live in apt bldg. central air Heat pump FHP MFG EC060-1HZC. Had TH8100U1003. Could no longer adjust temp as if right side of screen died. Replaced with RTH8500D. Wired same as old one. Red to R Bl… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 116B and wondering if the nest thermostat is
Hello, I have a Bryant 116B and wondering if the nest thermostat is compatible? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
I have a Lennox G40UH furnace and there is no power
Hi there! I have a Lennox G40UH furnace and there is no power registering at the thermostat and furnace at this time. I checked the circuit breaker and re-checked the wire connections in the thermosta… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,690 satisfied customers
Do I need an app to my wifi thermostat. Linksys. I can
Do I need an app to my wifi thermostat JA: Who makes your router? Customer: linksys JA: What have you tried so far? Customer: I can connect but not control or program JA: Anything else you want the Ne… read more
Sheri
Sheri
Bachelor\u0027s Degree
413 satisfied customers
We have a gas burner that will not run. It fires, rumbles
We have a gas burner that will not run. It fires, rumbles and goes out. We can do this all day. The gas water column is correct. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The furnace is Lenox, Model G20Q3E-75-4, Serial number
The furnace is Lenox, Model G20Q3E-75-4, Serial number 5894M35521. This was in a foreclosed house so I don't know the history. The blower comes on but the burners don't come on.… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Blower Motor runs all the time even when thermostat is set
Blower Motor runs all the time even when thermostat is set above/ below set point. Condenser cycles on/off when set point is reached. … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
976 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x