We have a Model no. rpka-018jaz from 1998 it works fantastic…

Hi Pearl, my name...

Hi Pearl, my name is***** have a Model no. rpka-018jaz from 1998 it works fantastic but since we had a Nest thermostat installed the contactor won't engage on the heat setting. i've had Nest check it twice and they can't diagnose it beyond the thermostat. could it be a wiring problem at the heat pump or compressor/

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Only filter is at the return air in the hall and Nest has done remote check and come to the house to check settings. when i turn on heat i have to go to the compressor and put a small nail in to hold the contractor down. if i don't the unit buzzes very loud.

Contractor's Assistant: Do you plan on doing the work yourself?

That depends on the level of difficulty. Probably not

Contractor's Assistant: Anything else we should know to help you best?

The system worked fine with the old white rogers thermostat. nothing else

Show More
Show Less
Ask Your Own HVAC Question
Answered in 8 minutes by:
3/18/2018
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,155
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

hello,

can you tell me what color wires are on what terminal?

Ask Your Own HVAC Question

and you have a heat pump?

It appears you are wired for gas furn and ac....there is no wire in w2/aux which is usually white...and there is no wire in O/B which is a reverse valve that determine heat or cool

Ask Your Own HVAC Question
Customer reply replied 5 months ago
the heat pump is also Rheem

Ok we may have to get into the air handler...

The thermostat is not wired for heat pump ...we can move the white to w2/aux easy enough but we are missing a wire that should be on O/B

Ask Your Own HVAC Question

can you get into the indoor blower unit for me?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Is that wire from heat pump to thermostat or heat pump to compressor/

it is a wire from the outdoor unit that comes into the air handler and then leapfrogs to thermostat.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
blower, do you mean compressor

no...you have a heatpump outside and a blower unit inside correct?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I can get into the compressor

what about the air handler inside?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I can get to the air handler but not now

ok lets see if we can find what color goes to reverse valve...can you see wiring at outdoor heat pump?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I’m going outside now

remove the metal panel to where we can see the defrost board...when was the last time this ran as a cooling and heating heat pump? I only see 3 wires hooked up?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Thermostat wires are yellow brown and white connecting to Brownyellow and dark blue With a purple wire that is capped

Interesting...commonly there are 5-6 wires attached at outdoor unit..

I am going to guess the white wire is being used for reverse valve...do you mind a quick test at thermostat that involves twisting certain wires together?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
No

first test..

Red wire twisted to yellow and green....so red yellow green all combined...do you get ac?

Ask Your Own HVAC Question

then add the white...so red white yellow green all twisted together..NOT the C wire....do you get heat?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
Ac is on

then add the white...so red white yellow green all twisted together..NOT the C wire....do you get heat?

Ask Your Own HVAC Question
Customer reply replied 5 months ago
heat is on

ok so there was some creative wiring done at some point.

Leave red in rh

green in g

yellow in y

MOVE white to O/B

Then put a short wire jumper in w2 to Y1....you can use a piece of thermostat wire unused about 1-2 inch long.

Then you will have heat and cool....the reverse valve O/B terminal may need to be set for Heat

Ask Your Own HVAC Question
Customer reply replied 5 months ago
OK. I’ll have to go to my truck to get some wire. Not clear on the Reverse valve OB

you will move the white wire to O/B terminal.

Once booted the Nest will pick up there is a wire in O/B and ask you if you want to energize for ac or heat...you will energize for heat

Ask Your Own HVAC Question

just let me know back here how it goes.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I have yellow in y1, jumper won’t fit

then you would need to cut Y wire about 2-3 inches back from end and add a jumper with a wire nut...so the yellow wire would come up and split into 2 like a y with one in Y1 and the other in W2

Ask Your Own HVAC Question
Customer reply replied 5 months ago
55357;�

let me draw something..just a minute

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I’m going to have to put this on hold and get a small wire nut. I will get back in touch with you when I do that. Thank you for your help so far.

ok move w2 to w1 and see how the nest interprets

Ask Your Own HVAC Question
Customer reply replied 5 months ago
nearest said it could not respond without wire changes. So W-2 went back to W1. I’ll get some’s smaller gauge thermostat wire and wire nut and try this later this afternoon. Thanks again, John

Ok, just let me know when you get more updates.

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,155
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 5 months ago
Billy, Jon Love here. The jumper worked, heat and cooling are up and running from the Nest! Thanks very much for your help.

Great news...I am glad all is well.

Just rate service with the 5 star system close. Thank you for your patience!

