I have an Amana furnace 70K btu model # GSI070B30B. It

Customer Question
I have an Amana...

I have an Amana furnace 70K btu model # GSI070B30B. It suddenly stopped operating yesterday morning after running one heating cycle to warm the house.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

I replaced the thermostat with one that I knew was functional - no success. The filter is a bit dirty.

Contractor's Assistant: Do you plan on doing the work yourself?

I installed a Bryant 80K upflow in my own home a few years back. The Amana is at my rental. So, yes.

Contractor's Assistant: Anything else we should know to help you best?

Circuit breaker did not trip. Otherwise, I didn't test power to the unit yet.

Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
3/19/2018
HVAC Technician: Rick, HVAC Supervisor replied 1 month ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 23,765
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

Does the draft/exhaust fan run? do you have power to the unit?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Nothing runs. As I noted above, I did not check power to the unit but have no reason to believe the power supply was interrupted.How to I check power to the unit?
HVAC Technician: Rick, HVAC Supervisor replied 1 month ago

You need a multi-meter and probe the incoming electrical feed.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Assuming I have power, what is the next step?
HVAC Technician: Rick, HVAC Supervisor replied 1 month ago

I'm not doing hypotheticals. You need to be onsite to trouble shoot this.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
What I am looking for are step-by-step instructions to diagnose the problem. Ideally, your service would have a basic diagram of the electrical system (I understand that manufacturers have differences but, the units are basically the same).Just received your message that you are not doing 'hypotheticals'. If I go to the site, later this morning is there an additional charge to resume this conversation?
Customer reply replied 1 month ago
Also, would a volt meter suffice?
HVAC Technician: Rick, HVAC Supervisor replied 1 month ago

No these units are not basically the same when it comes to trouble shooting. No additional charge to pick this up later. This is an old unit with next to no specs available so I'd need a clear picture of the wiring diagram if basic first steps don't work. It is usually pasted to the inside of one of the access panels. A voltmeter is OK if it can read both 120 and 24 volts AC.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I have a Klein ET200 voltage and continuity tester with a range from 12 to 600 voltsHow do I resume this call and can I text you a photo of the wiring diagram?
HVAC Technician: Rick, HVAC Supervisor replied 1 month ago

Just come back here.

Click on the link below for info on posting pics here

http://ww2.justanswer.com/help/how-do-i-send-photo-or-file-expert-hl

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The compressor trips the circuit breaker in the house, not
the compressor trips the circuit breaker in the house, not immediately, about after 5 minutes. what are my options? can i replace only the compressor? It is a frigidare model FS3BC-042KA … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
Air Handler # NFCX3600C2 what causes the circuit breaker
Air Handler # NFCX3600C2 what causes the circuit breaker panel to fry? I replaced it once and the heat worked OK but when I tryed to run A C the board fryed again … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
My Amana furnace is not working. I did, There is 3 blink
Hi JA: Hi. How can I help? Customer: My Amana furnace is not working JA: Did you check the furnace's filters? Customer: Yes I did, There is 3 blink error JA: Do you plan on doing the work yourself? Cu… read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
Our new Amana Furnace (installed earlier this year) won't
Hi Pearl, our new Amana Furnace (installed earlier this year) won't seem to heat up past 60-66 … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,676 satisfied customers
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
My amana furnace is not igniting. Hopefully. The red light
My amana furnace is not igniting JA: Did you check the furnace's filters? Customer: Yes JA: Do you plan on doing the work yourself? Customer: Hopefully JA: Anything else we should know to help you bes… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an amana furnace pga30b0702c and the led light inn
I have an amana furnace pga30b0702c and the led light inn the control board is not on. I have 120v going to the board in 2 places. It is a 240v unit. Should three light always be on or is there someth… read more
Chad DeYoung
Chad DeYoung
11 satisfied customers
I have an Amana furnace. it won't light. it will if I remove
I have an Amana furnace. it won't light. it will if I remove the drain line on the bottom of the vent blower. i have cleaned the line out but when i put it back in the drip leg it shuts down again. co… read more
Rick
Rick
HVAC Supervisor
23,765 satisfied customers
I have an Amana furnace and am having trouble getting it to
I have an Amana furnace and am having trouble getting it to fire. … read more
Rick
Rick
HVAC Supervisor
23,765 satisfied customers
Amana furnace. Heater has only turned on once, very
Amana furnace. Heater has only turned on once, very randomly, since the cooler weather began. Fan works fine when turned to “on”. Doesn't run at all on “auto”. I've tried turning the heat up over 70, … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
Appliance Guru
Appliance Guru
17,731 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
767 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,514 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,099 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x