I replaced the batteries on a Chronotherm IV plus. Honeywell…

I replaced the batteries...

I replaced the batteries on a Chronotherm IV plus. Honeywell and now cannot get ac or heat to come back on. The fan will cycle but not the heat or ac. Can you help?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Filters are good. I am running a test program for ac now with unit. But outside ac unit not turning on seems like just fan running

Contractor's Assistant: Do you plan on doing the work yourself?

I was hoping it was some kind of reset since it was working fine prior to replacing batteries

Contractor's Assistant: Anything else we should know to help you best?

I have a downstairs and upstairs unit and both stopped operating when batteries replaced on thermostat

Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 4 months ago
I have checked circuit breakers and even reset them
Customer reply replied 4 months ago
Is someone there .
Customer reply replied 4 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 4 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Customer reply replied 4 months ago
Is anyone there
Answered in 53 minutes by:
3/19/2018
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, I am reading your question now, back in a minute

Ask Your Own HVAC Question

So far it sounds like the pins on the thermostats wall mounted sub base got bent or for some reason are not making contact with the thermostat once you have it back in place.

To test, tell me what color of wire goes to which lettered terminal on the thermostat sub base, and I will then instruct you on how to do the needed tests.

.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today.

If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
Customer reply replied 4 months ago
I took off the cover but cannot see wire colors on sub base
Customer reply replied 4 months ago
Should I take off the sub panel?

Send me a photo of the wall mounted sub base with the thermostat removed, it is not the thermostat cover we want to remove, but the entire thermostat, most of those can be gently pried off of the wall mounted sub base... the thermostat wire connections there are out in the open at that point and obvious

Ask Your Own HVAC Question

Yes I got the photo's thanks, ***** ***** paper clip wire to jumper R to W, the heat should come on, next jumper R to Y, the cooling should come on, next jumper R to G the fan should come on.... it all that happens, but not with the thermostat, the problem is with the thermostat, try refitting the thermostat and setting to extremes for heat and cool tests, and tell me what you can discover.

We can go from there

Ask Your Own HVAC Question
Customer reply replied 4 months ago
Ac made a clicking noise outside but did not turn on with wires red to yellow connectedSo outside compressor problem ?

Yes. make sure the power to the AC outside is turned on, next do the other jumper tests, R to W and R to G and tell me if the heat and fan came on or not

Ask Your Own HVAC Question
Customer reply replied 4 months ago
heat and fan seemed to come on. It is really hot so I did not leave heat on for long. I think I have to give up and call technition tomorrow

Thanks for the test, if these functions worked with jumpers in place, but not the thermostat, then the thermostat is bad OR you put the batteries in backwards OR the batteries were no good etc. Try that before you spend hundreds of dollars on a service call, then get back to me.

We can go from there

.

Its time to rate my input for the day, that gets me paid, locate the "finish and rate your expert" link near the top of the page and click on it. I will appreciate that very much.

I am in every day from 9 am to 11 pm west coast USA time to do any follow up needed.

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified
Phil and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,701
9,701 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,701 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a honey well thermostat with 2 systems in a 2 story
I have a honey well thermostat with 2 systems in a 2 story house. One thermostat for downstairs (Main one) , one for upstairs (secondary ) . Currently, the upstairs unit is running on the desire cool … read more
Phil
Phil
Mechanical Engineer
9,701 satisfied customers
I have upstairs and downstairs w/ seperate thermostats. Upstairs
I have upstairs and downstairs w/ seperate thermostats. Upstairs works fine. Downstairs thermostat says its working but no air.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Honeywell T8131C thermostat displays Low bat and I cannot
My Honeywell T8131C thermostat displays Low bat and I cannot get it to go off or get the heat running.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am having difficulty getting my heat to come on & stay on. Sometimes it is in wake m
I am having difficulty getting my heat to come on & stay on. Sometimes it is in wake mode or return mode. I woke up to 53° and turned system off. Just returned home and it was in RETURN mode when I tu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Quick question Douglas, I have two of these same thermostats in my townhome. Houston has
Quick question Douglas, I have two of these same thermostats in my townhome. Houston has days that start off in the 50's and end in the 70's... My girlfriend sometimes leaves the upstairs thermo on he… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We
Honeywell Chronotherm III unit shows 9642 and 189459D inside. We had a normal yearly service and now it keeps resetting the unit internally to cool when it is set on heat for the bottom setting and th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have two thermostats in our hosue, both different models,
We have two thermostats in our hosue, both different models, one upstairs one downstairs. The batteries in the upstairs thermostat, a Honeywell Chronotherm III, model T8600(C1014?), recently died, wit… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Hello. I have a Honeywell Chronotherm III thermostat, installed
Hello. I have a Honeywell Chronotherm III thermostat, installed around 1989 or 1990. I have identical units upstairs and downstairs. The downstairs unit indicates "replace battery." I replaced the bat… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
my honeywell chronotherm iv plus T8602D 2018 thermostat is
my honeywell chronotherm iv plus T8602D 2018 thermostat is not working and indicates that the battery needs replacing, but I have just replaced the battrey. Any idea what is wrong?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, my thermostat digital screen in blank and it is not
Hello, my thermostat digital screen in blank and it is not cooling. It must have power to it because I can turn on the fan by sliding it from auto to fan an it comes on… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
The LCD of my honeywell thermostat chronotherm iv plus goes
The LCD of my honeywell thermostat chronotherm iv plus goes blank. I removed the panel and found no battery. The model is T860002028. What should I do? Thank you!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane 4TWx4030A, with air handler 4TEE3F31A, and Honeywell
Trane 4TWx4030A, with air handler 4TEE3F31A, and Honeywell T8611G (Chronotherm IV) is not heating. What I have Checked: Checked fuses (with fluke)-Ok, Checked all Breakers-OK, the thermostat says heat… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Honeywell Chronotherm IV upstairs and down (different
I have a Honeywell Chronotherm IV upstairs and down (different models). The upstairs heat works, but the downstairs will not. The thermostat has power, and the "flame" icon comes on, but not the heate… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Honeywell Chronotherm IV plus thermostat. we programed temp
Honeywell Chronotherm IV plus thermostat. we programed temp for 7 days. press run program.. nothing happen !… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I replaced my AA batteries in my Honeywell Chronotherm IV Plus
I replaced my AA batteries in my Honeywell Chronotherm IV Plus programable thermostat and now the furnace continually runs unless I disconnect the unit from the wall. How can I prevent this from happe… read more
DuWayne
DuWayne
Sales/ Service
Vocational, Technical or Trade Scho
126 satisfied customers
Hello, I have a honeywell chronotherm IV plus thermostat model
Hello, I have a honeywell chronotherm IV plus thermostat model number T8601D2019. The display turned off suddenly and will not come back on. Breakers are on. I did not see any replaceable batteries fo… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a honeywell chronotherm III T8601 that is not working.
I have a honeywell chronotherm III T8601 that is not working. The display was blank so we changed the batteries and now the display is showing the correct programmed times and temps, but when we try t… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Hello! I didnt know how to ask you my specific question
Hello! I didn't know how to ask you my specific question, so I'm trying this method of asking the question. I'm trying to reset the filter on a Honeywell Chronotherm IV Plus electronic thermostat. Tha… read more
Curtis
Curtis
High School or GED
2 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x