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 23,155
23,155 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a RUDD Achiever compressor. About a month ago, it
HI, I have a RUDD Achiever compressor. About a month ago, it started making a loud buzzing sound and the only way I could really keep the house warm was to use the Emergency Heat setting. Now, it's un… read more
Bill
Bill
Service Mgr
114 satisfied customers
My carrier system keeps giving me a “system malfunction
HelloMy carrier system keeps giving me a “system malfunction message' and when i check the Infinity thermostat it suggested the Contractor Shorted. So it is now twice I have had to do this and still g… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Aloha from Maui, hot today no a/c. neither air handler or
Aloha from Maui, hot today no a/c. neither air handler or compressor will run. checked thermostat, no 24 volt input. checked contactor at compressor, have 250v power but no voltage at contactor coil i… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Sure thanks so I just turned the heat on for the first time,
sure thanks so I just turned the heat on for the first time, and after a few minutes it starts buzzing. This happened last year too, and I had a guy come out and fix it, but it was really simple fix, … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,751 satisfied customers
I am having a problem with my compressor. Thermostat
Hello, I am having a problem with my compressor. Thermostat is on and fine, air handler in the attic is moving air, but the compressor is not coming on when I call for cooling from the thermostat.… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
AC quit cooling. Mouse nest in outdoor a/c by Cap and switch.
AC quit cooling. Mouse nest in outdoor a/c by Cap and switch. Cleaned. Fan works, but doesn't blow cold air. Sometimes, inside thermostat flashes cool. When I took rat nest out, it would run for 10 se… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
80 satisfied customers
I'm trying to troubleshoot a problem with my Goodman condenser
I'm trying to troubleshoot a problem with my Goodman condenser unit. It runs constantly. I have replaced the contractor with a new one. At the unit outside, I measure 27 VAC between the common (blue w… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have a BDP compressor. When I turn on the AC the compressor
I have a BDP compressor. When I turn on the AC the compressor does not come on and the fan just blows warm air. It just stopped working this afternoon and the compressor is probably 30 years old. Can … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, My A/C started blowing warm air last night. I checked
Hi, My A/C started blowing warm air last night. I checked the circuit breaker and saw that the breaker for the A/C had tripped. I switched breaker to off and then to on again. Checked the unit outside… read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
State Licensed Mechanical Contractor
23,155 satisfied customers
Central air on coolsetting fan runs compressor fan runs but
Central air on coolsetting fan runs compressor fan runs but doesnt seem to pump freon high and low press pipes not hot or cold… read more
Appliance Tech Larry
Appliance Tech Larry
Outside inhome service tech
High School or GED
19,156 satisfied customers
I have a Lennox HP26-030-7-P Heat Pump unit. When the thermostat
I have a Lennox HP26-030-7-P Heat Pump unit. When the thermostat calls for heat or cooling, the compressor contactor only engages for a second or two, then stops. The compressor damage safety delay is… read more
spivco
spivco
153 satisfied customers
TRANE HEAT PUMP MODEL 2WCC3042A1000AA - SER # XXXXX Manufactured
TRANE HEAT PUMP MODEL 2WCC3042A1000AA - SER # XXXXX Manufactured 4/2006 - Install date 6/26/2006 - Standard Limited Warranty 5 years, (just missed the cutoff) Units serviced within last 5 weeks for wi… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Im working on a 3 phase, 7.5 ton, 2-stage Trane Condenser.
I'm working on a 3 phase, 7.5 ton, 2-stage Trane Condenser. It is a 2006 system-not too old. When in cooling mode condenser fan will come on, but not compressor. I've checked all electrical connection… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Arcoaire N8MPN furnace, the fan for the air conditioner
I have a Arcoaire N8MPN furnace, the fan for the air conditioner would not start. (I tried turning the thermostat to heat and that didn't work either) I removed the access panel and found that the 5 a… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
My 1yr old Goodman Heatpump(GSZ130241AB) makes loud hard
My 1yr old Goodman Heatpump(GSZ130241AB) makes loud hard start noise @ start up, it made this noise about a day after installed. It is a slit system with about a 50 ft. line set. no inverted loop in l… read more
Charles
Charles
State Licensed HVAC Contractor
Associate Degree
68 satisfied customers
Have an older RUUD unit-inside fan turns on when set to cool,
Have an older RUUD unit-inside fan turns on when set to cool, but outside unit will not start. Contactor has no voltage to engage either fan or compressor; if I manually press down contactor everythin… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
I just had rheem 18 seer 2 stage split unit installed. It has
I just had rheem 18 seer 2 stage split unit installed. It has two compressors. It is cooling the house great but there is a loud buzzing noise coming from the outside unit. Any idea what can cause thi… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
My window air conditioner makes a loud buzzing noise when the
My window air conditioner makes a loud buzzing noise when the cooling kicks in. Is there anything I can do to remedy this? It seems to get worse the longer its been running.… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x